#16 | |
|
Member
![]() Join Date: Apr 2002
Location: NC
Posts: 1,429
|
Quote:
Link: http://us.idec.com/Catalog/ProductSe...yName=Software I haven't tried it. What I do to test a program is change the program PLC configuation to FA-3S which I have. Most of the time it works well enough to test the code. |
|
|
|
|
#17 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
Sir
I am working to convert the program to a format the PR3 can deal with. I have a question about two internal relays. One on rung 3 M0020 and one on rung 10 M0021. They are the outputs from the 1 hour timers. I wanted to know what that value should be. Are they some special internal relay I should be worried about? Thanks |
|
|
|
#18 |
|
Member
![]() Join Date: Apr 2002
Location: NC
Posts: 1,429
|
They are just dummy internal relays, used as a shortcut to fill a space on the rung. They have no other use. Don't worry about them, just pick an unused "R" address (maybe R420 and R421) to substitute for M20 and M21. Don't use a latch type output coil, just an ordinary output coil. See page 5-6 of th 01A1 manual for the address allocation table.
Last edited by jrwb4gbm; June 26th, 2012 at 01:18 PM. |
|
|
|
#19 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
That is what I figured because I did not see them any other place in the program but wanted to be sure. Thanks for the quick reply.
|
|
|
|
#20 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
Sir,
I got the program loaded and it seems to be running well. I have been doing tests with a 30 minute cycle in place of the 12 hours. I did need to make some minor changes to get it to do what I needed. 1st I added a 30 sec delay to the start up. Should we have a power flicker (as we ofter do here in Maine) I did not want the fans starting and stopping till the power was stable again. 2nd I have to use the output from rungs 3 (M0020)and 10 (M0021)as I was not able to get my PR3 to let me load the counter output with out them. Sure it is my error but using the outputs works fine. 3rd the leadership here has desided they want an 8 hour run in place of 12 so I just changed counters C001 and C003 to 8. I would like to thank you one last time for all your help on this project. I learned alot from your posts and now I feel comfortable using counters in my programs. You saved me alot of time and sleepless night. Great forum. Thanks again. |
|
|
|
#21 |
|
Member
![]() Join Date: Apr 2002
Location: NC
Posts: 1,429
|
The 30 second delay (timer TMR 2, rung 1) can work for manual re-start. You may have to hold the button down for the full 30 seconds to get it to work. The use of S and R type outputs for Q0 or Q1 needs to be changed. They will start immediately after power is restored unless they are handled differently. I will add some more code to address that and post it later today if I have time.
|
|
|
|
#22 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
My input 1 on rung 0 is just a jumper (pice of wire)from com to input 1. They want it to power up whenever the panel is powered up. That is why the 30 sec hold for a power outage and the SOT.
It is ok if the counters and timers restart if the power goes out. The system they have in place now does that and I guess it is not causing them any problems. However I would like to learn for myself how to make the changes you are talking about. |
|
|
|
#23 |
|
Member
![]() Join Date: Apr 2002
Location: NC
Posts: 1,429
|
Attached is my idea on revisions. I added the following:
1. A standard start-stop type control logic for the cycle start, rung 1. 2. Changed the original Q0 relays to internal M7 (rung 3,4,5,7,8,9,10) and Q1 to M14 (rung 3,10,11,12,14,15,16). 3. Re-located the 30 sec timer TMR2, rung 2. 4. Used the 30 second timer and internal relays to control the Q0 and Q1 physical outputs as non-retentive, see rungs 19 and 20. I did not add a manual Counter Reset feature yet. Check your Private messages, button is near top right side of the webpage. Edit: As you have indicated in post #22, it will probably work OK for most cases provided the Main Power is locked out if anyone is in the kiln or near the fan motors. Maybe you might want to add some of the changes shown in the revision attached or maybe not. Last edited by jrwb4gbm; June 27th, 2012 at 02:21 PM. |
|
|
|
#24 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
Thank you for the updated ver. I looked at it and am going to study it a bit more to try and fully understand what it is doing and why.
I enjoy this kind of thing and want to learn all I can about programing. |
|
|
|
#25 | |
|
Member
![]() Join Date: Apr 2002
Location: NC
Posts: 1,429
|
Quote:
Link: http://www.ebay.com/itm/IDEC-Micro-1...item564743fa94 |
|
|
|
|
#26 |
|
Member
![]() Join Date: Jun 2012
Location: Auburn, Maine
Posts: 15
|
Installed the PLC in place of the old relay/timer setup today. Seems to be working well.
I wanted to take a moment to thank you one last time for your help. You saved me a ton of time and I learned alot. Thank you sir. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Micro 1200 Modbus Slave Error Question | Duwop | LIVE PLC Questions And Answers | 1 | October 5th, 2007 06:16 PM |
| Fireye Lingering Flame Failure Timing Question | Russ | LIVE PLC Questions And Answers | 19 | February 13th, 2006 10:15 AM |
| 90 micro on delay timer question | plc_padawan | LIVE PLC Questions And Answers | 5 | September 18th, 2005 01:36 PM |
| 300 Micro list / message question. | Mark_H | LIVE PLC Questions And Answers | 3 | August 8th, 2005 06:43 PM |
| micro view 300 question! | darrentpi | LIVE PLC Questions And Answers | 7 | June 6th, 2005 02:17 AM |