plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old June 13th, 2011, 02:34 PM   #1
WrongWay
United States
WrongWay is offline
WrongWay's Avatar
2-wire ac NC proximity sensor
These are not used very often I know. I do not have a PLC on this piece of equipemnt that I am attempting to install a monitoring/alarm circuit in. My intent is to use this prox to monitor for weld wire presence and to switch the load to a timer relay when no wire is detected. When the relay times out at 11 seconds it will latch a relay that sounds/lights an alarm condition that requires a key reset to unlatch. I installed the prox using a micro qd with #3 suppling load(120VAC) and #2 to the timer relay. Sometimes the prox doesn't light at all and other times after cycling power I have gotten a flash on/off from the red LED indicating a short circuit. Also, the micro qd cable I have the red/white to load and the red/black to the relay
How far off the track am I?
__________________
John
In the land of plenty, conservation is a foreign word.
Old June 13th, 2011, 02:44 PM   #2
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Is your "micro qd" some type of smart relay or electronic relay?
You have to be careful about what type and size of load you use with a prox switch. Not all prox switches will successfully switch all different loads (relays). DC relays can be difficult, as are some electronic relays.
Old June 13th, 2011, 02:45 PM   #3
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
If it's a two wire AC prox, then you should be able to wire it either way with the same results. I have seen some that also include a 3rd connection for ground.
If the prox is directly feeding the coil of a relay, then its indicator should always function unless it is damaged. Perhaps the prox was shorted or the load of the relay coil is too much for it?
Can you post a link to the part(s) you're using?
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old June 13th, 2011, 02:51 PM   #4
bkottaras
United States
bkottaras is offline
Ive seen both.
I agree with Paul.
Chances are that the load of the relay is too much for the prox. The prox is primarily used as a signal/feedback device and it is not capable of load switching. Check the prox specs.
Old June 13th, 2011, 02:52 PM   #5
keithkyll
United States
keithkyll is offline
A 2 wire prox needs a good size load to power it's internal electronics. Check specs. I believe it's minimum 20 mA or so. Give it a load like an incandescent lamp.
Old June 13th, 2011, 02:53 PM   #6
Brijm
United States
Brijm is offline
Brijm's Avatar
Is it an electronic Timer? It may have too high of a resistance (minimum current to power the prox) Try putting a coil relay in between, or us a resistor to draw a few mA.
__________________
Brian
Old June 13th, 2011, 03:57 PM   #7
WrongWay
United States
WrongWay is offline
WrongWay's Avatar
micro qd is a type of "quick disconnet" that has 3 terminals and 2 keyways to assure proper mating
__________________
John
Old June 13th, 2011, 04:20 PM   #8
WrongWay
United States
WrongWay is offline
WrongWay's Avatar
Thank you for the replies, both parts are AB.
The prox is a 871TM-B4C12-R3,switches up to 200ma. The timing relay is a 700-HRP42TA17. I grabbed the timer I had on the shelf and did not qualify it fully, it appears that it requires quite a load to energize it. As for the load to the prox, I put a 250ma AGC fuse inline before the prox.
__________________
John
Old June 13th, 2011, 04:47 PM   #9
keithkyll
United States
The prox needs a minimum load of 5 mA. There isn't a load spec on the timer datasheet. I suspect it might be small. Looked at similar Fuji timers from AD. They are only 10 VA. You should use a relay that draws at least 5 mA in between.
Old June 14th, 2011, 06:49 AM   #10
WrongWay
United States
WrongWay is offline
WrongWay's Avatar
I threw in a omron MY2 between the prox and timing relay. I was trying to minimalize the amount of components in the circuit by landing directly on the timer. Of course, no I can just use a NO prox. I guess what I learn here is that is a certain item is rarely used, its probably that there is a better, more mainstream way of doing it.
thanks again
__________________
John
Old June 14th, 2011, 11:20 AM   #11
tommy23t
United States
tommy23t is offline
tommy23t's Avatar
I would put a 10K ohm 2W resistor across the coil of the timer. AC switches need a minimum load to stay "on", this is common when using solid state timers to turn on a load.
tommy23t
Old June 14th, 2011, 11:28 AM   #12
keithkyll
United States
That's a common value, good for most applications. The problem is it will run a little hot.
For this application, 22K will give us a little over 5 mA, enough to meet the prox spec. Watts drops down to .6 Watts.
Old June 14th, 2011, 03:39 PM   #13
WrongWay
United States
WrongWay is offline
WrongWay's Avatar
I was able to test this today with no problems making the latch. The prox energizes the coil on a omron MY2 relay which closes a circuit to the timer. I'm probably missing something, but isn't there plenty of amperage to power that coil?
__________________
John
Old June 14th, 2011, 03:42 PM   #14
keithkyll
United States
Coil draws 9.2 mA at 120V. Well within your range of 5-250 mA for the prox.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
4 wire proximity sensor to plc input jeii LIVE PLC Questions And Answers 9 March 14th, 2011 02:22 AM
AC proximity sensor rguimond LIVE PLC Questions And Answers 2 February 13th, 2011 08:37 PM
Inductive proximity sensor interfacing xilog LIVE PLC Questions And Answers 16 March 22nd, 2010 10:06 PM
How to connect AC sensor and motor to PLC Zhen LIVE PLC Questions And Answers 5 April 10th, 2009 06:47 AM
proximity sensor on sugar mill labingtone LIVE PLC Questions And Answers 6 January 17th, 2003 08:14 PM