2-wire ac NC proximity sensor

These are not used very often I know. I do not have a PLC on this piece of equipemnt that I am attempting to install a monitoring/alarm circuit in. My intent is to use this prox to monitor for weld wire presence and to switch the load to a timer relay when no wire is detected. When the relay times out at 11 seconds it will latch a relay that sounds/lights an alarm condition that requires a key reset to unlatch. I installed the prox using a micro qd with #3 suppling load(120VAC) and #2 to the timer relay. Sometimes the prox doesn't light at all and other times after cycling power I have gotten a flash on/off from the red LED indicating a short circuit. Also, the micro qd cable I have the red/white to load and the red/black to the relay
How far off the track am I?
__________________
John
In the land of plenty, conservation is a foreign word.
  Reply With Quote
Old June 13th, 2011, 02:44 PM   #2
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 8,696
Is your "micro qd" some type of smart relay or electronic relay?

You have to be careful about what type and size of load you use with a prox switch. Not all prox switches will successfully switch all different loads (relays). DC relays can be difficult, as are some electronic relays.

Last edited by Lancie1; June 13th, 2011 at 02:50 PM.
  Reply With Quote
Old June 13th, 2011, 02:45 PM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,645
If it's a two wire AC prox, then you should be able to wire it either way with the same results. I have seen some that also include a 3rd connection for ground.

If the prox is directly feeding the coil of a relay, then its indicator should always function unless it is damaged. Perhaps the prox was shorted or the load of the relay coil is too much for it?

Can you post a link to the part(s) you're using?
__________________
Justice is a nice ideal, but don't be surprised nor hurt when it is denied you.

It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."
  Reply With Quote
Old June 13th, 2011, 02:51 PM   #4
bkottaras
Member
United States

bkottaras is offline
 
Join Date: Oct 2005
Location: Chicago
Posts: 1,411
Quote:
Originally Posted by OkiePC View Post
If it's a two wire AC prox, then you should be able to wire it either way with the same results. I have seen some that also include a 3rd connection for ground.

If the prox is directly feeding the coil of a relay, then its indicator should always function unless it is damaged. Perhaps the prox was shorted or the load of the relay coil is too much for it?

Can you post a link to the part(s) you're using?
Ive seen both.
I agree with Paul.
Chances are that the load of the relay is too much for the prox. The prox is primarily used as a signal/feedback device and it is not capable of load switching. Check the prox specs.
  Reply With Quote
Old June 13th, 2011, 02:52 PM   #5
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,302
A 2 wire prox needs a good size load to power it's internal electronics. Check specs. I believe it's minimum 20 mA or so. Give it a load like an incandescent lamp.
  Reply With Quote
Old June 13th, 2011, 02:53 PM   #6
Brijm
Lifetime Supporting Member
United States

Brijm is offline
 
Brijm's Avatar
 
Join Date: May 2006
Location: St. Marys, PA
Posts: 609
Is it an electronic Timer? It may have too high of a resistance (minimum current to power the prox) Try putting a coil relay in between, or us a resistor to draw a few mA.
__________________
Brian
  Reply With Quote
Old June 13th, 2011, 03:57 PM   #7
WrongWay
Member
United States

WrongWay is offline
 
WrongWay's Avatar
 
Join Date: May 2011
Location: Sturgis,Mi
Posts: 31
micro qd is a type of "quick disconnet" that has 3 terminals and 2 keyways to assure proper mating
__________________
John
In the land of plenty, conservation is a foreign word.
  Reply With Quote
Old June 13th, 2011, 04:20 PM   #8
WrongWay
Member
United States

WrongWay is offline
 
WrongWay's Avatar
 
Join Date: May 2011
Location: Sturgis,Mi
Posts: 31
Thank you for the replies, both parts are AB.
The prox is a 871TM-B4C12-R3,switches up to 200ma. The timing relay is a 700-HRP42TA17. I grabbed the timer I had on the shelf and did not qualify it fully, it appears that it requires quite a load to energize it. As for the load to the prox, I put a 250ma AGC fuse inline before the prox.
__________________
John
In the land of plenty, conservation is a foreign word.
  Reply With Quote
Old June 13th, 2011, 04:47 PM   #9
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,302
The prox needs a minimum load of 5 mA. There isn't a load spec on the timer datasheet. I suspect it might be small. Looked at similar Fuji timers from AD. They are only 10 VA. You should use a relay that draws at least 5 mA in between.
  Reply With Quote
Old June 14th, 2011, 06:49 AM   #10
WrongWay
Member
United States

WrongWay is offline
 
WrongWay's Avatar
 
Join Date: May 2011
Location: Sturgis,Mi
Posts: 31
I threw in a omron MY2 between the prox and timing relay. I was trying to minimalize the amount of components in the circuit by landing directly on the timer. Of course, no I can just use a NO prox. I guess what I learn here is that is a certain item is rarely used, its probably that there is a better, more mainstream way of doing it.
thanks again
__________________
John
In the land of plenty, conservation is a foreign word.
  Reply With Quote
Old June 14th, 2011, 11:20 AM   #11
tommy23t
Member
United States

tommy23t is offline
 
tommy23t's Avatar
 
Join Date: Nov 2003
Location: New Jersey
Posts: 136
I would put a 10K ohm 2W resistor across the coil of the timer. AC switches need a minimum load to stay "on", this is common when using solid state timers to turn on a load.
tommy23t
  Reply With Quote
Old June 14th, 2011, 11:28 AM   #12
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,302
That's a common value, good for most applications. The problem is it will run a little hot.
For this application, 22K will give us a little over 5 mA, enough to meet the prox spec. Watts drops down to .6 Watts.
  Reply With Quote
Old June 14th, 2011, 03:39 PM   #13
WrongWay
Member
United States

WrongWay is offline
 
WrongWay's Avatar
 
Join Date: May 2011
Location: Sturgis,Mi
Posts: 31
I was able to test this today with no problems making the latch. The prox energizes the coil on a omron MY2 relay which closes a circuit to the timer. I'm probably missing something, but isn't there plenty of amperage to power that coil?
__________________
John
In the land of plenty, conservation is a foreign word.
  Reply With Quote
Old June 14th, 2011, 03:42 PM   #14
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,302
Coil draws 9.2 mA at 120V. Well within your range of 5-250 mA for the prox.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
4 wire proximity sensor to plc input jeii LIVE PLC Questions And Answers 9 March 14th, 2011 02:22 AM
AC proximity sensor rguimond LIVE PLC Questions And Answers 2 February 13th, 2011 08:37 PM
Inductive proximity sensor interfacing xilog LIVE PLC Questions And Answers 16 March 22nd, 2010 10:06 PM
How to connect AC sensor and motor to PLC Zhen LIVE PLC Questions And Answers 5 April 10th, 2009 06:47 AM
proximity sensor on sugar mill labingtone LIVE PLC Questions And Answers 6 January 17th, 2003 08:14 PM


All times are GMT -5. The time now is 03:55 PM.


.