AC proximity sensor
Having an issue with these: http://www.automationdirect.com/stat...inductivev.pdf
Using them to sense whether doors are opened or closed. Blue lead is AC hot, brown connected to input on a Zelio programmable relay. With no object in sensing distance, I get a bleed-through of between 80 and 85 volts, which is above the threshold of the input. Thus, the input is always on. I have a tech support opened with AD, but won't get an answer until sometime tomorrow. I was hoping someone will have a solution. I'm suspecting it'll be a series resistance...
__________________
"If you can't measure it, you can't manage it!" |
|
|
|
#2 |
|
Lifetime Supporting Member + Moderator
|
Two wire devices have to have enough current to function to decide when to turn all the way on. That's the leakage current. They aren't mechanical switches or magnetic switches being moved by something external. These are active electronic circuits looking at the amount of disturbance in the field of an inductor. They need current to operate.
Assuming you REALLY want to use these it will take a bypass resistor (this will be in parallel to the input of the Zelio, not in series) to allow that "waiting to decide to turn on" function to operate. We'll need the turn-on voltage and current of the input to help calculate the proper bypass resistor.
__________________
Controlling outputs is the PLC's way of getting its inputs to change. www.thePLCguy.com |
|
|
|
#3 |
|
Lifetime Supporting Member
|
Depending on the off-state leakage current, interposing relays may help you. I have had to add 1 watt resistors in a similar situation, but they tended to get hot for the 15 seconds that the prox switch was in the on state. Just make sure your choice of resistor is accurately calculated and sized for the right wattage if you go that route. If you choose interposing relays (my preference) make sure the relay coil requires considerably more power that the off state leakage to prevent it from overheating or false triggering.
Probably the best thing to do would be use a prox switch with built in contacts or less off-state leakage.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Inductive proximity sensor interfacing | xilog | LIVE PLC Questions And Answers | 16 | March 22nd, 2010 10:06 PM |
| How to connect AC sensor and motor to PLC | Zhen | LIVE PLC Questions And Answers | 5 | April 10th, 2009 06:47 AM |
| Proximity sensor continued | boxhead | LIVE PLC Questions And Answers | 5 | October 28th, 2005 09:46 PM |
| proximity switch as level sensor | labingtone | LIVE PLC Questions And Answers | 6 | February 13th, 2003 03:04 AM |
| proximity sensor on sugar mill | labingtone | LIVE PLC Questions And Answers | 6 | January 17th, 2003 08:14 PM |