Isolation of input and output modules of PLC

Hi,

I don't have hands on experience on PLC hence i would like to have few clarifications on PLC specifications as indicated below.

One of the client PLC specification indicates the following under Input and Output modules description:

a) All input output modules shall have optioncal isolation from logic system(1500 VDC)

b) The I/O field channels shall be elctrically isolated from the I/O module electronics.

I would like to know what is the difference between these point a & b. Also, why it's required.Please clarify.

c) Also i would like to know whether if a PLC specification says relay output then the relay is in-built in the Output card itself or it's external relay.

d) In-built relays are of always Solid-State type?


Thanks in advance for valuable reply.

By
GB
__________________
Ganesh Babu
Instrument Engineer
  Reply With Quote
Old January 16th, 2004, 10:38 PM   #2
Eric Nelson
Lifetime Supporting Member + Moderator
United States

Eric Nelson is offline
 
Eric Nelson's Avatar
 
Join Date: Apr 2002
Location: Randolph, NJ
Posts: 4,296
Re: Isolation of input and output modules of PLC

Quote:
Originally posted by gb_sv
a) All input output modules shall have optioncal isolation from logic system(1500 VDC)

b) The I/O field channels shall be elctrically isolated from the I/O module electronics.

I would like to know what is the difference between these point a & b. Also, why it's required.Please clarify.
I think 'a' just clarifies 'b' by giving a type (optical) and rating (1500VDC) of the isolation. 'b' may additionally mean that the I/O field wiring cannot share the same power source as the I/O module...

Quote:
Originally posted by gb_sv
c) Also i would like to know whether if a PLC specification says relay output then the relay is in-built in the Output card itself or it's external relay.
If you buy a 'relay output' module, the relays are built into the card and may or may not be field replaceable.

Quote:
Originally posted by gb_sv
d) In-built relays are of always Solid-State type?
No. Solid-state outputs are usually called 'transistor' (DC) or 'triac' (AC) outputs.

beerchug

-Eric
  Reply With Quote
Old January 17th, 2004, 12:01 AM   #3
ArikBY
Member
Israel

ArikBY is offline
 
ArikBY's Avatar
 
Join Date: Oct 2003
Location: Oranit Israel
Posts: 1,433
You wrote

b) The I/O field channels shall be elctrically isolated from the I/O module electronics.

The way I use to do it is to put small realy/SSR on the input the signal from the field swtich the relay/SSR who switch the input, in that way you have TOTAL ISOLATION. Same for the output.For the output you can use PLC transistor outputs card which is cheaper.
You can find very small relay 5mm wide instead your terminal block.
AB or Phoenix Contact have this relays.
I work on project with 2 PLCs Omron asd Siemens and Thosiba robot.
I wanted totally isolation between them to take off the responsibility for any damage from me (I made the machine with the Omron and I responsible to handshake).
__________________
Arik

Barak Control Israel
  Reply With Quote
Old January 17th, 2004, 07:43 AM   #4
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is online now
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 4,980
The important thing to remember here is that my interpretation of the specs (or Eric's or Arik's) is nowhere near as important as the client's interpretation. Anything we say here should only be used to help you ask better questions of the client. Of course, it may turn out that the actual user of the equipment didn't write the spec and doesn't have any idea what it's asking for.

To me, a) is specifying that input and output modules use optical isolation between the logic side and the field signals. That is typical design practice and has been for years. This should not be any problem no matter which PLC you decide to use.

b) could be specifying what we usually call 'interposing relays'. You should get clarification from the client on this one, because the answer could significantly affect your cost and the amount of cabinet space you need.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 06:24 AM
Simulator, Simulation, Shadow Code Terry Woods LIVE PLC Questions And Answers 1 January 2nd, 2005 01:40 PM
PLC analog input output rate tom2378 LIVE PLC Questions And Answers 3 March 15th, 2004 06:09 AM
1 input 3 outputs guest LIVE PLC Questions And Answers 26 February 8th, 2004 04:33 PM
Normally open or closed or... Phil Melore LIVE PLC Questions And Answers 15 February 3rd, 2003 07:14 PM


All times are GMT -5. The time now is 12:19 PM.


.