Can MicroLogix 1400 communicate with EtherNet/IP adapter?
My company perchased a "MicroLogix 1400" to verify the connection with our
"EtherNet/IP to Modbus gateway", which is use as an EtherNet/IP adapter while The MicroLogix 1400 is an EtherNet/IP scanner. Here are my problems: 1 I have notice a comment on website of ML1400 says “allows controllers to exchange data with other controllers through messaging; does not support scanning of I/O on Ethernet adapters”. Does it means MicroLogix 1400 cannot act as an EtherNet/IP scanner and work with an EtherNet/IP device which acts as an EtherNet/IP adapter? 2 I tried to setup the MSG block on RSLogix 500 to communicate with our module and always get "Invalid data type" error. No matter what data type I select. And of course I can't connect with our module. |
|
|
|
#3 |
|
Lifetime Supporting Member + Moderator
|
Are you manufacturing this device, or are you testing something made by another company ?
I'm not going to describe all of EtherNet/IP in a Forum post: you can get that from the ODVA. But I'll hit the highlights. In general, MicroLogix and SLC family controllers perform PCCC functions that are transported by CIP. PCCC is a protocol used mostly for older (PLC, SLC, and MicroLogix) controller data table reads and writes, rather than for I/O exchange. ControlLogix family controllers (including CompactLogix) use EtherNet/IP differently; they not only perform CIP data table reads and writes, but also perform cyclic I/O connections using EtherNet/IP. The technical name for devices participating in I/O connections on EtherNet/IP are Client and Server, or Target and Originator. The terms Scanner and Adapter are commonly used to describe the hardware, but are not the proper technical terms for EtherNet/IP protocol roles. The MicroLogix 1400 does have the ability to perform a CIP Generic Message to read and write the Assembly Object of a CIP device, but the connection is still an explicit message connection, not a cyclic I/O connection. Some devices will work identically with an explicit or a cyclic message connection to the Assembly Object. Many will not. To properly test a device that is intended to work with ControlLogix and CompactLogix, you need to use a ControlLogix or a CompactLogix.
__________________
"Intelligence is the capacity to know what we are doing and instinct is just instinct. The results are about the same." |
|
|
|
#4 |
|
Member
![]() Join Date: Mar 2012
Location: Taiwan
Posts: 2
|
Well, I am manufacturing this device and just want to figure out if our device can work properly with AB's PLC.
I had already test my device can properly work with a ControlLogix and its EtherNet/IP module which we borrow from other company. But eventually my company bought MicroLogix 1400 for it is much cheaper than ControlLogix. And I soon realize they are totally different... My device did support "explicit message connection". So do you mean there got to be some way to read/write data to my device? Anyway, thanks for answering my questions. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Micrologix 1400 + Panelview 550 + DH485 | alexbeatle | LIVE PLC Questions And Answers | 2 | September 13th, 2011 10:30 AM |
| micrologix 1400 and barcode scanner | irondesk40 | LIVE PLC Questions And Answers | 0 | August 17th, 2011 12:04 PM |
| MicroLogix 1400 Network | seaston_65 | LIVE PLC Questions And Answers | 2 | July 15th, 2011 12:57 PM |
| Micrologix 1100 and Ethernet/IP barcode reader | SCUBA NooB | LIVE PLC Questions And Answers | 2 | June 11th, 2011 09:20 PM |
| Micrologix 1400 and RSLinx 2.54 | Tharon | LIVE PLC Questions And Answers | 7 | April 28th, 2011 08:26 AM |