I want to use a goto Loop in a pH subroutine (RSLogix).
Issue #1: From reading the posts here I have one immediate concern, which is that the watchdog timer S2:3/H will interfere with my loop. I anticipate that the loop needs to be active for ~10 minutes and the watchdog timer defaults to 10ms.
(10 min / 10ms) = 60000!
I rather doubt that i can increase the watchdog timer value enough.
Issue #2: I went into LogixPro Simulator to see what the consequence might be to an infinite loop. To my surprise, it was necessary to use Windows Task Manager to recover. If i manage to put a ML-1100 into such a loop, and since it reboots by running whatever program is loaded, how might I recover. I would like to know this answer before i do the loop!
Narlin
Old November 15th, 2011, 11:09 AM   #2
Tharon
United States
Tharon is offline
Is there any reason you need to use a loop in your subroutine? I'll admit, I haven't done very "complex" programs, but Jumps and Loops are one thing I've never used in a ladder program. Just always seems that anything I can think of that could use one has a simpler solution that works with the way a PLC ladder program is executed.
Especially considering you want to "stay in the subroutine" for 10 minutes. Seems like you are trying to use a programming language thought process (like C++) when programming ladder logic.
Old November 15th, 2011, 11:16 AM   #3
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
I agree with Tharon. LAD2 is already an infinite loop, just count passes through it...
Quote:
Narlin
It will fault (and stop the running program) when the watchdog timer is done, killing all outputs and just sit there with a red light saying "fix me". If you power cycle it or otherwise clear faults and put it in run mode, it will do the same thing again. I am not sure what the max watchdog timer is, but that would be that maximum time that your Micro will be "frozen" by the loop. During that period, I don't think you will be able to communicate with it.
Hopefully we have talked you out of using JMP/LBL looping for this task.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old November 15th, 2011, 11:18 AM   #4
Narlin
United States
Narlin is offline
Narlin's Avatar
Tharon, you are right on my wavelength here. Understanding that the PLC loops continuously and all the time anyway, I am working hard to not use a JMP-LBL loop. I am an old C++ programmer (learned on Fortran), and PLCs can be programmed like that, but i agree that there is also another way.
Any comment on the consequence of an infinite loop?
Old November 15th, 2011, 11:27 AM   #5
Tharon
United States
Tharon is offline
Describe what you want to accomplish in this 10 minute loop and people here could help you implement it without using loops in ladder.
Old November 15th, 2011, 11:28 AM   #6
bernie_carlton
United States
bernie_carlton is offline
bernie_carlton's Avatar
Without more information there is no way to discuss the merits of an infinite loop within a subroutine. Why do you feel that the normal looping of the PLC is insufficient for your needs? Can you describe your operation?
If in the subroutine continously then the system cannot perform the other functions like communication processing.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.
www.thePLCguy.com
Old November 15th, 2011, 11:28 AM   #7
TConnolly
United States
TConnolly is offline
TConnolly's Avatar
The watchdog timer of your ML1100 cannot be made greater than 2.5 seconds, at which time your processor will fault. If you clear the fault and put it in run mode again it will fault again in 2.5 seconds. So in practice you cannot make an infinite loop using JMP-LBL pairs.
For next loops are useful for things you want to process in a single scan - for example you might use one to sum a finite series of values. Otherwise construct your ladder to take advantage of the fact that ladder 2 repeats infinitely.
__________________
True craftsmanship is only one more power tool away.
That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
Old November 15th, 2011, 11:40 AM   #8
Narlin
United States
Narlin is offline
Narlin's Avatar
Thank you for the watchdog timer limit. I see why the jmp-lbl structure exists and that i was thinking about it in a manner not suitable to the PLC device.
Bernie, I am not going to put the logic forward just yet. Part of the fun with these toys is to program them myself. If i get stuck, I will come back for help and give a lot of detail.
I suspect that i am on the right track now.
narlin
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Flow loop and pressure loop ddeshi2 LIVE PLC Questions And Answers 9 November 16th, 2011 11:29 AM
Servo "PID" Algorithim (Allen Bradley) kdcui LIVE PLC Questions And Answers 10 September 21st, 2011 02:59 PM
Loop Control PLC Vs. Loop Module ddnnis LIVE PLC Questions And Answers 9 August 31st, 2011 04:02 PM
Tuning Primary Loop in Cascade Loops?? RPax LIVE PLC Questions And Answers 9 November 14th, 2007 02:53 PM
Servo Velocity vs Torque control TimothyMoulder LIVE PLC Questions And Answers 10 June 26th, 2006 10:42 AM