Old February 28th, 2012, 08:49 PM   #1
jspann7
Member
Australia

jspann7 is offline
 
Join Date: May 2011
Location: Rockhampton, Australia
Posts: 19
Wink 3-Wire Transmitter Analogue Wiring

Hi Guys,

I have been looking around for an answer to my question and so far have had no success.

I have an AB 1762-OF4 module which is connected to a ML 1400 1766-L32BWA PLC. I need to run a proportional solenoid valve with the 4-20mA output of the module however I am stuck.

The solenoid is 12V DC but the 1762-OF4 is 24 DC. The solenoid is wired via a 3-wire transmitter - the power supply for the setup shares the common of the transmitter with the common of the analogue output. I know the analogue card doesn't output any power, it's merely a 4-20 mA signal.

I need to how I can get this to work considering I have two different voltage ratings for the transmitter and the analogue module.

My electrician originally asked me this question. I attached a diagram of the setup.

Also, if my question seems naive, it's because I'm actually a mechanical engineer.

Thanks in advance.
Attached Images
File Type: jpg 3-Wire Transmitter.jpg (17.8 KB, 151 views)
  Reply With Quote
Old February 28th, 2012, 08:54 PM   #2
Earthscape
Member
United States

Earthscape is offline
 
Join Date: Sep 2011
Location: PNW
Posts: 84
A proportional solenoid valve? What's the make and model?
  Reply With Quote
Old February 28th, 2012, 09:22 PM   #3
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,523
You can't wire a transmitter to an output card. They are both trying to control the loop.

Or am I missing something here. What is this transmitter?
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 28th, 2012, 09:46 PM   #4
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 7,252
Mickey,

I think that in the drawing, the 12 volt DC proportional solenoid is mislabeled "3-Wire Transmitter".

Edit: No wait, that will not make sense either. Something is wrong or missing, or this was done by a mechanical hack!

JS, What you posted is the standard wiring diagram for how to wire a 3-wire signal transmitter with it's own external power supply to a MicroLogix PLC Analog INPUT. But you said your proportional solenoid is wired to a 1762-OF4 Analog OUTPUT module. The twain ard different and shall never mix or work if you wire Outputs like a diagram made for INPUTS.

More information needed. What the heck is really going on? As Earthscape said' "Do you have the make and model of the solenoid"?

Last edited by Lancie1; February 28th, 2012 at 10:00 PM.
  Reply With Quote
Old February 28th, 2012, 09:50 PM   #5
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,523
Quote:
Originally Posted by Lancie1 View Post
Mickey,

I think that in the drawing, the 12 volt DC proportional solenoid is mislabeled "3-Wire Transmitter".

HMMM? He did say this
Quote:
The solenoid is wired via a 3-wire transmitter
But it's not the first time I got it wrong.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 28th, 2012, 10:04 PM   #6
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 7,252
Mickey,

Even if the transmitter is mislabeled, still the box on the right is plainly an analog input module, therefore will not serve as an OUTPUT to control a solenoid valve, proportional or otherwise.

Those poor mechanical engineers always get into trouble when they get away from air conditioning systems....

Maybe the solenoid has an analog input that tells it how far to open, and an analog ouput that sends its position back to the PLC? Nah, that is way too complicated, right?

Last edited by Lancie1; February 28th, 2012 at 10:11 PM.
  Reply With Quote
Old February 28th, 2012, 10:15 PM   #7
jspann7
Member
Australia

jspann7 is offline
 
Join Date: May 2011
Location: Rockhampton, Australia
Posts: 19
OK. Sorry for any confusion.

The proportional solenoid is:
Make: Command Controls Corp.
Model: EPFD-16-N-10-0-M-12DG

To function with the analogue output of the module it needs:

Make: Command Controls Corp.
Model: PWM-1400-12

This is the 'transmitter' I'm talking about.

Refer to the attached.

The solenoid is connected to terminals 6 and 7, the 12V DC power supply is connected to terminals 4 and 5, the analogue +ve output (4-20mA current) is connected to terminal 1 and the common is connected to terminal 4. This matches the '3-wire transmitter' setup I was talking about.

Thanks for your replies so far.

Joel
Attached Files
File Type: pdf Proportion controller.pdf (87.4 KB, 27 views)
File Type: pdf Proportional Valve.pdf (227.2 KB, 21 views)
  Reply With Quote
Old February 28th, 2012, 10:18 PM   #8
jspann7
Member
Australia

jspann7 is offline
 
Join Date: May 2011
Location: Rockhampton, Australia
Posts: 19
Mickey,

Yes the diagram was from the input section but it basically shows the idea I am trying to convey. Change the In +/In - to Out +/Out -.

Joel
  Reply With Quote
Old February 28th, 2012, 10:18 PM   #9
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,523
Quote:
Originally Posted by Lancie1 View Post
Mickey,

Even if the transmitter is mislabeled, still the box on the right is plainly an analog input module, therefore will not serve as an OUTPUT to control a solenoid valve, proportional or otherwise.

Those poor mechanical engineers always get into trouble when they get away from air conditioning systems....

Maybe the solenoid has an analog input that tells it how far to open, and an analog ouput that sends its position back to the PLC? Nah, that is way too complicated, right?

You are making me queasy.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; February 28th, 2012 at 10:20 PM.
  Reply With Quote
Old February 28th, 2012, 10:30 PM   #10
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,523
My read is the output from your PLC ( 4-20ma) (0-20ma) would connect to terminals 1 and 3 only.
2 and 3 for voltage. No connection to the power common.

The drawing shows the pot connected to the power common only to power the pot.

You may want to consider an isolator between the PLC output and the Valve controller.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; February 28th, 2012 at 10:45 PM.
  Reply With Quote
Old February 28th, 2012, 10:38 PM   #11
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 7,252
See picture.

Your solenoid must have its own 12 volt power supply, which has nothing to do with the analog control signal coming out of the 1662-OF4.

Look at the wiring diagram for the solenoid. Your analog current signal from the PLC should be connected to terminals 1 (+) and 3 (-).
Attached Images
File Type: jpg Proportional Solenoid Current Input Signal.jpg (63.8 KB, 132 views)

Last edited by Lancie1; February 28th, 2012 at 11:16 PM.
  Reply With Quote
Old February 28th, 2012, 11:04 PM   #12
jspann7
Member
Australia

jspann7 is offline
 
Join Date: May 2011
Location: Rockhampton, Australia
Posts: 19
Lancie1,

Thanks. Just to make sure I;ve got this:

1 = Analog Out +ve
2 = n/a
3 = Analog Out -ve (com)
4 = 12V DC -ve
5 = 12V DC +ve
6 & 7 are the coil.

If thats right then thank you to everyone for your help!

Joel
  Reply With Quote
Old February 28th, 2012, 11:09 PM   #13
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 7,252
Yes, that is the correct wiring. Now as Mickey said, the 1762-OF4 module cannot be configured for either 1-5 volts or 0-20 mA (many other Allen Bradley modules can be). Therefore you do need some type of signal converter to convert the 4-20 mA signal to 0-20 mA. You may have one already. That "transmitter" you mentioned sounds like it might be a signal converter. If not, then you can buy one from many different vendors that will do the job. That is probably the best way overall to make this thing work.

Phoenix Contact is one brand of signal converter (also called signal isolator). You need one that takes a 0-20 mA input and converts it to a 4-20 mA output (which then is wired to your Commnad Controls solenoid). Notice that most of these converters will need their own power supply, so I would look at where it will be mounted, and if near the PLC, look for a 24 VDC converter, but if located at the solenoid, then try to find one that runs on 12 VDC.

http://www.phoenixcontact.com/signal...1244_14827.htm

Last edited by Lancie1; February 28th, 2012 at 11:22 PM.
  Reply With Quote
Old February 28th, 2012, 11:29 PM   #14
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 7,523
I went back and took a closer look at the 1762-OF4's manual and it can be configured for 0-20ma see pdf below. I edited my post to delete that info about it's output ranges. Sorry for any confusion. Still a little queasy.
Attached Files
File Type: pdf 1762OF4dataFormat.pdf (47.3 KB, 21 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 29th, 2012, 12:13 AM   #15
jspann7
Member
Australia

jspann7 is offline
 
Join Date: May 2011
Location: Rockhampton, Australia
Posts: 19
I just realised that I have the 1762-IF2OF2 module, not the OF4 module...

The IF2OF2 has an analog normal operating range (Current) 4 to 20 mA and a full scalar analog range of 0 to 21 mA. Can this module be configured to 0-20mA, and if so, how?

Thanks,
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
HELP SIEMENS CPU315-2DP Analogue Module Wiring NiCeBoY LIVE PLC Questions And Answers 14 August 1st, 2011 04:22 AM
Analogue Output Wiring DiscEng LIVE PLC Questions And Answers 6 July 13th, 2010 11:55 PM
three wire transmitter connection panthripu LIVE PLC Questions And Answers 8 November 1st, 2009 10:58 PM
Humidity transmitter wiring help MGuenette LIVE PLC Questions And Answers 5 March 13th, 2008 06:28 AM
Transmitter wiring GregPLC LIVE PLC Questions And Answers 3 January 29th, 2003 10:13 PM


All times are GMT -5. The time now is 05:37 PM.


.