Member
|
Factory Talk View SE Errors
I am trying to edit a factory talk view se application V5.10 and when i try to delete some objects and save i am getting this error.
Unable to Load Active X control for display 10-Press Parameters Cause RsView 32/SE Idle Detect Control : Activex control not found on your computer. Cause RsView 32/SE Idle Detect Control : CAB File Missing on the server : http://localhost/RSViewActiveXContro...eDetectocx.CAB Any Ideas? I have never seen this happen before. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
It means what it says. For whatever reason, some VBA or object on a display is looking for an ActiveX DLL to handle (guessing) Idle state detection. Since FTView SE is basically a glorified web browser, it supports automatic installs of ActiveX components (depending on your IE Security settings too).
ActiveX installs are made by archiving a DLL file and an INF file into a CAB file, and sticking in that directory for FTView SE to find.
__________________
------------------------------------ How to ask questions the SMART Way! Look First, Ask Second! |
![]() |
![]() |
#3 |
Member
|
You need to install the RA idle detect utility. It's a free download.
|
![]() |
![]() |
#4 |
Member
|
Got it and installed it. How do you configure the idle time amount. I see no way to access the utility from start/programs,etc?
|
![]() |
![]() |
#5 |
Member
|
As I recall, since it's an ActiveX control, a instance of this control must be placed on a .gfx screen that is always running. This could be a header bar on top of the screen for example. In the grafix editor once the control is installed, you can brouse to it to place it on the FTView screen editor ActiveX toolbar. Once on the screen, you can right click on it to set the properties. There should be documentation that come with the download which explains it's operation.
|
![]() |
![]() |
#6 |
Member
|
I downloaded it from KB document 23830. There was no documentation with it and that is the only place i found it on the AB site.
|
![]() |
![]() |
#7 |
Member
|
From TN 48268:
|
![]() |
![]() |
#8 |
Member
|
Thanks
|
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Feb 2016
Location: Nashik
Posts: 1
|
Unable to download Ra ideal Utility ..PLease send free download link
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Factory Talk View SE fail to load HMI server | MALRDG | LIVE PLC Questions And Answers | 13 | January 29th, 2014 09:28 AM |
Rockwell Factory Talk View SE with windows 7 | msynco | LIVE PLC Questions And Answers | 3 | August 27th, 2011 04:48 AM |
alarm fault dialog limit in Factory Talk View Studio SE 5 | NumeG | LIVE PLC Questions And Answers | 0 | February 17th, 2010 09:31 AM |
Factory Talk View SE Client | kurt.brinker | LIVE PLC Questions And Answers | 3 | September 11th, 2008 10:11 AM |
Upgrade to factory talk view se | kurt.brinker | LIVE PLC Questions And Answers | 2 | January 11th, 2008 03:37 PM |