poorly written vendor software
Had a freaky occurrence today:
I was attempting to tune a new machine driven with a Parker DC servo motor and a Gemini GV6K controller. The "Motion Planner" software by Parker has a tuning utility that's supposed to allow you to perform a short low speed move and graph the results and adjust drive parameters accordingly. The move was supposed to be a 6-ish inch move up (the machine is a small stage elevator that carries scenery) over about 20 seconds. I had the distinct feeling that I shouldn't really trust this software, as it's obtuse and reads like stereo instructions, so my left hand was hovering over the E-stop while my right hand clicked MOVE. The elevator took off like a scalded dog in the down direction (it was supposed to go up, slowly ). I figure my response to the sound of the servo trying to exceed the speed of sound was a little less than a second. In that time, the elevator dropped 3+ feet. Glad I put the elevator in the middle of it's 10' travel before this little adventure began.I came really close to utterly destroying a set piece first thing this morning - not the best way to start a week. Needless to say, I did the tuning manually from there on out. Parker certainly isn't the only offender, but how can vendors justify releasing half-finished and just-plain-wrong software to support their hardware? I got lucky today; someone else might end up damaging some expensive equipment, or even worse hurting someone. Just a crappy move on vendors' parts, as far as I'm concerned. On the other hand, the new E-stop system got a real-world test. It passed with flying colors. -rpoet |
|
|
|
#2 |
|
Member
|
Did you do a polarity check first? You should make sure that a positive output generates a positive direction move by do a small jog. It sounds like the the controller was still in closed loop with the polarity of the output not setup correctly.
Closed loop systems with the polarity wrong will take off like a scalded dog.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|
|
|
#3 |
|
Lifetime Supporting Member
|
IMHO,
When big expensive equipment or human life is at stake it is always a good idea to power up and do first run tests with motors disconnected from other moving parts. Even if it means more time and a second tune-up after all is connected.
__________________
LEARN something today so you can TEACH something tomorrow. DETAIL in your question promotes DETAIL in my answer. Do you "Believe"? Do you vote? Please Read: Dominus Vobiscum <))>( |
|
|
|
#4 |
|
Member
![]() Join Date: Jun 2008
Location: Ashland, OR
Posts: 247
|
Peter,
I'm sure I was ultimately the one who did something incorrectly to cause our motor to take off like it did. However, the software is unclear and unfinished (it's riddled with spelling mistakes, for instance). I'm sure you're right about having incorrect settings causing the move. The trouble was, I didn't know what I didn't know. My gripe is more about shoddy software not letting the user be clear about what's about to happen. Motion Planner from Parker is OLD software; the software and the Gemini drives it was written for first came out in the late 90's. Old software shouldn't be an excuse for allowing bugs and issues to persist. Parker is trying to phase out that line and move to their new Aries controllers, which I'm told are much more user-friendly all around. motion Planner is essentially obsolete, but I'm stuck with it for now. I'll continue to use it for downloading configs to the drives, but not so much for tuning. -rpoet |
|
|
|
#5 |
|
Member
|
I've seen it over and over again. The development of most industrial software seems to be farmed out to low bidder Asians who work/live in cubes without a clue as to how the software is actually used. It's low cost and low performance.
A software package meets marketing's need to say "there's software" and they don't get graded on its performance. I've seen numerous inquiries on control sites that are clearly from programmers in Asia, wondering about basic terminology and 'how things work' and "what does this mean?". They're trying to figure out how to code what's they now have a contract to deliver. Sounds like you have a stellar example of such. |
|
|
|
#6 |
|
Member
|
Just look at Beckhoff's I/O rack configuration software (KS2000). In this case, I would rather picture a German schoolboy doing some side work while on vacation...
__________________
Don't trust, don't fear, don't beg... |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Is there a market for written software ... | Combo | LIVE PLC Questions And Answers | 3 | June 8th, 2011 08:53 AM |
| Different values written to PID PDFile (AB Micrologix) | gripster | LIVE PLC Questions And Answers | 3 | May 31st, 2011 10:52 AM |
| Siemens S7 Flip-Flop written in SCL. Possible? | MrTysk | LIVE PLC Questions And Answers | 12 | April 30th, 2009 02:58 AM |
| Byte To Integer problem (written an error in S7) | Combo | LIVE PLC Questions And Answers | 2 | April 28th, 2008 02:55 AM |
| Does anyone have this formula already written in AD PLC? | Anibal Hernandez | LIVE PLC Questions And Answers | 4 | July 1st, 2005 04:05 PM |