press and hold

I need some instruction help in logix5ooo. Here is my question, I have a button on a screen (rsview) for lets say a drain valve. The problem is some of the operators mistake pushing this instead of the inlet valve button, I would like to have them press and hold this button for say two seconds so they are forced to acknowledge what the button says and that it is the correct button. What instruction would I use?
__________________
Sweet johnny

It's a cult, and I am not drinking the kool-aid.
  Reply With Quote
Old August 2nd, 2012, 08:46 AM   #2
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 10,002
First, I would put clear labels on ALL buttons.

Then if I still needed the enable delay, I would reprogram the button in the RSLogix 5000 program so that it starts a timer, and the timer does not enable the button function (what it does) until the display time has passed. Two seconds may be too short. It takes maybe a second to read the pop-up label and about 1.5 seconds for the average person to respond (connect brain to finger muscles), so 3 seconds may be closer to what you need.

If you only have access to the RSView program (not the PLC program) then you can create a Derived Tag for the button. The Derived Tag will be an expression for Time delay & Old button. You will have to be able to rename the new Derived Tag with the same name as the old tag, otherwise the exisiting PLC program will not use it.

Last edited by Lancie1; August 2nd, 2012 at 09:11 AM.
  Reply With Quote
Old August 2nd, 2012, 08:56 AM   #3
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,207
If possible a visual representation of the vessel with the button placed at the approximate position of these valves. This can be in addition to the time delay requested.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old August 2nd, 2012, 09:13 AM   #4
sweetjohnny
Member
United States

sweetjohnny is offline
 
sweetjohnny's Avatar
 
Join Date: Feb 2012
Location: Iowa
Posts: 55
Putting clean and understandable labels on the buttons was the first thing I did. It is also the same on the graphic. I guess i was over thinking this, a timer. Brain ****. Thank you guys.
__________________
Sweet johnny

It's a cult, and I am not drinking the kool-aid.
  Reply With Quote
Old August 2nd, 2012, 09:14 AM   #5
sweetjohnny
Member
United States

sweetjohnny is offline
 
sweetjohnny's Avatar
 
Join Date: Feb 2012
Location: Iowa
Posts: 55
Evidently the common term for flatulence is frowned upon in this forum. Sorry.
__________________
Sweet johnny

It's a cult, and I am not drinking the kool-aid.
  Reply With Quote
Old August 2nd, 2012, 09:53 AM   #6
gscure
Member
United States

gscure is offline
 
gscure's Avatar
 
Join Date: Aug 2007
Location: Georgia
Posts: 133
Pop Up Confirmation

As we all know...operators will in time ignore all indications on the screen no matter how clear they are. New operators are better at pressing the correct button because they will read the text. Once it becomes habit they get ignored the same as alerts and alarms.

I suggest using a pop up that confirms what button they just pressed. It doesn't add much to the operation but allows them to read the pop up screen and confirm their choice. This will not eliminate errors only reduce them.
  Reply With Quote
Old August 2nd, 2012, 10:08 AM   #7
Darkzadow
Member
United States

Darkzadow is offline
 
Join Date: Nov 2011
Location: Phily
Posts: 94
One thing I like to do with new HMI screens is to make on that I think is clearly labeled then give it to the operator for a day and ask what he thinks the buttons should be named, and ask why he would hit the wrong button. Operator feedback does half my HMI design and improvement for me. This method is convenient for me cause my office is on plant floor 100 feet from my equipment. (and as a new guy i have the time to ask what they think)
  Reply With Quote
Old August 2nd, 2012, 10:41 AM   #8
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 10,002
Quote:
Once it becomes habit they get ignored the same as alerts and alarms.
Once the operators know what a button does, there is no need for them to read the label. Adding a confirmation just adds to operator frustration. An efficient program does not resort to such tactics unless the button controls a life-or-death situation.

Quote:
Operator feedback does half my HMI design and improvement for me.
That is a very effective method. Customer feedback (whomever the customer may be) is always a useful tool. If you don't know what the customer wants, then you are guessing based on your opinions. Your opinions don't count for much unless you are willing to use your product for 24 hours non-stop. I once told that to a doctor who was prescribing a CPAP torture machine for me. I asked him if he had ever used this machine, and he said "no, why should I?" I said so that you know what the he!! you are talking about.

Last edited by Lancie1; August 2nd, 2012 at 10:44 AM.
  Reply With Quote
Old August 2nd, 2012, 10:48 AM   #9
gscure
Member
United States

gscure is offline
 
gscure's Avatar
 
Join Date: Aug 2007
Location: Georgia
Posts: 133
Quote:
Once the operators know what a button does, there is no need for them to read the label. Adding a confirmation just adds to operator frustration. An efficient program does not resort to such tactics unless the button controls a life-or-death situation.
If the operator is accidentally pressing the wrong button the best program in the world will not stop the error from happening. You apply the confirmation popup only where the application calls for it. Just like everything else in automating equipment...you use the right tools for the right function. I was not implying everything has a confirmation popup.

Last edited by gscure; August 2nd, 2012 at 10:50 AM. Reason: Operator frustration
  Reply With Quote
Old August 2nd, 2012, 10:50 AM   #10
gscure
Member
United States

gscure is offline
 
gscure's Avatar
 
Join Date: Aug 2007
Location: Georgia
Posts: 133
Sometimes frustrating the operator is exactly what needs to happen when they get lazy at what they do. This does happen and it is a huge problem. Not all operators and not all applications but can be effective.
  Reply With Quote
Old August 2nd, 2012, 09:13 PM   #11
redlinej
Member
Antigua and Barbuda

redlinej is offline
 
Join Date: Jul 2012
Location: antigua
Posts: 3
I work write a text when the button is press to pop up saying " open the drain valve? and ok at the bottom of it, i see a lot of hmi have this and it's idiot proof.
  Reply With Quote
Old August 2nd, 2012, 11:36 PM   #12
dcooper33
Lifetime Supporting Member + Moderator
United States

dcooper33 is offline
 
dcooper33's Avatar
 
Join Date: Jun 2011
Location: Rogers, AR
Posts: 694
Quote:
Originally Posted by redlinej View Post
I work write a text when the button is press to pop up saying " open the drain valve? and ok at the bottom of it, i see a lot of hmi have this and it's idiot proof.
Never underestimate the power of the latest and greatest idiot. They come out with new versions much faster than we can make the patches!

I have used the same method on crowded screens, or where the wrong button press can cause serious problems. Invariably, operators will complain about the extra button presses, though. It's a double-edged sword.
__________________
I'll walk a mile in your shoes. Now I'm a mile away, and I got your shoes.
  Reply With Quote
Old August 3rd, 2012, 05:58 PM   #13
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,341
Quote:
Originally Posted by sweetjohnny View Post
I need some instruction help in logix5ooo. Here is my question, I have a button on a screen (rsview) for lets say a drain valve. The problem is some of the operators mistake pushing this instead of the inlet valve button, I would like to have them press and hold this button for say two seconds so they are forced to acknowledge what the button says and that it is the correct button. What instruction would I use?
Try to be pro-active with the system...

There will be times when it is appropriate to open the inlet valve - say when the tank is empty, and times when it might be inappropriate to open the inlet valve - say when the tank already has some contents. Similar thing for the drain valve.

Design pop-up confirmations to appear only when the action may be inappropriate, and bubba will soon learn what button to press at the relevant time. If you ask him if "Are you sure" every time, he'll just get used to saying yes.

But if he learns that he can avoid a pop-up by thinking about which button to press - he'll get the right one every time.

This is a strategy that does work - I've seen it in action
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old August 3rd, 2012, 06:44 PM   #14
Liam Moran
Lifetime Supporting Member
Ireland

Liam Moran is offline
 
Liam Moran's Avatar
 
Join Date: May 2011
Location: Carlow
Posts: 330
I have found that setting up an operator log, and making the operator aware of this, significantly reduces errors. They will never press the wrong button if they will be held accountable.
  Reply With Quote
Old August 3rd, 2012, 08:19 PM   #15
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,732
For something like this, a pop up with two widely spaced and clearly labelled buttons. Confirm/execute the action or cancel (close popup). Then they are only burdened with one more button press, so you have given them an opportunity to think twice, which may reduce the erorrs, but you can't fix all human errors, so don't make it too difficult to operate.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

Last edited by OkiePC; August 3rd, 2012 at 08:21 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
what are Integer, Real #, word, Hex, bin, etc Siemener LIVE PLC Questions And Answers 7 July 29th, 2008 11:46 AM
AD DL06 programming help ThermoT LIVE PLC Questions And Answers 46 June 7th, 2006 08:21 AM
Tough Nut... Terry Woods LIVE PLC Questions And Answers 58 October 26th, 2004 07:47 PM
Can Anyone Draw This In Rslogix And Send Pic To Me?? fremont LIVE PLC Questions And Answers 3 October 14th, 2004 07:09 PM
answer needed ramakrishna LIVE PLC Questions And Answers 6 July 28th, 2002 07:08 PM


All times are GMT -5. The time now is 06:45 AM.


.