power flex 4 fault 042
hey guys,
I need urgent help. We have one power flex 4 and it is showing fault 042. checked the manual. it says check for short b etween u w phase. I cheked everythin ok. Check motor resistance. all ok. WHen i disconnect the motor the drive is increasin its frequency. Wht could be problem .Please help |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
I would recommend that you power down the drive and wait for the DC bus to bleed down. Then disconnect the motor leads from the drive and test the motor circuit for shorts to ground with a megger (megohmmeter) set for 1000V. You need at least a few megohms to ground in order for that drive to be "happy". I like to see a couple hundred megohms to ground, but in some wet environments, this is unrealistic.
Next, using a good quality ohmmeter, check the leg to leg resistance of the entire motor circuit. All three ohm readings should be the same within a couple %. It is best to perform these tests without disturbing any other connections between the drive and motor. Don't open any local disconnects or do anything else that might affect the test. If you pass all these tests, replace the drive. Since you said the drive will run (without faulting?) and ramp up to command speed with the motor disconnected, I am pretty sure there is something wrong with the motor circuit, which includes all the wiring and the motor...
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. Last edited by OkiePC; January 19th, 2011 at 04:47 PM. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: May 2010
Location: Riyadh
Posts: 309
|
thanks. i disconnected and checked resistance . all seem ok. but when i connect the drive it is faulted
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: May 2010
Location: Riyadh
Posts: 309
|
the manual says replace the drive if fault cannot be cleared
|
![]() |
![]() |
#5 |
Lifetime Supporting Member + Moderator
|
Have you tried it without the Motor connected? If so, do you still get the Fault?
Stu.....
__________________
There's never time to do it right, but there is always time to do it over! No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced. ![]() |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: May 2010
Location: Riyadh
Posts: 309
|
![]()
yes, I disconnected the wires form the drive goin to motor. The drive seems to run fine. The display shows it is increasin the frequency. I , still dont get what could be problem. I check resistance betweem UVW and ground all seem ok. I dont think it is drive problem .My electrician says it is motor which is causing this but all seems ok to me.
|
![]() |
![]() |
#7 | |
Lifetime Supporting Member + Moderator
|
Quote:
Stu....
__________________
There's never time to do it right, but there is always time to do it over! No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced. ![]() |
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Nov 2004
Location: Seattle Wa. USA
Posts: 3,680
|
I would disconnect motor leads from VFD and
1.. Megger phase to ground 2. Read phase to phase resistance with ohmeter. YOu can also put 6 or 12 VDC on motor leads read current and then calc resitance. Would want no more than 3 to 5% variation in resistance. 3. IF one and two OK then would give some thought to disconnect motor and megger line both phase to phase and phase to ground. 4. Hook motor to independent power supply and check line currents and line volt to ground at terminal box. CURIOSITY Could he hook resistors across VFD output correctly sized to compare to motor current? Waste of time since VFD runs OK unloaded or is it? Dan Bentler |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,321
|
How far in wire feet is the motor from the drive? Since this is a PF4, it's probably low hp which can be very susseptible to lead capacitance currents causing faulting.
And, follow OkiePC's advice on this exactly. Anything less than a 1000V megger is not going to help you. And use it to check phase-to-phase, not just phase-to-ground. |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Jan 2011
Location: South Carolina
Posts: 3
|
Try disconnecting the cable from the motor and cap the ends to make sure there are no problems with the cable itself.
|
![]() |
![]() |
#11 | |
Member
![]() ![]() Join Date: May 2010
Location: Riyadh
Posts: 309
|
Quote:
![]() |
|
![]() |
![]() |
#12 | |
Lifetime Supporting Member + Moderator
|
Quote:
Most MultiMeters only have a 9VDC Battery in them, which is no where near enough voltage to get the Motor Winding Insulation to break down. The higher voltage of the Megger is enough to cause the Insulation to break down if there is a weak spot. It is usually to ground, but it can also be from winding to winding. Sometimes even in the conductors from the VFD to the motor. Thus DickDV's and OkiepC's advice. A good quality Megger is indispensable when troubleshooting motor problems. Stu....
__________________
There's never time to do it right, but there is always time to do it over! No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced. ![]() |
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,321
|
bornwild, insulation is similar to the wall of a pipe. Within a range of pressures, the wall functions properly but above that range it fails and the contents of the pipe escape.
Insulation also has a maximum voltage (pressure) rating that can change as it ages. Moisture and dust also can degrade it. So, when checking the quality of the insulation, it is important to check it at or above a level where it normally operates. Since a 480VAC sinewave reaches 660V at its peak, that would be the max on a sinewave. PWM power from a drive can reach as much as 1600V momemtarily due to ringing and other high frequency effects. Thus the 1000V megger. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
AB SLC 5/03 going to fault after power failure | sns | LIVE PLC Questions And Answers | 13 | January 24th, 2010 10:52 AM |
5000 Fault | JeffKiper | LIVE PLC Questions And Answers | 15 | September 1st, 2009 03:19 PM |
RSLogix User Fault Routine | jthornton | LIVE PLC Questions And Answers | 17 | October 23rd, 2008 03:55 PM |
Flex IO communications fault | bbear | LIVE PLC Questions And Answers | 2 | December 17th, 2006 12:27 PM |
power supply fault | porky | LIVE PLC Questions And Answers | 3 | May 6th, 2004 07:56 PM |