Pressure Switch (reverse differential)
shepjess
Nov 2009
Kemmerer
If you have a Differential Pressure Switch and the "High" port goes lower pressure than the "Low" port... will it activate the switch ever? (reverse differential)
No, not the switches I have ever dealt with. But you should test it and make sure
it preforms as you want it to.
Ok thanks! I've been trying to find a diagram or drawing that shows how the insides of the thing works but have been unsuccessful thus far.
If you want to detect a both positive differential(HP > LP) and a negative differential (HP < LP) then you choose a switch with the appropriate range and calibrate it accordingly. For example if you require to measure say +50 PSI and -50 PSI then choose a switch with a range of say -75 PSI to +75 PSI. The unit would also require to be equipt with 2 switches, one to detect the -ve dp and one to detect the +ve dp. You cannot achieve both on one switch.
Or if you only want to check for a negative differential simply pipe the switch the other way round.
If you want to check for both + and - d.p. use 2 switches piped the opposite way to each other.
If your differential is going + & - don't forget to check the manufacturers data on maximum reverse pressure differentials.
Company wants a digital pressure switch panel mounted in a 8x8x6 enclosure on a machine, near where the operator stands for ease of adjustment...
1,187
Hi All, I was asked to see if I can get air pressure readings from lid weld station to an HMI ? I am not sure if this is even possible. Not sure...
3,956
i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are...
2,938
I am looking for a pressure switch with the range of up to 100 psi. Single throw, dual pole. This will be a pneumatic application. 1/2 NPT would...
3,556
Hi my friends. I have a problem with this pressure switch with analog output. I have it connected to the Balluff I/O link analog module (BNI...
1,836