Old October 5th, 2010, 09:15 AM   #1
Mike_RH
Lifetime Supporting Member
Canada

Mike_RH is offline
 
Join Date: Sep 2006
Location: Toronto
Posts: 322
Siemens Drive ES Basic

Can anyone tell me what this software will do, that Starter does not?

When I ask my local Siemens guys, the drive guy says its a PLC thing, the PLC guy says its a drive thing, and I going WTF?

When / why do I need it?

Thanks
__________________
Mike
  Reply With Quote
Old October 5th, 2010, 09:34 AM   #2
dskohio
Member
United States

dskohio is offline
 
Join Date: Sep 2005
Location: Virginia
Posts: 104
My understanding is that Drives ES will integrate into your Simatic Manager software. This way you can save one project file that contains your PLC program and your drives configuration.
  Reply With Quote
Old October 5th, 2010, 09:51 AM   #3
Mike_RH
Lifetime Supporting Member
Canada

Mike_RH is offline
 
Join Date: Sep 2006
Location: Toronto
Posts: 322
Yes, but how is that different than Starter (Which is free!)
__________________
Mike
  Reply With Quote
Old October 5th, 2010, 09:56 AM   #4
dchartier
Member
Canada

dchartier is offline
 
Join Date: May 2003
Posts: 1,492
Hello Mike;
Have a look at the following information from dsiemens:
http://support.automation.siemens.co...ew/en/43265497
Summarized:

Advantages a Drive ES Basic installation with respect to all of the individual tools (STARTER Stand alone, SIMOCOM U/A and DriveMonitor)
    • Drives can be more easily integrated into the hardware configuration of SIMATIC S7
      using the Object Manager (SlaveOM and DeviceOM) instead of using GSD files.
    • Communication that also extends beyond network limits using routing in the SIMATIC and SIMOTION stations.
      Without Drive ES, the individual tools can only communicate with drives, which are
      connected to the same subnetwork (PROFIBUS, PROFINET) as the engineering PC/PG.
    • The tool can be directly called from the SIMATIC Manager in a context sensitive way.
      When this is done, all of the network infrastructure information is automatically transferred for the routing.
    • Data is archived/saved in the S7 project
    • Direct communication via PROFIBUS
      Without Drive ES, the DriveMonitor can only communicate with drives using the
      USS protocol via a serial interface or via a PROFIBUS-OPC server
Hope this helps,
Daniel Chartier
  Reply With Quote
Old October 5th, 2010, 10:06 AM   #5
Mike_RH
Lifetime Supporting Member
Canada

Mike_RH is offline
 
Join Date: Sep 2006
Location: Toronto
Posts: 322
Thanks Daniel,
That link helped, but I am still a little unsure of the difference (benefits) of Drive ES vs Starter.
__________________
Mike
  Reply With Quote
Old October 5th, 2010, 10:06 AM   #6
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 10,788
This part is not true:
"Communication that also extends beyond network limits using routing in the SIMATIC and SIMOTION stations.
Without Drive ES, the individual tools can only communicate with drives, which are
connected to the same subnetwork (PROFIBUS, PROFINET) as the engineering PC/PG."
I have succesfully had routing with only STARTER and MM4 drives. With STARTER being connected via ethernet to the PLC which connected to the MM4 via Profibus.

And this part only pertains to Drivemonitor, not to STARTER:
"Direct communication via PROFIBUS
Without Drive ES, the DriveMonitor can only communicate with drives using the
USS protocol via a serial interface or via a PROFIBUS-OPC server"
STARTER can communicate via Profibus.

So I dont think there is much advantage to DRIVE ES Basic.
__________________
Jesper
  Reply With Quote
Old October 5th, 2010, 10:25 AM   #7
Mike_RH
Lifetime Supporting Member
Canada

Mike_RH is offline
 
Join Date: Sep 2006
Location: Toronto
Posts: 322
Jesper, I have also used Starter routed from Ethernet to DP, and slso integrated with Step 7. Which is why I am confused about the benefits of Drive ES Basic.

Anymore comments / opinions?
__________________
Mike
  Reply With Quote
Old October 5th, 2010, 12:37 PM   #8
Mike_RH
Lifetime Supporting Member
Canada

Mike_RH is offline
 
Join Date: Sep 2006
Location: Toronto
Posts: 322
Just to give this a little bump.

What would be nice is a comparison table between Drive ES and Starter, showing / highlighting the differences.

Thanks
__________________
Mike
  Reply With Quote
Old October 5th, 2010, 02:54 PM   #9
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 10,788
I think it boils down to what dskohio wrote.
__________________
Jesper
  Reply With Quote
Old October 7th, 2010, 05:48 PM   #10
JRW
Member
United States

JRW is offline
 
JRW's Avatar
 
Join Date: Jun 2002
Location: Upstate South Carolina
Posts: 846
I think post #4 explains it best

Mike- what other details are you looking for?

There's also another package called DriveES Simatic. This is a library of function blocks
for communication, converting drive parameters to data blocks, blocks for displaying alarms...etc

Last edited by JRW; October 7th, 2010 at 05:51 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens drive support in canada allscott LIVE PLC Questions And Answers 2 October 21st, 2009 04:58 PM
Simatic HW config missing Drive ES/ Simotion ason LIVE PLC Questions And Answers 4 September 18th, 2009 02:04 PM
Controlling Siemens variable frequency drive Pandiani LIVE PLC Questions And Answers 4 January 13th, 2008 02:54 PM
turn on drive with siemens plc kaushik LIVE PLC Questions And Answers 0 January 7th, 2008 01:31 AM
plc5 with AB 1771-DB basic module, its urgent plz help me nileshsurya LIVE PLC Questions And Answers 6 July 20th, 2005 01:45 AM


All times are GMT -5. The time now is 08:27 AM.


.