Ab plc-5 dh+

I've a DH+ network connecting more than 20 AB PLC-5. I use the usb to DH+ converter (1784-U2DHP) to monitor and troubleshoot problems. when the DH+ cable is pluged in to the network the Rslinks does not see any of the PLCs on the network however the network for the m/cs is healthy and all m/cs are running. only when I disconnect the network from the PLC that I'm pluged in to, only then the RSlinks can see that one PLC and communicate withno problems. I've changed the lead, PC and I've tried to plug in to another PLC and the result is the same. Can any one help please? Thanks
  Reply With Quote
Old October 16th, 2011, 07:53 AM   #2
curlyandshemp
Lifetime Supporting Member
Canada

curlyandshemp is online now
 
curlyandshemp's Avatar
 
Join Date: Jul 2005
Location: Toronto
Posts: 1,611
Quote:
Originally Posted by eams2010 View Post
I've a DH+ network connecting more than 20 AB PLC-5. I use the usb to DH+ converter (1784-U2DHP) to monitor and troubleshoot problems. when the DH+ cable is pluged in to the network the Rslinks does not see any of the PLCs on the network however the network for the m/cs is healthy and all m/cs are running. only when I disconnect the network from the PLC that I'm pluged in to, only then the RSlinks can see that one PLC and communicate withno problems. I've changed the lead, PC and I've tried to plug in to another PLC and the result is the same. Can any one help please? Thanks
Perhaps the node # of your RSlinx DH+ converter is the same as an existing node on the network.
__________________
Work to Ride,
Then Ride to Work
  Reply With Quote
Old October 16th, 2011, 07:54 AM   #3
eams2010
Member
Egypt

eams2010 is offline
 
Join Date: May 2009
Location: Alex
Posts: 26
Thnaks for the rapid response. No I usually use zero and the 1st number followed is five.
  Reply With Quote
Old October 16th, 2011, 12:34 PM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,519
What do the status indicators on the USB device tell you? See PDF below.

I would try a very high node address e.g. 63. It can't hurt.
Attached Files
File Type: pdf Status_Lites.pdf (58.0 KB, 11 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old October 19th, 2011, 07:36 AM   #5
eams2010
Member
Egypt

eams2010 is offline
 
Join Date: May 2009
Location: Alex
Posts: 26
Quote:
Originally Posted by Mickey View Post
What do the status indicators on the USB device tell you? See PDF below.

I would try a very high node address e.g. 63. It can't hurt.
Thank you,
I found the problem. There was short in the wiring of the DH+ network. What makes me confused that the netwotk was healthy and all machines were running and communicating with each other with the present of the short in wiring !!!
  Reply With Quote
Old October 19th, 2011, 09:09 AM   #6
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,519
Thanks for coming back with your solution. Good to hear all is well now.

The addition of one more node may have tipped the network over the edge.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB PLC scan time Arun LIVE PLC Questions And Answers 16 September 27th, 2011 05:34 AM
Question on AB PLC limsgp LIVE PLC Questions And Answers 20 September 9th, 2011 08:45 AM
AB PLC 5/60 & 6200 (v4.41) software cywa LIVE PLC Questions And Answers 16 August 8th, 2010 06:14 PM
Comment list ab plc indra LIVE PLC Questions And Answers 1 March 31st, 2009 01:59 AM
AB PLC Processors Unregistered LIVE PLC Questions And Answers 7 June 23rd, 2005 09:33 AM


All times are GMT -5. The time now is 02:28 PM.


.