PanelBuilder32 Pass through communications with SLC
Currently I'm running the following applications.
WinXP SP 3 RS-Linx 2.52 RS-Logix 500 8.00 Panelbuilder 32 Version 3.82 I'm trying to download to a PV1000 through a SLC 5/05. I'm connected to the SLC via Ethernet. The SLC is connected to the Panelview via RS-232 using RS485 protocol. I can see the PV in RS-Linx. When I try to upload from the PV it works perfectly. I'm pretty sure I've got the SLC 5/05 configured properly for pass through and I've got my laptops IP entered into the Routing table in the SLC. I've recently performed a power off reset of the SLC since the routing table was last updated. But when I try to download to the PV it stops at the stage Checking Operator Terminal for Compatibility PB32 than returns with an error code 1030. Anybody have an idea how to get this to work? |
|
|
|
#2 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
Oh... The PV part Number and Rev level are
2711-K10G9 PV1000 Gray Key, FRN 3.00-3.09 |
|
|
|
#3 |
|
Lifetime Supporting Member + Moderator
|
You might have to delete the application in the PanelView terminal before it will accept a download over the Passthrough route.
Be sure also that the Passthrough Link ID's for the Ethernet port and Channel 0 port of the SLC-5/05 are different. PanelBuilder32's support for the various "passthrough" implementations over the years has been spotty. I try to keep flash memory cards around just for this sort of thing. |
|
|
|
#4 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
In RS-Logix 500, The pass through link for the ethernet is 2. the pass through link for the DH485 is 1.
My Passrhru Routing table has Current Mappings 0: Local 5/05 1: 10.255.3.108 ( my lapttops IP ) The SLC 5/05 is at IP 10.255.30.238 I don't have the appropriate flash card to download to the Panelview and I'm not sure how to erase the panelview. Even if I did, I'm a little worried about doing that because if I still can't download to it, I may shut down a working machine. If I do erase the panelview, what mode will that put the RS-232 ports into? If they default to RS-232 mode, I should be able to communicate via the DF1 driver direct? Is there any Link ID stored in the Panelview itself in the panelbuilder software. Since I can upload from the Panvelview, I should be able to determine that. |
|
|
|
#5 |
|
Lifetime Supporting Member
|
The memory card is the fastest and safest way to perform the download in my opinion. You don't have to erase the existing application to do this. If you get to the config screen, and find the new application on the memory card, the panelview will check its compatibility before erasing what it already has loaded. If it doesn't like it, you can go right back to run mode with no harm done.
I 2nd Ken's recommendation to get an ATA style PCMCIA memory card (or an adapter and a compactflash card) and go that route.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
|
|
#6 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
Trying to get that memory card in my plant is going to be painful. Was hoping to avoid that.
|
|
|
|
#7 |
|
Lifetime Supporting Member
|
There are some KB articles on the subject. You will need a tech connect contract ( I don't have one) to view them though.
I.D. 17573, I.D. 19851, I.D. 4129. http://rockwellautomation.custhelp.c...13025/search/1
__________________
Mickey If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else. ----- Chinese Proverb |
|
|
|
#8 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
Sadly, I don't have a tech connect contract... I'll see if I can get that info through my distributor.
|
|
|
|
#9 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
This gets weirder and weirder.
We have another Panel View... a PV 550 on a machine right next to the machine with the PV 1000. Both machines have their own separate SLC 5/05. A few weeks ago, we had a engineer from the vendor for that machine, download using Ethernet pass through a SLC 5/05 to the PV 550 on DH485 protocol to the other machine. I know it worked, because I set up the pass through for that engineer. When I tried to download to that same PV 550 today, I had the same issue, I could upload, but not download. I've set the SLC 5/05 in the other machine to point at the IP address of my laptop. I also tried, moving my laptop over next to the two machines and plugging into the same ethernet port that had worked properly a few weeks ago. Please don't say the solution is in a knowledge base document, since I have no way to access those documents. |
|
|
|
#10 |
|
Lifetime Supporting Member
|
What is the OS in the 5/05? One technote says it needs to be OS501
What are the Passthrough Link IDs of all the 5/05s on the network? Each channel of each SLC must have a unique Passthrough Link ID.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
|
|
#11 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
The SLC 5/05 on the one machine is OS501
In the Processor Status File I've got. OS Cat Number 501 OS Series A OS FRN 5 Processor Cat Number 551 Processor Series A Processor FRN 1 |
|
|
|
#12 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
The passthrough link IDs are
Channel 1 Passthru Link ID 2 Channel 0 Passthru Link ID 1 Do these have to be unique for each SLC on the Ethernet Network? The SLCs are on the same Ethernet network, but seperate DH485 networks. |
|
|
|
#13 | |
|
Lifetime Supporting Member
|
Quote:
They claim that if you have duplicates on different channels or different SLCs, that you'll see the Panelview in RSwho but "passthrough will fail"...sounds like your symptoms to me.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." Last edited by OkiePC; February 28th, 2011 at 10:35 AM. |
|
|
|
|
#14 |
|
Lifetime Supporting Member
![]() Join Date: Mar 2007
Location: York, PA
Posts: 54
|
I tried changing the Link IDs in the channel configuration of both channel 0 and channel 1. It did interrupt the ability of the Panelview to communicate with the SLC.
![]() Next, I tried disconnecting the SLC from the plant network, and hooking my laptop up to the SLC with my own switch. Changed, my laptop to the same subnet as the SLC, since it was now a local network. Changed the Routing table to the new laptop IP address and Power cycled the control enclosure. Still unable to download to the panelview. ![]() I'm wondering if maybe our IT department installed some virus blocker on my laptop that is blocking this communication. |
|
|
|
#15 |
|
Lifetime Supporting Member
|
Go get yourself one of these:
http://www.amazon.com/Transcend-Card.../ref=pd_cp_e_3 and a pack of these: http://www.amazon.com/SanDisk-128-MB...8919993&sr=1-5 and be done with it ![]() Paul
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| SLC 5/03 Pass through Comms | Kabir | LIVE PLC Questions And Answers | 3 | August 29th, 2010 08:45 PM |
| SLC 500 Ethernet Setup | JSPLC | LIVE PLC Questions And Answers | 3 | June 1st, 2010 04:15 PM |
| SLC 5/05 Pass Through to 485 PV | Bob8417 | LIVE PLC Questions And Answers | 2 | December 8th, 2008 03:18 PM |
| SLC 500/RSLogix 500 Communications | kerch | LIVE PLC Questions And Answers | 25 | October 15th, 2006 12:19 AM |
| SLC 5/05 pass through to DH485 | Jezz | LIVE PLC Questions And Answers | 10 | November 17th, 2004 05:35 AM |