WinCC flexible Data Entry Limit

Hi All,
I have issue with WinCC data entry field if somebody can help me with. There are few set points to be written to PLC from the Simatic multipanel HMI. I am using WinCC flex Advance to configure this HMI.

Whenever an operator enters the setpoint from the HMI, HMI should check the limit on the Setpoint tag, if the value entered exceeds the limits on the tag then it should not allow that data entry and should show previously entered value.

I tried to implement this but what is happening just now is, HMI is not passing the exceeded value to the PLC but it is holding exceeded value in the field on the dispaly so operator could be mislead that the value has been through to PLC. The value only returns to the previous value when you navigate to different screen and come back again on same screeen.

I appreciate all the help.
  Reply With Quote
Old September 12th, 2010, 08:11 AM   #2
CharlesM
Member
United States

CharlesM is offline
 
Join Date: Aug 2005
Location: Arkansas
Posts: 1,085
I don't know if its a limit problem. When I set limits to a tag and enter a number out of range it will go back to what it had in it. Also as I am entering the tag a pop up will display the limits. I am using PC RT but I would think this would be the same. I have had this type of problem with recipes. If the tag is in a recipe it must be sync with plc. You can do this by calling the setdatarecordtags from the onchange event of the tag.
  Reply With Quote
Old September 12th, 2010, 08:21 AM   #3
JNS
Member
United Kingdom

JNS is offline
 
Join Date: Apr 2009
Location: UK
Posts: 26
Hi Charles,
The values is going back to previous for some but not for others and I dont see difference in the configuration between them.Any idea what could it be???

Thanks
  Reply With Quote
Old September 12th, 2010, 09:23 AM   #4
erdemsvri
Member
Germany

erdemsvri is offline
 
Join Date: Jul 2009
Location: Germany
Posts: 171
Hello

This looks like a acquisition problem. Please check your tag acquision mode unders Tags properties (under General Tab) in WinCC Flexible.

Communication >Tags >General >Acquisition mode

It should either be cyclic on use or cyclic continous.
  Reply With Quote
Old September 12th, 2010, 10:25 AM   #5
JNS
Member
United Kingdom

JNS is offline
 
Join Date: Apr 2009
Location: UK
Posts: 26
Hi,
The issue is resolved. It was to do with they were selected as just "input" i.e. no readback is allowed. I have changed them to "input/ouput" and now they are working perfectly fine.


Cheers
  Reply With Quote
Old September 12th, 2010, 11:23 AM   #6
ankitjain
Member
India

ankitjain is offline
 
Join Date: Sep 2010
Location: delhi
Posts: 6
Hii....can anyone guide me how does scada intouch communicate with plc fatek???
  Reply With Quote
Old September 12th, 2010, 12:59 PM   #7
Paul B
Member
United States

Paul B is offline
 
Paul B's Avatar
 
Join Date: Sep 2009
Location: North Carolina
Posts: 571
Quote:
Originally Posted by JNS View Post
Hi,
The issue is resolved. It was to do with they were selected as just "input" i.e. no readback is allowed. I have changed them to "input/ouput" and now they are working perfectly fine.


Cheers
I have been bitten by that before...

Glad you got it fixed!
__________________
"I never let a cowboy make the coffee."
Yeah, thats what Granny always said to my Grandad.
And he'd say: "Never tell a joke that ain't that funny more than once."
"And if you wanna hear God laugh, tell Him your plans."
Van Zant "Help Somebody"
  Reply With Quote
Old September 12th, 2010, 01:02 PM   #8
Paul B
Member
United States

Paul B is offline
 
Paul B's Avatar
 
Join Date: Sep 2009
Location: North Carolina
Posts: 571
Quote:
Originally Posted by ankitjain View Post
Hii....can anyone guide me how does scada intouch communicate with plc fatek???
You should start a new thread with your question, after you have searched.

Go here:
http://www.plctalk.net/qanda/forumdisplay.php?f=2

And search.

Then if you need to ask your question, start a new thread.
http://www.plctalk.net/qanda/newthre...=newthread&f=2

Welcome to the forum!
__________________
"I never let a cowboy make the coffee."
Yeah, thats what Granny always said to my Grandad.
And he'd say: "Never tell a joke that ain't that funny more than once."
"And if you wanna hear God laugh, tell Him your plans."
Van Zant "Help Somebody"
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Citect Vs WinCC - Long Doug_Adam LIVE PLC Questions And Answers 20 May 28th, 2013 12:02 PM
Batchsystem in WinCC Flexible, opinions about what they want Combo LIVE PLC Questions And Answers 26 September 8th, 2008 08:20 AM
Wincc Flexible Runtime / Archives for RT dwcy LIVE PLC Questions And Answers 9 March 18th, 2008 12:24 PM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 06:24 AM
WinCC Flexible Quirks tvey LIVE PLC Questions And Answers 5 May 3rd, 2007 05:57 AM


All times are GMT -5. The time now is 09:16 PM.


.