PanelBuilder32 Pass through communications with SLC

Currently I'm running the following applications.

WinXP SP 3
RS-Linx 2.52
RS-Logix 500 8.00
Panelbuilder 32 Version 3.82

I'm trying to download to a PV1000 through a SLC 5/05.

I'm connected to the SLC via Ethernet. The SLC is connected to the Panelview via RS-232 using RS485 protocol.

I can see the PV in RS-Linx. When I try to upload from the PV it works perfectly.

I'm pretty sure I've got the SLC 5/05 configured properly for pass through and I've got my laptops IP entered into the Routing table in the SLC. I've recently performed a power off reset of the SLC since the routing table was last updated.

But when I try to download to the PV it stops at the stage

Checking Operator Terminal for Compatibility

PB32 than returns with an error code 1030.

Anybody have an idea how to get this to work?
  Reply With Quote
Old February 24th, 2011, 02:59 PM   #2
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
Oh... The PV part Number and Rev level are

2711-K10G9 PV1000 Gray Key, FRN 3.00-3.09
  Reply With Quote
Old February 24th, 2011, 03:12 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 8,573
You might have to delete the application in the PanelView terminal before it will accept a download over the Passthrough route.

Be sure also that the Passthrough Link ID's for the Ethernet port and Channel 0 port of the SLC-5/05 are different.

PanelBuilder32's support for the various "passthrough" implementations over the years has been spotty. I try to keep flash memory cards around just for this sort of thing.
  Reply With Quote
Old February 25th, 2011, 06:35 AM   #4
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
In RS-Logix 500, The pass through link for the ethernet is 2. the pass through link for the DH485 is 1.

My Passrhru Routing table has Current Mappings

0: Local 5/05
1: 10.255.3.108 ( my lapttops IP )

The SLC 5/05 is at IP 10.255.30.238

I don't have the appropriate flash card to download to the Panelview and I'm not sure how to erase the panelview. Even if I did, I'm a little worried about doing that because if I still can't download to it, I may shut down a working machine.

If I do erase the panelview, what mode will that put the RS-232 ports into?

If they default to RS-232 mode, I should be able to communicate via the DF1 driver direct?

Is there any Link ID stored in the Panelview itself in the panelbuilder software.

Since I can upload from the Panvelview, I should be able to determine that.
  Reply With Quote
Old February 25th, 2011, 09:02 AM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,496
The memory card is the fastest and safest way to perform the download in my opinion. You don't have to erase the existing application to do this. If you get to the config screen, and find the new application on the memory card, the panelview will check its compatibility before erasing what it already has loaded. If it doesn't like it, you can go right back to run mode with no harm done.

I 2nd Ken's recommendation to get an ATA style PCMCIA memory card (or an adapter and a compactflash card) and go that route.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."
  Reply With Quote
Old February 25th, 2011, 09:27 AM   #6
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
Trying to get that memory card in my plant is going to be painful. Was hoping to avoid that.
  Reply With Quote
Old February 25th, 2011, 09:33 AM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,515
There are some KB articles on the subject. You will need a tech connect contract ( I don't have one) to view them though.
I.D. 17573, I.D. 19851, I.D. 4129.

http://rockwellautomation.custhelp.c...13025/search/1
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 25th, 2011, 09:49 AM   #8
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
Sadly, I don't have a tech connect contract... I'll see if I can get that info through my distributor.
  Reply With Quote
Old February 28th, 2011, 09:06 AM   #9
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
This gets weirder and weirder.

We have another Panel View... a PV 550 on a machine right next to the machine with the PV 1000. Both machines have their own separate SLC 5/05.

A few weeks ago, we had a engineer from the vendor for that machine, download using Ethernet pass through a SLC 5/05 to the PV 550 on DH485 protocol to the other machine. I know it worked, because I set up the pass through for that engineer.

When I tried to download to that same PV 550 today, I had the same issue, I could upload, but not download. I've set the SLC 5/05 in the other machine to point at the IP address of my laptop.

I also tried, moving my laptop over next to the two machines and plugging into the same ethernet port that had worked properly a few weeks ago.

Please don't say the solution is in a knowledge base document, since I have no way to access those documents.
  Reply With Quote
Old February 28th, 2011, 10:08 AM   #10
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,496
What is the OS in the 5/05? One technote says it needs to be OS501

What are the Passthrough Link IDs of all the 5/05s on the network? Each channel of each SLC must have a unique Passthrough Link ID.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."
  Reply With Quote
Old February 28th, 2011, 10:11 AM   #11
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
The SLC 5/05 on the one machine is OS501

In the Processor Status File I've got.

OS Cat Number 501
OS Series A
OS FRN 5

Processor Cat Number 551
Processor Series A
Processor FRN 1
  Reply With Quote
Old February 28th, 2011, 10:13 AM   #12
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
The passthrough link IDs are

Channel 1 Passthru Link ID 2

Channel 0 Passthru Link ID 1

Do these have to be unique for each SLC on the Ethernet Network?

The SLCs are on the same Ethernet network, but seperate DH485 networks.
  Reply With Quote
Old February 28th, 2011, 10:33 AM   #13
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,496
Quote:
Originally Posted by Barry Kirk View Post
The passthrough link IDs are

Channel 1 Passthru Link ID 2

Channel 0 Passthru Link ID 1

Do these have to be unique for each SLC on the Ethernet Network?
Yes, according to one technote. They show two 5/05 ch. config screens with Passthgough Link IDs of 2,1,4,3

They claim that if you have duplicates on different channels or different SLCs, that you'll see the Panelview in RSwho but "passthrough will fail"...sounds like your symptoms to me.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."

Last edited by OkiePC; February 28th, 2011 at 10:35 AM.
  Reply With Quote
Old February 28th, 2011, 12:44 PM   #14
Barry Kirk
Lifetime Supporting Member
United States

Barry Kirk is offline
 
Join Date: Mar 2007
Location: York, PA
Posts: 54
I tried changing the Link IDs in the channel configuration of both channel 0 and channel 1. It did interrupt the ability of the Panelview to communicate with the SLC.

Next, I tried disconnecting the SLC from the plant network, and hooking my laptop up to the SLC with my own switch.

Changed, my laptop to the same subnet as the SLC, since it was now a local network.

Changed the Routing table to the new laptop IP address and Power cycled the control enclosure.

Still unable to download to the panelview.

I'm wondering if maybe our IT department installed some virus blocker on my laptop that is blocking this communication.
  Reply With Quote
Old February 28th, 2011, 01:07 PM   #15
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,496
Go get yourself one of these:

http://www.amazon.com/Transcend-Card.../ref=pd_cp_e_3

and a pack of these:

http://www.amazon.com/SanDisk-128-MB...8919993&sr=1-5

and be done with it



Paul
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/03 Pass through Comms Kabir LIVE PLC Questions And Answers 3 August 29th, 2010 08:45 PM
SLC 500 Ethernet Setup JSPLC LIVE PLC Questions And Answers 3 June 1st, 2010 04:15 PM
SLC 5/05 Pass Through to 485 PV Bob8417 LIVE PLC Questions And Answers 2 December 8th, 2008 03:18 PM
SLC 500/RSLogix 500 Communications kerch LIVE PLC Questions And Answers 25 October 15th, 2006 12:19 AM
SLC 5/05 pass through to DH485 Jezz LIVE PLC Questions And Answers 10 November 17th, 2004 05:35 AM


All times are GMT -5. The time now is 01:47 AM.


.