plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old September 13th, 2011, 04:42 PM   #1
ndecks
United States
ndecks is offline
Motor Hz Calculations
I need some help. I am programming a spice auger system. I want to base how fast the auger should run on the required spice (gram/min, value known). I have my auger motor, I have all the name plate data on the motor.
So I know:
My motor runs 60Hz at 2500 rpm, it has a 10:1 reducer
I know what my gram/revolution needs to be for my auger. For this case 8.16 g/rev
I also know how much spice I need to run. The value is in gram/min.
What I need is to know the calculation to get to how many Hz to send to my motor to run.
Old September 13th, 2011, 04:59 PM   #2
jrwb4gbm
United States
jrwb4gbm is offline
I'm curious, is this a universal motor with brushes? That is the only motor type that I've seen run 2500 RPM at 60 Hz. I'm more familiar with regular AC motors at 60 Hz. that run either approx. 3550 RPM (two pole construction) or approx. 1725 RPM (4 pole construction).
In any event, at max gearbox output RPM (250) multiply by the grams per Rev. (8.16) to get the max grams/min. (2040). That would also = your motor max RPM (2500). Divide the 2500 rev. by 60 Hz. Each Hz. would = 34 gram/min. As you can see, this is not a formula but an attempt to explain the math. I hope this helps a little.
Old September 13th, 2011, 05:10 PM   #3
Tharon
United States
Tharon is offline
So you have:
8.16 Grams/Revolution of your ball screw.
Motor speed, 2500 Revolutions/Minute (60HZ)
10:1 reduction
You want:
Grams/Minute of spice output
At 60HZ, your ball screw is spinning at 2500/10 or 250 Revolutions/Minute which gives you 2040 Grams/Minute of spice output.
At 30HZ, Your ball screw is spinning at 1250/10 or 125 Revolutions/Minute which gives you 1020 Grams/Minute of spice output.
(Drive Command in Hz) / 60 * 2500 * (1/10) * 8.16 = Output in Grams/Minute
Old September 13th, 2011, 05:16 PM   #4
DickDV
United States
DickDV is offline
As jrwb4... points out, there is something fundementally wrong with the statement " at 60hz the speed is 2500rpm. Not if it is an induction motor! Better check that before you go any further.
60hz is going to give you either 3600rpm, 1800rpm, 1200rpm, or some other even interger divided into 7200rpm.
It could be a four pole motor running at 2500rpm but the frequency will be around 78hz, not 60.
Old September 13th, 2011, 05:22 PM   #5
bce123
United States
bce123 is offline
bce123's Avatar
could be a gear reduction motor ?
__________________
"You can teach a dog to sit and lie down but then he justs gets lazy"
Old September 13th, 2011, 05:25 PM   #6
DamianInRochester
United States
DamianInRochester is offline
DamianInRochester's Avatar
That is an odd base speed indeed.
So you have....
60Hz/2500mRPM * 10mRPM/1aRPM * 1aREV/8.16grams
so Hz = 0.0294 * X (Grams/Min)
In my experience, I have found augers to be horribly non-linear with speed. If your motor is open loop you will also get variation just from the loading changes.
Old September 13th, 2011, 05:29 PM   #7
bce123
United States
bce123 is offline
bce123's Avatar
maybe feedback? encoder wouldnt want my secret sauce to change flavors
__________________
Old September 14th, 2011, 01:14 AM   #8
iant
Australia
iant is offline
iant's Avatar
what are you using to program this with?
place one or two tags on the Auger into a counter
control the revs from there
__________________
Give all the answers
- People seldom learn.
Guide People to the posibilities
- Their Answers will come easily.
- Their Knowledge will grow.
They will then teach others
Regards
Ian Trost
Old September 14th, 2011, 09:12 AM   #9
ndecks
United States
ndecks is offline
here is the motor name plate data.
SPEC-33-2328Z148G1
HP-.5
RPM-2500
Frame-42CZ
Type-3327P
Volts-90
Amps-5
Serial-WO608280049
Gear ratio-10-1
iant, I am using RSlogix!
Old September 14th, 2011, 09:37 AM   #10
DickDV
United States
DickDV is offline
That's a permanent magnet DC motor. Note the 90V. There must be a 120VAC powered DC drive ahead of the motor for speed control.
That complicates your auger feed rate calculations because the frequency is not controlling your motor shaft speed. The DC output voltage from the DC drive is. And, unless the DC drive has encoder or tach feedback from the motor shaft, the speed regulation under motor load variations will be as much as 5%.
At any rate, if your auger can be trusted to output 8.16g of spice per revolution over the whole speed range, then it follows from the gearbox ratio that it will output .816g per motor revolution. Since 90VDC equals 2500rpm on the motor, the feed rate could also be expressed as:
.816g/1(mtr rev) x 2500(mtr rev)/90VDC = 22.67g/VDC
This is, as mentioned above, only about 95% accurate (5% error) but that might be close enough for your purposes especially if the load on the auger is constant. The error will be worse under about 100rpm on the motor too so it would be better to operate above that speed.
If this works out to be unacceptably sloppy, you might want to consider using a stepper motor to run your auger. They are not expensive and can be controlled simply with very little error.
Good luck!
Old September 14th, 2011, 09:42 AM   #11
Doug_Adam
Australia
Doug_Adam is offline
Doug_Adam's Avatar
Looking at the name plate data, I would guess you have a DC motor, or possibly a universal motor if it is actually running on AC. Definately single phase.
If this is the case, then you cannot effectively adjust speed by changing the hz. You would have to vary the voltage. Also, you would also not get an accurate adjustment unless you have some sort of feedback, probably an encoder would be best.
Have you actually got this motor running now and just want to adjust the speed? Or are you setting up the motor for the first time, and have not run it yet?
Also, what make of motor do you have?
Old September 14th, 2011, 03:29 PM   #12
ndecks
United States
ndecks is offline
There is a DC drive controlling the motor. Sorry I went from what the mechanics told me and spent time looking at the system today. So there is a drive board from MINARIK, SHANKLIN and here are the specs on the drive DRIVE, VARIABLE SPEED, ELEC, AC INVERTER, 1 HP, 115 VAC, 50/60 HZ INPUT, 90/180 VDC OUTPUT.
I am looking through the drive manual right now!
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Speed / tension calculations execution JeffKiper LIVE PLC Questions And Answers 9 April 27th, 2010 01:13 PM
OT Z coordinate calculations for graphics mordred LIVE PLC Questions And Answers 10 May 6th, 2008 02:21 PM
Feeder Accel,Decel calculations johnfarrugi LIVE PLC Questions And Answers 15 April 28th, 2008 12:50 PM
OT- Stirling engine calculations tom_stalcup LIVE PLC Questions And Answers 40 June 30th, 2006 11:10 AM
Flow Rate Calculations Siemens S7 Tigger LIVE PLC Questions And Answers 3 October 27th, 2005 07:43 AM