ge fanuc 90-30 programing problem
Hello Everybody,
I AM USING A GE FANUC 90-30 PLC, VERSAPRO TO WRITE THE LADDER DIAGRAM, THE PROBLEM IS THAT I HAVE AN OLD LADDER PRINTED ON PAPERS, I WANT TO WRITE IT ON VERSAPRO, THIS LADDER IS ALSO FOR GE FANUC 90-30, BUT WRITTEN USING ANOTHER SOFTWARE, THERE ARE SOME LADDER SYMBOLS THAT I DONOT UNDERSTAND WHAT IS THE CORRESPONDING SYMBOLS TO THEM IN VERSAPRO AS : -(M)- , -(SM)- , -(RM)- ONE LAST THING, I NEED TO DOWNLOAD Ge Fanuc Proficy 5.00 Cimplicity Machine Edition, IF ANYONE KNOWS DOWNLOAD LINKS, IT WILL REALLY HELP. THANKS FOR YOUR TIME, I REALLY APPRECIATE YOUR HELP. Last edited by mamadoo95; March 23rd, 2011 at 03:27 PM. |
|
|
|
#2 |
|
Lifetime Supporting Member + Moderator
|
The older program was written using Logicmaster software. The instructions that are confusing you point out a major difference (and in my opinion a poor design choice) between Versa Pro and Logicmaster.
The Logicmaster intructions -(M)-, -(SM)-, and -(RM)- denote retentive instructions. The corresponding -( )-, -(S)-, and -(R)- instructions are non-retentive. Versa Pro does not use the -(M)-, -(SM)-, and -(RM)- instructions. Instead when using Versa Pro you declare each individual variable to be either retentive or non-retentive. And here's where they made a boneheaded move. All Versa Pro %M and %Q variables are retentive by default. If you don't want them to be retentive you must change from the default state. The default state should have been non-retentive. When they came out with Proficy Machine Edition, they corrected their blunder and went back to using -(M)-, -(SM)-, and -(RM)- instructions. I don't know of any legitimate site where you can download Machine Edition. |
|
|
|
#3 |
|
Member
![]() Join Date: Mar 2011
Location: cairo
Posts: 18
|
thanks alot steve , so is there a link to download logic master 90..
|
|
|
|
#4 |
|
Lifetime Supporting Member + Moderator
|
The Versa Pro CD includes Logicmaster.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| GE Fanuc online problem | Mr.Beaver | LIVE PLC Questions And Answers | 2 | August 17th, 2010 12:01 PM |
| ge fanus 90 30 comm problem | johnplouffe | LIVE PLC Questions And Answers | 3 | December 17th, 2006 08:43 PM |
| GE Fanuc LM1F | bchilders | LIVE PLC Questions And Answers | 2 | May 26th, 2006 12:46 PM |
| GE Fanuc PLC Axis Module Problem | ManiDuraiswamy | LIVE PLC Questions And Answers | 1 | September 16th, 2003 07:54 AM |
| Fanuc Robot Problem | cdlove23 | LIVE PLC Questions And Answers | 13 | August 16th, 2002 09:09 PM |