Safety Monitor Reset

Anyone know if a PLC output can be used to reset a safety monitor?

I want to use an OIT, in addition to a local pushbutton, to turn a PLC output (relay) on to reset a Guardmaster safety monitor (Cat 3 wiring). Don't see anything in the rules about that.
  Reply With Quote
Old March 1st, 2012, 08:30 PM   #2
Doug_Adam
Member
Australia

Doug_Adam is offline
 
Doug_Adam's Avatar
 
Join Date: Sep 2002
Location: Perth
Posts: 946
I do it all the time.

The particular rules I have to work to require that a safety reset is initiated by an operator, and is not done automatically, so be careful that your code will not allow automatic triggering.
You also need to do a risk analysis for this, which basically shows what will happen if you have a failure and the reset switches on permenently. Best way over this is to ensure your safety relay is set for pulse reset and will not reset if the output is on permenently. All other normal safety requirements should be met, including checking the state of all contactors and relays before reset.
  Reply With Quote
Old March 1st, 2012, 08:32 PM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,494
Don't forget to consider "stuck button syndrome" when you do something like this. Consider what will happen when the comms cable is yanked out after the reset button is pressed on the HMI. Program it with a timer timing bit or oneshot type of instruction so that a transition from false to true is required to activate the reset.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."
  Reply With Quote
Old March 1st, 2012, 08:37 PM   #4
Mtech
Member
United States

Mtech is offline
 
Join Date: Mar 2010
Location: Indiana
Posts: 128
We have seen operators use wire ties to hold reset buttons in.
  Reply With Quote
Old March 1st, 2012, 08:43 PM   #5
intradave
Member
United States

intradave is offline
 
intradave's Avatar
 
Join Date: Nov 2010
Location: Pasadena
Posts: 32
I think the safety monitor won't reset unless it sees a false-to-true transition, so tying a button down or a stuck PLC output wouldn't be an issue. AND all of the E-Stops, Doors Switches, etc... would need to be in the proper positions. Most times E-Stops are kept pressed in until the time to reset....
The only thing that COULD be an issue is a PLC output that is "flickering" at a low rate. But I would think that would be easily detected and corrected.
  Reply With Quote
Old March 1st, 2012, 08:54 PM   #6
Eric Nelson
Lifetime Supporting Member + Moderator
United States

Eric Nelson is offline
 
Eric Nelson's Avatar
 
Join Date: Apr 2002
Location: Randolph, NJ
Posts: 4,077
Quote:
Originally Posted by Mtech View Post
We have seen operators use wire ties to hold reset buttons in.
I have seen an operator use a stack of nickels and tape to hold down a flush reset pushbutton. A one-shot solved that issue, and I kept the nickels...

Back to the OP's question. I don't see any issue with this, keeping Doug and OkiePC's advice in mind.

Similarly, I often tie the normally-open contacts of a relay into the safety circuit. This way, in addition to the standard e-stops and guard switches, the PLC also has a say in the matter. At a minimum, this relay is energized when the PLC is in the RUN state. This also give me the ability to trigger an e-stop from within the program to avoid mechanical damage to the equipment.



-Eric
  Reply With Quote
Old March 1st, 2012, 08:59 PM   #7
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,494
Quote:
Originally Posted by Eric Nelson View Post
...I often tie the normally-open contacts of a relay into the safety circuit. This way, in addition to the standard e-stops and guard switches, the PLC also has a say in the matter. At a minimum, this relay is energized when the PLC is in the RUN state. This also give me the ability to trigger an e-stop from within the program to avoid mechanical damage to the equipment.



-Eric
I did that once to prevent short-cycling of an e-stop circuit that was breaking the input to a $3000 servo drive as well as "breaking" the drive. The PLC would make the e-stop stay "dropped out" for a minimum amount of time to let the DC bus bleed down to a safe level before being re-energized.

It also had the wanted side-effect of teaching the operators not to use the e-stop for normal stop situations since they didn't have the patience to wait 30 extra seconds to start back up again.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."

Last edited by OkiePC; March 1st, 2012 at 09:02 PM.
  Reply With Quote
Old March 1st, 2012, 09:03 PM   #8
intradave
Member
United States

intradave is offline
 
intradave's Avatar
 
Join Date: Nov 2010
Location: Pasadena
Posts: 32
Yeah, one of the benefits of a PLC controlled reset is the ability to add a minimum off time before reset, to allow VFDs to dissipate energy....
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pneumatic Safety. Tharon LIVE PLC Questions And Answers 13 August 3rd, 2011 03:06 PM
Safety Relay- Basic Question Sundae8pm LIVE PLC Questions And Answers 13 November 19th, 2009 11:18 AM
Review of Banner SC22-3 safety controller kolyur LIVE PLC Questions And Answers 1 June 15th, 2008 07:42 PM
Survey of Safety PLCs Doug_Adam LIVE PLC Questions And Answers 3 September 29th, 2005 04:30 AM
E-Stop Circuit Wiring jshiepe LIVE PLC Questions And Answers 35 July 26th, 2004 09:46 AM


All times are GMT -5. The time now is 11:23 AM.


.