plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old October 8th, 2010, 09:56 PM   #1
randy741985
United States
randy741985 is offline
What is a Thermocouples true range.
Looking at thermocouple ranges on the internet, they very mixed.
you will find type J measures up to 2000F other say 1500F, 1400F.
Type K 2200F to 2500F.
using Omega site it list Type J scale to 32F to 1382F
type K -328 to 2282F.
Just thought this was interesting.
thnaks for any input.
Old October 8th, 2010, 11:10 PM   #2
longshanks
United States
longshanks is offline
I worked at a firm that built wood fired burners. At the throat of the furnace, we measured the output, typically at up to 2200F. However, those TC's were encased in a 3/4" diameter Ceramic tube and the TC wire itself consisted of #8AWG TC wire. Very heavy to withstand the heat. Smaller sizes don't last very long at those temperatures. Smaller responds to temperature changes faster, but aren't as robust. They were type K and were wired to 4/20maDC converter modules. They were about 3' long to get the "head" end well outside the heating zone. We went by the Omega listings and most of the TC's were from Omega. Just FYI..
Old October 9th, 2010, 12:27 AM   #3
Tharon
United States
Tharon is offline
I would trust the Omega site. They are a big name with good data. All my thermocouple Temp vs. Voltage charts come from Omega as well.
Old October 9th, 2010, 08:03 AM   #4
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
Maybe a little over simplistic but my thought is that from a control standpoint it doesn't matter. What matters is the signal conditioner or input card you put the T/C into. This is the range usable by yourcontrol process.
Now I have never worked near the end of a range of a T/C or On a bight heat load system so there are definately other considerations and indeed the materials and type of construction could be very different even for the same letter designation and limit it more than the simple physics of the metal joint. So I guess they all could be right for their particular design.
__________________
nOrM
nOrM=Norman Dziedzic Jr.
"I decry the current tendency to seek patents on algorithms. There are better ways to earn a living than to prevent other people from making use of one's contributions to computer science." Donald Knuth
Old October 11th, 2010, 10:04 AM   #5
TConnolly
United States
TConnolly is offline
TConnolly's Avatar
The temperature rating accounts for the sheath material as well. For example a Type K T/C in a stainless steel sheath is rated to 900C, but the same T/C in an inconel sheath can be rated to 1200C, while the Type K T/C range covers up to 1370C. Atmospheric conditions should be considered as well. A type K TC can be used at higher temperatures in a vacuum or a reducing atmosphere, but should be derated when used in an oxidizing atmosphere.
__________________
True craftsmanship is only one more power tool away.
That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
Old October 12th, 2010, 08:21 AM   #6
shooter
Netherlands
shooter is offline
shooter's Avatar
The max temp is the temp nothing will happen with the sensor, like oxidation, melting etc. or the insulation will melt are become glass or something other.
it is absolute temp not the difference between the sensor and the CJ.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
Old October 12th, 2010, 08:49 AM   #7
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
It is my opinion that, as Shooter implied, the limitation on the T/C are physical destruction and not output. A T/C creates a voltage as a function of its temperature. This is non-linear, and the voltage temperature relationship varies dpending on the two metals at the hot juncion. I think that the useable range is more a function of the degree of non-linearity at various temperatures, and depending on the supplier (and the transmitter if used) the defined range will vary.
Old October 12th, 2010, 01:27 PM   #8
randy741985
United States
Thanks For the Input,
I asked because if I were scaling this in a PID what should be my max scale.
Other words if brought a T/C in as scaled for pid 0-16383 what would be
MIN. and MAX.?
Thanks In advance.
Old October 12th, 2010, 01:53 PM   #9
TConnolly
United States
TConnolly's Avatar
It would be whatever value 16383 represents in your hardware, not the value from your sensor. Eg, if your PLC TC input card specified that 16383 was 1370C then that is what you would use.
Be careful and check your specs, most T/C cards perform the linearization for you and return a value in engineering units.
__________________
Old October 12th, 2010, 07:06 PM   #10
randy741985
United States
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Trying to enhance my Siemens SCL abilities ELake20 LIVE PLC Questions And Answers 22 July 29th, 2010 05:36 AM
bitswaps in a byte SCL Combo LIVE PLC Questions And Answers 2 November 5th, 2008 08:58 AM
Functionality of the XOR Instruction? randy741985 LIVE PLC Questions And Answers 33 April 19th, 2007 12:50 PM
Momentary Push button plcnovel LIVE PLC Questions And Answers 7 March 17th, 2006 05:47 AM
one button two functions bulletin blues LIVE PLC Questions And Answers 22 March 16th, 2003 08:30 AM