analog inputs ??

hey folks ...

i have a question regarding analog inputs in s7 200 plc's
what does A+ / A- / AR means ...and how can i connect them to the sensor i mean what kind of sensor ... i herd that there 2 wire type and three wire type ?? is that correct... and please give enough details about HOW TO CONNECT the sensor to the A+,A-,AR, inputs.

thanks in advance...
kumar.
  Reply With Quote
Old November 17th, 2003, 09:10 AM   #2
jvdcande
Member
Belgium

jvdcande is offline
 
jvdcande's Avatar
 
Join Date: Apr 2002
Location: Menen
Posts: 1,960
Kumar,

the meaning of those connections is:
  • A+: analog input - positive side
  • A-: analog input - negative side
  • AR: analog input - resistor

The how to connect part is to be found in the "S7-200 Programmable Controller - System Manual" in chapters A.28 "Expansion Module EM231 Analog Input AI 3 x 12 Bits" and A.29 "Expansion Module EM235 Analog Combination AI 3 / AQ 1 x 12 Bits".

Kind regards,
__________________
Jean Pierre Vandecandelaere
Trainer nautical sector
VDAB Competentiecentrum
L. Blondeellaan 9
B-8380 Zeebrugge
Belgium
  Reply With Quote
Old November 17th, 2003, 01:45 PM   #3
kumar
Guest
 
Posts: n/a
Thumbs up

hi jvdcande,
thank you for the reply ...

i have the manual that came along with the micro win document cd
but the part which i dont understands ...which of these A+ A- AR
give the PLC analog input the 0 to 10v signal,do you mean that the
A+ , A- are the power supply from the plc to the sensor ,and the AR is the sigle returned from the sensor to the plc input ?

can you please explain more jean ..... thank you in advance.

bebst regards .kumar.
  Reply With Quote
Old November 18th, 2003, 01:24 AM   #4
jvdcande
Member
Belgium

jvdcande is offline
 
jvdcande's Avatar
 
Join Date: Apr 2002
Location: Menen
Posts: 1,960
Quote:
do you mean that the A+ , A- are the power supply from the plc to the sensor ,and the AR is the sigle returned from the sensor to the plc input ?
NO! The voltage output of the sensor has to be connected to both the A+ and the A- input as can be seen on the first figure in chapter A.28 (in my case figure A-27).

If you are using a current sensor, you have to connect the positive side of the sensor to both the resistor and the positive input of the module (shown are RC and C+) while the negative side of the sensor is to be connected to the negative input (here C-). In this way you generate a voltage across the resistor (current-to-voltage converter).

If you don't use a certain input you have to short the positive and the negative inputs (here B+ and B-) to avoid noise readings.

The internals of the module are shown in the fourth figure of that chapter (in my case figure A-30), which should clarify everything. The power supply of the sensors is not shown on these figures and has little or nothing to do with the PLC itself.

Kind regards,
__________________
Jean Pierre Vandecandelaere
Trainer nautical sector
VDAB Competentiecentrum
L. Blondeellaan 9
B-8380 Zeebrugge
Belgium
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens CPU313C Analog Inputs sherman4 LIVE PLC Questions And Answers 2 February 25th, 2005 03:02 AM
S7 300 SM331 Analog Inputs Problem; Relative DC leval of adjacent inputs. David Torrens LIVE PLC Questions And Answers 4 November 10th, 2004 10:14 AM
Analog Inputs asha6965 LIVE PLC Questions And Answers 4 August 17th, 2004 03:32 PM
Siemens Analog Inputs KA24DE LIVE PLC Questions And Answers 5 February 4th, 2004 05:05 AM


All times are GMT -5. The time now is 12:32 PM.


.