Local/Off/Remote Selector Switches & Continuous Processes
agarb
May 2006
USA
309
Is an Local-Off-Remote switch just another name for a Hand-Off-Auto switch?
If so, I assume that a LOR switch would be implemented similar to the HOA switch in the attached pdf.
I am normally used to working on stand-alone machinery that performs a specific sequence and then repeats after being unloaded and loaded by an operator.
Now consider some machinery running a continuous process. There are approximately 10 motors which all must be running and remain running for the process to continue. Why would a customer specify that they want LOR switches for all the motors? It seems to me that there would be the danger of somebody walking by and turning off one motor thus disrupting the entire process. The process in question is not trivial to start up, especially if not "emptied" out properly before stopping.
Thoughts? How are LOR switches implemented in your facility?
Your customer could want Local switches: 1. To test the motor and what it does without running the entire system, 2. To allow manual operation when the Remote device fails.
Yes, there is a danger that someone could switch to Local when he should not. However, without the Local mode, there is a danger that your Remote device will fail and the owner will be left with nothing. What this says (one way or another) is that he does not completely trust what you are using and doing.
I always request Local-Off-Remote or Hand-Off-Auto switches everywhere that is appropriate, because I, too, am not a trusting guy.
I am using Twincat 3.0 and I am new to Beckoff products. I have been using Siemens most of the time a d ABB. I have tried Beckoff with twincat...
19
5,098
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
33
Is there a way to add a local message display to Studio 5000 View Designer? If its there, I’m not finding it. I have used them in older versions...
406
Hi, I'm trying to export data from a DataGrid to Excel using VBA, but I'm getting an error "Object doesn't support this property or method". The...
75
So our Powerflex 525's are set up to allow REMOTE operation from PLC through network. But if network is lost we want to be able to run in LOCAL...
564