Absolute Encoder and Fast Input Card
juanmdx
May 2007
SLP
281
Hello,
I'm currently working on a 1769-L32E CPU (compaq logix) with a 1769-IQ16F (fast input card) and a 845D Absolute Encoder (natural binary code), it's my first time using absolute encoders and I'm not shure how should I do it.
I connected the first ten inputs of the card to the encoder's cables (according to the manual) and then power to the encoder (according to manual), but nothing, I can't read anything, I just get 1's (except for the input 0, it remains 0), I have turned the encoder slow and fast and inputs doesn't change...
Can anyone tell me what I'm doing wrong please...
Thanks and best regards
Juan
It sounds to me like a voltage reference issue. The signal coming from the encoder is not what the input module is looking for. What is the full part number of the encoder you are using and exactly how is it wired, including power source and common.
Keith
845D-SJDZ25ANDW4
It is wired like this:
A - Input 0 on the 1769-IQ16F
B - Input 1 on the 1769-IQ16F
C - Input 2 on the 1769-IQ16F
D - Input 3 on the 1769-IQ16F
E - Input 4 on the 1769-IQ16F
F - Input 5 on the 1769-IQ16F
G - Input 6 on the 1769-IQ16F
H - Input 7 on the 1769-IQ16F
J - Input 8 on the 1769-IQ16F
K - Input 9 on the 1769-IQ16F
L - No use
M - No use
N - No use
P - No use
R - To change direction, not always on use
S - Only 24VDC when I want to reset it
T - 0VDC (well I put the 0VDC reference here the LEDs on the card didn't showed up, when I disconnected the LEDS came up, so I'm not shure it needs it)
U - This is the latch control, not shure how to use it..
V - 24VDC
As I read it the 24VDC power supplies common needs to be connected to pin T. Also that same common needs to be connected to the input card's common.
That's right, pin T is to the common of the 24VDC powersupply, and that same common is connected to the cards common, but nothing, I don't get anything on the card's inputs..., but if I unplug the encoders common (pin T to noting), I get some inputs, but they don't change...
Whan can be wrong?
You have the non-latching version of the encoder so you don't need to worry about the latch line.
However, the encoder is designed with NPN outputs. They pull the encoder line to ground when it is active. So you need to wire up the input card to work wit hsinking inputs. This means connecting 24VDC to the DC COM 1 and DC COM 2 terminals on the input card.
Keith
Thanks for the NPN tip (well, if I'd read all the datasheet I would've noticed that..., sorry), so I connected 24VDC to the COM's, but still not getting any input..., anymore ideas?
Hello. An absolute encoder on a rotary axis gives values in range -2147483648 to 2147483648. When value is > 2147483648 , the encoder value is...
20
2,292
I have 2 Absolute Encoders 8192 steps per Rev. (Model TR Electronic CEV65m-11003) These Encoders communicate to the PLC5-60 via Parallel push/pull...
1,516
Hi guys I am new to Encoders, so I have limited understanding of how to actually configure it, to the situation that I am in. Using this Absolute...
1,575
Hello to you all! I hope there is someone who can clarify some things to me..... Equipment used: TM PosInput1 (6ES7138-6BA00-0BA0) to read the...
1,269
How to connect the absolute encoder(12 bit resolution) to Hsc module of Slc500 Plc and get raw-data to my ladder logic? Please give me example...
2,695