How to calculate the Accuracy of Pressure Transmitter and rtd's
Hi friends;
I done the calibration of pressure transmitters and rtd's.
I give one example of data for both plz guide me how i calculate the accuracy of the transmitter and RTD's.
Pressure transmitter:
Range 0 to 200" w.c
signal applied reading
0 0
50 51
100 101
150 151
200 201
The error is 1"w.c how i calculate the accuracy?
RTD's example
32 32
100 101
150 152
200 203
Now how i calculate the RTD accuracy while i used PT100 RTD.
PLz help me?
Old June 19th, 2011, 08:55 AM   #2
danw
United States
danw is offline
danw's Avatar
For the pressure transmitter, the range is 0-200" for a span of 200".
An error of 1" over 200" is 1/200 or 0.5%
For the RTD, the range is 32-200 or 168
An error of 3 over a span of 168 is 3/168 or 1.8%
Old June 19th, 2011, 09:24 AM   #3
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
Just make sure that whomever you give the information to understands what you are giving them.
Other things that effect overall accuracy are temperature and hysteresis. Some manufacturers lump all effects into a single value, others list them all separately. Just make sure you give enough information with your accuracy so the person using it can use the information properly.
__________________
nOrM
nOrM=Norman Dziedzic Jr.
"I decry the current tendency to seek patents on algorithms. There are better ways to earn a living than to prevent other people from making use of one's contributions to computer science." Donald Knuth
Old June 19th, 2011, 11:54 AM   #4
JoeFin
United States
JoeFin is offline
Accuracy = (Deviation / Span ) * 100
Deviation = Expected Value - Actual Value
Since you said "Transmitter" and "Data" be sure you differentiate between sensor values and analog output values. That and 5 point checks up and down and you should be good
Old June 21st, 2011, 03:06 AM   #5
shooter
Netherlands
shooter is offline
shooter's Avatar
calcs by danw are correct, however you also have the accuracy of the testsignal and its reading.
if you are using steaming water the pressure of the air is important, just like with pressure readings.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump