AB PLC 5 Processor fault

We have a AB PLC 5/??? showing fault LED RED ON. Operator does not seem to be able to change set point on PIDs and PLC is not responding to these setpoint changes or to the ON/OFF commands from HMI display. The comms are still working because when we removed the comm cable from the back of the HMI PC, we lost what ever data were diplayed on the screen.When we put back the cable, data lost came back on the screen. Technican told me that they repalced the Processor battery and we switched from the run mode to Prog and remote but no success.
  Reply With Quote
Old March 13th, 2011, 07:19 AM   #2
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,112
Quote:
Originally Posted by mureed View Post
We have a AB PLC 5/??? showing fault LED RED ON. Operator does not seem to be able to change set point on PIDs and PLC is not responding to these setpoint changes or to the ON/OFF commands from HMI display. The comms are still working because when we removed the comm cable from the back of the HMI PC, we lost what ever data were diplayed on the screen.When we put back the cable, data lost came back on the screen. Technican told me that they repalced the Processor battery and we switched from the run mode to Prog and remote but no success.
The PLC has a "Major Fault", and you will need to get online and investigate what that fault is.

Because you can see data, I don't think you have lost the program.

Short-term solution if you can't get online.... try resetting the Major Fault by toggling the keyswitch back and forth several times through all 3 switch positions rapidly - this may clear the fault and allow the PLC to re-start.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old March 13th, 2011, 11:37 AM   #3
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 1,939
Quote:
Originally Posted by daba View Post
Short-term solution if you can't get online.... try resetting the Major Fault by toggling the keyswitch back and forth several times through all 3 switch positions rapidly - this may clear the fault and allow the PLC to re-start.
Watching the LED's on the newer Logix platform, it appears that one key switch cycle (run > program > run) will clear the fault, then the next cycle puts it back into run mode. Of course, this will not work if the fault condition remains.

The trick is (as daba mentions) going to all 3 positions, program to remote just leaves it in program mode, it has to go back to run mode. Doing it 3 times will make sure that you did at least 2 complete cycles.
  Reply With Quote
Old March 13th, 2011, 06:10 PM   #4
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,112
But of course, the PLC has major faulted before, it may well do it again immediately, tomorrow, next week, in 6 months time.....

It will be far better to find out NOW what the fault is and deal with it. Resetting the fault (and its info) now, will make it very hard to remove the cause of the fault.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB PLC 5/60 & 6200 (v4.41) software cywa LIVE PLC Questions And Answers 16 August 8th, 2010 06:14 PM
Comment list ab plc indra LIVE PLC Questions And Answers 1 March 31st, 2009 01:59 AM
AB 825P to Yokogawa PLC vnz_ph LIVE PLC Questions And Answers 2 November 14th, 2008 02:48 AM
AB PLC Processors Unregistered LIVE PLC Questions And Answers 7 June 23rd, 2005 09:33 AM
Password in Micrologix1200 AB PLC krunalc LIVE PLC Questions And Answers 6 September 1st, 2002 09:33 AM


All times are GMT -5. The time now is 05:58 AM.


.