plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old March 2nd, 2012, 03:32 PM   #1
BLESSEN12
Ireland
BLESSEN12 is offline
B & R ACOPOS 1090 error
Hi, what is the reason servo drive acopos 1090 ready GREEN LED blinking? cannot find the error on any manuals. please help
Old May 17th, 2012, 02:24 AM   #2
kp2009
Thailand
kp2009 is offline
Quote:
I'm sorry.I not good english.
Used B&R Automation Studio communication with Acopos 1090 find >>>>
error code:7210 DC Bus:Charging :Voltage unstable
You can change Capacitor value 0.033uF/275Vac.
Acopos 1090 connect 3 phase input.
Email:langsun2009@Hotmail.com
Old June 27th, 2012, 08:15 AM   #3
kp2009
Thailand
kp2009 is offline
Old September 21st, 2012, 10:05 AM   #4
nortechplus
Algeria
nortechplus is offline
probléme with acopos 1090
السلام عليكم
Hi, what is the reason servo drive acopos 1090 with module plugin C114 error LED blinking? cannot find the error on any manuals. please help plis..
Old September 21st, 2012, 10:18 AM   #5
MarkNightingale
United Kingdom
MarkNightingale is offline
Which error LED is blinking, the one on the drive or the LED on the module, and what colour is it blinking.
Mark
Old November 3rd, 2012, 12:37 PM   #6
DaveInMinneapolis
United States
DaveInMinneapolis is offline
Smile Successful Repair - THANK YOU!
Quote:
Originally Posted by kp2009 View Post
THANK YOU for this information! It solved our problem with the same drive.
Symptom: Green LED on drive continuously blinking.
Changed all three (3) noise supression caps, as suggested.
Drive now starts up and is stable once again.
We found these capacitors at DigiKey Electronics:
http://www.digikey.com/product-detai...599-ND/3465874
THANK YOU, THANK YOU, THANK YOU!!
Dave In Minneapolis
DaveInMinneapolis@hotmail.com
Last edited by DaveInMinneapolis; November 3rd, 2012 at 12:45 PM. Reason: typo & format
Old January 8th, 2013, 03:18 AM   #7
kp2009
Thailand
kp2009 is offline
Old February 15th, 2013, 02:40 AM   #8
segar
Malaysia
segar is offline
hi,
i also have facing same symptom LED GREEN blinking ,what is the problem on this driver Acopos 1090 ?????????????
please need help
thank you
Old February 15th, 2013, 02:51 AM   #9
segar
Malaysia
segar is offline
hi, kp2009
i have check that capacitor 3 units, in the my driver is not 0.033uf its 1uf/400vac i have remove that capacitor and measure with LCR meter,but its showing that 0.689 for the 2psc and the another one is show 0.989uf so can you please tell me is that is will ok or any other probelmis in the PCB?
PLEASE I NEED YOUR HELP
THANK YOU
Old February 19th, 2013, 05:22 AM   #10
Andy M
United Kingdom
Andy M is offline
If you look where the 3 phases from the bottom board come up onto the main power board, there are some small resistor chains leading away, they go over to 3 grey capacitors with glue on the top. Directly above it is a big grey capacitor, and above that is the power block/heatsink.
It will be one of those 3 capacitors which have failed. They drop the AC line voltage down to a low level where it is rectified and monitored by the control card.
They should measure 33nF but commonly one fails to around 6nF
If you require any industrial repairs, please email me
electronics@neutronictechnologies.com
Old February 19th, 2013, 06:43 AM   #11
segar
Malaysia
segar is offline
Andy M
DEAR FRIEND, as you said have 3 psc of gray color capacitor is correct, but the value of capacitor is 1uf/400v its not the 33nf
so could be is that capacitor is failure?
the reading i measured in the LCR meter is showing 0.689uf for 2 psc .the only 1 psc is showing 0.989uf so thereare some tolerence ,about 45% of the capacitor value is faild.
thank you .
Old February 19th, 2013, 06:49 AM   #12
Andy M
United Kingdom
Andy M is offline
If you are sure you are looking at the right capacitor then any that do not measure correctly are faulty. Polyester capacitors of this nature should be very accurate and so should measure their printed value.
The 3 capacitors are located on the big PCB below the heatsink, not on the long narrow board which contains many capacitors and is attatched with screws to the main board
Old February 19th, 2013, 06:49 AM   #13
Andy M
United Kingdom
Andy M is offline
Attach a photo showing the 3 capacitors you are looking at please
Old February 19th, 2013, 07:31 AM   #14
segar
Malaysia
segar is offline
Andy M
DEAR SIR, i would take picture and send to you by tomorrow ,i am sorry now the OFFLINE ,THANK YOU SIR.
THANKS FOR REPLY SIR.
Old February 20th, 2013, 02:17 AM   #15
Andy M
United Kingdom
Andy M is offline
Photo attatched with bottom filter board removed, the 3 capacitors are actually removed here but you can see where they go
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
B&R: PP015 and ACOPOS 1016 alexhv LIVE PLC Questions And Answers 1 May 17th, 2012 03:24 AM
RSView VBA error (Object library invalid) johnhines2 LIVE PLC Questions And Answers 5 January 19th, 2011 10:45 AM
Export/Import Textlists WinCC Flex 2008 STL??? LIVE PLC Questions And Answers 6 April 19th, 2010 04:44 PM
All the light on s7-400 panel flashing leon.LEE LIVE PLC Questions And Answers 2 January 8th, 2009 10:06 AM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 06:24 AM