Hi all.
I am kinda new at the RSNetWorx thing, but know just a little. The probelm I have is That I am setting up a new Network with only 2 nodes. One is the 1769_SDN scanner and the other a 3rd party Servo Drive (Control techniques). The problem I have is that I am trying to configure the SDN scanner with RSNetWorx, When I go "Online" to the network it sees the 1769-SDN scanner but says it is not recognised. I have loaded the EDS files for that SDN scanner. But still says not recognised. If I double click on the Not Recognised device, it says it is not registered. So I try registering it again with the EDS files, but still says not recognised. Is it because I am running a old version of RSNetWorx. and not a new version. I have version "Revision Product" 3.21.00 (Build 27) The SDN scanner has Major Rev 4 and Minor Rev 2. I have double checked the EDS fiels and am certain I am loading the correct EDS files, (infact I loaded all 4 files to make sure) Do I need a New Version of RSNetWorx, maybe version 10 that is out? Hopefully I can use it as a Demo version as I don't need the full version. (just useing 2 nodes) Thanx |
|
|
|
#2 |
|
Member
![]() Join Date: Oct 2010
Location: Milton keynes
Posts: 9
|
Ah Thought I'd just mention that the RSNetWorx network sees the Control techniques drive and I maped it and everything. Just trying to do the same with the SDN scanner.
|
|
|
|
#3 |
|
Member
![]() Join Date: Oct 2010
Location: Milton keynes
Posts: 9
|
After trying to register the SDN, I get this Message:
The Following error occurred parsing the EDS file: ' Invalid entry in memory Table's'. Contact your vendor for an updated EDS file. Now I have downloaded the newest EDS file from the AB website,and this is that is the message I get, so I know I have the correct EDS file. You think it is the RSNetWorx Software I need to upgrade ? |
|
|
|
#4 |
|
Lifetime Supporting Member + Moderator
|
RSNetworx v3 was released long before the CompactLogix existed, so it's probably choking on the 32-bit definition for the scanner's I/O table. It's probably more than ten years out of date.
Get RSNetworx for DeviceNet v10. The software still works in "demo mode" for nodes 0 through 5. You'll have to get it through your RA distributor; it's not a free download, because the demo mode was only distributed as part of Starter Kits. |
|
|
|
#5 |
|
Member
![]() Join Date: Oct 2010
Location: Milton keynes
Posts: 9
|
Thank You Ken, I'll see if I can get a v10 from my distributor. I will post back if al works.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| b & r version conflict | schrader | LIVE PLC Questions And Answers | 10 | February 15th, 2011 04:54 PM |
| Version Problem for Rockwell E3 module | Eric Le Yin | LIVE PLC Questions And Answers | 4 | January 22nd, 2009 01:05 AM |
| RSLogix 5000 Version Conflict | sadanand_kulkarni | LIVE PLC Questions And Answers | 5 | January 18th, 2009 12:57 AM |
| rsview32, using newer version of works editor with older version of runtime | diat150 | LIVE PLC Questions And Answers | 7 | February 11th, 2008 12:27 PM |
| Proworx Demo Vs. Full Version | CONTROLTESTGUY | LIVE PLC Questions And Answers | 2 | January 25th, 2006 01:45 PM |