comms errors with PV+ and L32E

Setup: PV+1000 (V5.10), 1769L32E processor (V19.11). The two units communicate, the devlopment version sees all the RS5000 tags as they are created but the PV shows runtime errors like "Item '{[Silo_Routing]B1[21]' is unresolved in the processor on route Compactlogix in slot 0... I can read numberic variables on the screen, all the colour change and visibility attributes work, but any bit addressed tags generate errors like "Write attempt for item '[Silo_Routing]HMI_Switches[5]' failed (configuration error) on compactlogix... etc. The same happens if I run the application on the pc. What have I missed this time, dudes??? Thanks.
  Reply With Quote
Old November 23rd, 2011, 04:23 PM   #2
bce123
Lifetime Supporting Member
United States

bce123 is offline
 
bce123's Avatar
 
Join Date: Feb 2011
Location: texas
Posts: 1,099
can you post the files?
__________________
"You can teach a dog to sit and lie down but then he justs gets lazy"
  Reply With Quote
Old November 23rd, 2011, 05:12 PM   #3
DairyBoy
Member
Wales

DairyBoy is offline
 
Join Date: Jun 2007
Location: UK
Posts: 270
Thanks for the offer but they're still over a meg zipped. So much for zipping.
  Reply With Quote
Old November 23rd, 2011, 06:06 PM   #4
ianingram
Lifetime Supporting Member
Australia

ianingram is offline
 
Join Date: Apr 2002
Location: Newcastle
Posts: 322
Quote:
Originally Posted by DairyBoy View Post
but any bit addressed tags generate errors like "Write attempt for item '[Silo_Routing]HMI_Switches[5]' failed (configuration error) on compactlogix... etc.
You said bit address...

[Silo_Routing]HMI_Switches[5]

Is that the correct address?
Or is the address something like
[Silo_Routing]HMI_Switches[5.0]
  Reply With Quote
Old November 23rd, 2011, 06:10 PM   #5
DairyBoy
Member
Wales

DairyBoy is offline
 
Join Date: Jun 2007
Location: UK
Posts: 270
Ian, "HMI_Switches" is a DINT, so [n] is the bit number within that DINT. I've checked the format against my only other 5000/PV+ project and the format is the same.

Anyway, third late night in a row on this one and eyes/brain are stuffed. Simplest plc prog I've ever written and it's giving me more grief than some of the bigguns. crazy. Time for bed. Delivering it tomorrow...

Last edited by DairyBoy; November 23rd, 2011 at 06:20 PM.
  Reply With Quote
Old November 23rd, 2011, 07:32 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 8,716
Square brackets denote a member of an Array Tag (BOOL, SINT, INT, DINT, REAL, STRING, etc)

A period denotes a bit sub-element of a SINT, INT, or DINT Tag, whether it is an array member or an ordinary atomic datatype.

If the Tag is a DINT, then MyTag.x is the syntax for a bit sub-element in that DINT.
If the Tag is a DINT array, then MyTag[y].x is the syntax for a bit in that array element.
If the Tag is a BOOL array, then MyTag[x] is the syntax for a bit in that array.
  Reply With Quote
Old November 23rd, 2011, 07:37 PM   #7
ianingram
Lifetime Supporting Member
Australia

ianingram is offline
 
Join Date: Apr 2002
Location: Newcastle
Posts: 322
Quote:
Originally Posted by DairyBoy View Post
Ian, "HMI_Switches" is a DINT, so [n] is the bit number within that DINT. I've checked the format against my only other 5000/PV+ project and the format is the same.

Anyway, third late night in a row on this one and eyes/brain are stuffed. Simplest plc prog I've ever written and it's giving me more grief than some of the bigguns. crazy. Time for bed. Delivering it tomorrow...
I was hoping that someone else would reply by now...

I am looking at projects that I have done, and the addressing format is [shortcut_name]tagname.bit_number

I am guessing that you are missing a . in your address format
  Reply With Quote
Old November 24th, 2011, 03:40 AM   #8
DairyBoy
Member
Wales

DairyBoy is offline
 
Join Date: Jun 2007
Location: UK
Posts: 270
Ken, Ian, you're both right. I've looked at the previous PV prog as a reference without sufficient care regarding the data types in the plc prog. I need to change the data type in the hmi. My mistake. Thank you.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off