Modicon Tsx Communication
Please, can any one explain to me how to establish communication with a Modicon PLC TSX model? What cable and Programming software to use?
Thanks. |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Feb 2012
Location: Bay of Plenty
Posts: 817
|
Is it a Micro, a Premium, a Quantum, etc etc? You haven't fully specified the processor. A catalog number would be useful.
I've only used the Premium processors with Unity Pro as the programming software - I believe the older offering from Schneider was software called PL7. How old is this processor? the version of Unity / PL7 you need depends on the processor - there are about 3 offerings for each software I believe - small, medium and large for Unity. Cables - again depending on the processor, but Ethernet comes standard with many of the higher range processors, and i know the M340 and Premiums come with a USB port. Ethernet is my preference, since we use remote STB I/O racks which communicate over ethernet I can program the PLC as well as configure / troubleshoot I/O from the same computer. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Mar 2012
Location: Lagos
Posts: 2
|
Thanks Saffa for your response.
It is actually a TSX 37_08 PLC Model. Please, do you also know how to configure the software for communication? Thanks |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Feb 2012
Location: Bay of Plenty
Posts: 817
|
Hi there,
I haven't used that model before so I'm not really sure. By "communication", do you mean setting up the programming software (what are you using to program this?) or some sort of I/O server for reading values from the PLC? |
![]() |
![]() |
#5 |
Member
|
Program is PL7 Pro. You need special cable for comunication. You can buy from Schneider, ebay or you can make your own cable. Link is;
http://www.plctalk.net/qanda/showthread.php?t=67970 Software run on XP. For cable you need to use serial converter. PL7 pro is easy to use program. |
![]() |
![]() |
#6 | |
Member
![]() ![]() Join Date: Jan 2013
Location: malaysia
Posts: 5
|
Quote:
But I don't know the IP address for the Ethernet module. Is that any method to auto detect IP address for the Ethernet module? |
|
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Dec 2015
Location: Alabama
Posts: 125
|
If it was programmed with Unity Pro then it can be uploaded from the PLC.
As to the IP address that can be decoded from the MAC address if it was not changed from the factory default (not used in the system perhaps.) I sometimes use Scan.exe to search for an address, but it may take a while. Others may have a suggestion. Schneider products equipped with an Ethernet port have a default IP address which is derived from its MAC address (unique identifier assigned by the manufacturer). For an M340 PLC, the default IP address format is 84.x.x.x where: 84 = fixed value x.x.x = the last three fields of the default IP address. These last three fields are obtained by converting the last three hexadecimal bytes from the MAC address into decimal values. Example: The MAC address for an M340 PLC is 000053121AC4. The conversion of the last three bytes from the MAC address into decimal values gives: 16#12=10#18 16#1A=10#26 16#C4=10#196 Therefore, the default IP address for this M340 PLC is 84.18.26.196. Notes: For more information on this subject, refer to the Unity Pro online help (Deriving IP parameters from a MAC address). The MAC address is marked on the module. The method for deriving the IP address of BMXNOE0100 and BMXNOE0110 modules is exactly the same: It is polite to write the assigned IP address in the PLC for the ones who may follow you. Usually those I follow have not done so, b ut there is always the first time. |
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Jun 2007
Location: uk
Posts: 1,235
|
As above, that's a PL7 processor, you need PL7 program.
|
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Jul 2013
Location: Johannesburg
Posts: 83
|
|
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Jan 2013
Location: malaysia
Posts: 5
|
|
![]() |
![]() |
#11 | |
Member
![]() ![]() Join Date: Jan 2013
Location: malaysia
Posts: 5
|
Quote:
It has been program into PL7 file because the existing Windows is Xp and the file extension is sts. I found PLC need to be flashed with firmware before it can program with Unity Pro. Is that any method to convert the program file from PL7 to Unity Pro? http://www.plctalk.net/qanda/showthread.php?t=90943 |
|
![]() |
![]() |
#12 | |
Member
![]() ![]() Join Date: Jul 2013
Location: Johannesburg
Posts: 83
|
Quote:
keep in mind if you are going to update the firmware you will need a modbus plus cable. |
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Jan 2014
Location: Egypt
Posts: 5
|
Hi All,
i have PLC Modicon TSX 3722 Micro i need to know where should i put the socket of programming cable on Ter or Aux port. and i see the file for making cable by myself for the converter should be B&B or i can use another model like Adam. thanks. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Flashing TER light on Modicon TSX Micro | peanutsue | LIVE PLC Questions And Answers | 0 | June 23rd, 2011 12:03 PM |
Errors i Modicon TSX P57 202 | cares_nayk | LIVE PLC Questions And Answers | 5 | October 24th, 2008 06:27 AM |
PID Control with Modicon TSX Micro 3722 | kop | LIVE PLC Questions And Answers | 1 | September 8th, 2007 05:13 AM |
Modicon TSX Microscan to AB Micrologix communication | kulkago1 | LIVE PLC Questions And Answers | 2 | July 27th, 2006 08:44 AM |