HMI Vijeo and DF1 from Micrologix 1400

Hi,

I have problem with communication between HMISTU655 and Micrologix1400.
HMI is connected by COM1 to channel2 of micrologix, channel1 it's used for other comm.

Did someone connect HMISTU to ML1400?
In documentation form vijeo "Allen-Bradley DF1-Full Duplex Driver" is only ML1000, 1200, 1500, so it's mean 1400 it's not compatibly? I hope that it's old document thats why 1100 and 1400 are not in list.
  Reply With Quote
Old November 8th, 2012, 12:28 AM   #2
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by Wiktor View Post
Hi,

I have problem with communication between HMISTU655 and Micrologix1400.
HMI is connected by COM1 to channel2 of micrologix, channel1 it's used for other comm.

Did someone connect HMISTU to ML1400?
In documentation form vijeo "Allen-Bradley DF1-Full Duplex Driver" is only ML1000, 1200, 1500, so it's mean 1400 it's not compatibly? I hope that it's old document thats why 1100 and 1400 are not in list.
Welcome to the Forum!

The ML1400 should be fine with DF1. Make sure that the ML1400 Serial Channel 2 is set for DF1, and that the PLC and HMI Baud Rates and Error Correction match. Be aware that there are variations in the DF1 Protocol between the PLC5 and SLC/ML lines. So, you have to make sure that the HMI and PLC are using the same Parameters.

What are you using for a Serial Cable between the HMI and PLC?

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old November 8th, 2012, 02:10 AM   #3
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Quote:
Originally Posted by sthompson View Post
Welcome to the Forum!

The ML1400 should be fine with DF1. Make sure that the ML1400 Serial Channel 2 is set for DF1, and that the PLC and HMI Baud Rates and Error Correction match. Be aware that there are variations in the DF1 Protocol between the PLC5 and SLC/ML lines. So, you have to make sure that the HMI and PLC are using the same Parameters.

What are you using for a Serial Cable between the HMI and PLC?

Stu....
Divers in HMI are chosen AB/micrologix/DF1, so it's not mixt with PLC5 or others protocol (separate drivers).

DF1 speed, parity, crc are identical in PLC and HMI.
Cable: home made D-SUB9 to RJ45. Quality control pass
PLC D-SUB have standard pin out (dsub9.gif) ?
I attached also 2 files with HMI pin out (form HMI doc.)
Attached Images
File Type: jpg PLC HMI pinout connection DF1 full duplex.jpg (33.1 KB, 40 views)
File Type: jpg HMI COM1 pinout.jpg (27.8 KB, 34 views)
File Type: gif dsub9.gif (8.3 KB, 33 views)
  Reply With Quote
Old November 8th, 2012, 02:39 AM   #4
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by Wiktor View Post
Divers in HMI are chosen AB/micrologix/DF1, so it's not mixt with PLC5 or others protocol (separate drivers).

DF1 speed, parity, crc are identical in PLC and HMI.
Cable: home made D-SUB9 to RJ45. Quality control pass
PLC D-SUB have standard pin out (dsub9.gif) ?
I attached also 2 files with HMI pin out (form HMI doc.)

Well, it all looks reasonable. According to the Diagrams, it should just be RXD, TXD, and SG. From the Diagrams you Posted, it would be easy to confuse the RXD, and TXD Pins.

If I am understanding the Diagrams correctly, Pin 1 of the HMI (RXD) goes to Pin 3 of the PLC (TXD), Pin 2 of the HMI (TXD) goes to Pin 2 of the PLC (RXD), Pin 8 of the HMI (SG) goest to Pin 5 of the PLC (SG).

Is that the way you see it?

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old November 8th, 2012, 02:44 AM   #5
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Problem solved by using Ethernet port!
I start form DF1 because I find in vijeo doc information that for Ethernet (ML1000, 1100, 1200, 1500)I need 1761-NET-ENI
No any info about ML1400, so I try to connect and it's work fine!

Finally ML1400 works fine with vijeo 5.1 drivers AllenBradleyEtherNetIP01 EIPMicroLogix01.
Problems with DF1 com on port3 not solved.

I try with ML1100 and... Ethernet connection works without 1761-NET-ENI !
Probably because of new FW (I have SER:B, REV:E, FRN:11)
  Reply With Quote
Old November 8th, 2012, 02:52 AM   #6
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by Wiktor View Post
Problem solved by using Ethernet port!
I start form DF1 because I find in vijeo doc information that for Ethernet (ML1000, 1100, 1200, 1500)I need 1761-NET-ENI
No any info about ML1400, so I try to connect and it's work fine!

Finally ML1400 works fine with vijeo 5.1 drivers AllenBradleyEtherNetIP01 EIPMicroLogix01.
Problems with DF1 com on port3 not solved.

I try with ML1100 and... Ethernet connection works without 1761-NET-ENI !
Probably because of new FW (I have SER:B, REV:E, FRN:11)
I am glad you have it working. I believe it should communicate with the ML1400 without problem, regardless of the Firmware Version. Other than the differences I mentioned in the earlier Post, DF1 should be DF1. Hopefully Ken Roach will chime in if he has time.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old November 8th, 2012, 03:42 AM   #7
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Quote:
Originally Posted by sthompson View Post
...the ML1400 without problem, regardless of the Firmware Version. ..
Stu....
ML1400: no any info about this model in Vijeo documentation.
ML1100: according Vijeo 5.1 doc need 1761-NET-ENI for Ethernet connection (more expensive than ML1100 itself!). I think when Schneider El. wrote this information because ML1100 was available with older FRN who not support Ethernet connection to HMI, or something like that.
Now on ML1100/FRN 11 connection works fine.
  Reply With Quote
Old November 8th, 2012, 09:15 PM   #8
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 424
Hi, If I may chime in...

Wiktor, I'm glad you realised that Ethernet is the best way to communicate between these 2 devices and are now up & running. I too use ML1400's with HMISTU655's & HMISTU855's, nice HMI.

Having read the thread, I felt it needed closure.
This is to assist others who may want, or have to use either DH485 or DF1 for ML1400 CH2(D-SUB9) to COM1(RJ45) on a HMISTO/STU & need to make a cable. It's not difficult, if you follow Schneiders driver help docs carefully, but some may get confused between the many wiring options they give as to which one to use. There is a little bonus too.

It's fairly comprehensive, so if someone feels this should be a "How To" posted somewhere else, please move it or ask me to post it seperately instead.

I had originally tried the ML1400 with the lesser, serial only, HMISTO511. Initially I used DH485 for that setup and made my own cable from the driver help file doc.

DH485 Cable: (ML1400 Ch2 D-SUB9>HMISTO/STU COM1 RJ45)
Page 14 of Schneiders "Allen-Bradley DH485 Duplex Driver" doc (attached below) shows the wiring options for COM1(RJ45) as RS-232C or RS-232C.
The top pinout is indeed RS-232C, but the bottom pinout is RS-422/485, it's a typo error. We are using RS-232C here.
So from this we use pin 1-RD(RXD), pin 2-SD(TXD) & pin 8-GND.
Now go to page 16. Here we use "b.Connection Diagram". Notice the CS/RS link on the target side & the note below. Ignore this link for STO/STU's, as it is only relevant to higher model Magelis HMI that have D-SUB9 COM ports.
In this diagram they do not show pin numbers on the target side as it relates to many different HMI models, which differ in port types & pinout numbering.
For reference, write "8" beside "GND", "2" beside "SD(TXD)" & "1" beside RD(RXD).
This is important! The diagram shows the D-SUB9 plug wiring intended for a NET-AIC. The ML1400 can connect directly to the HMI, if you don't have a NET-AIC. However, Ch2 on the ML1400 is a non-isolated port. The NET-AIC's ports are electrically isolated from each other & so it provides protection against ground loops & voltage differences between the devices connected to it. Connect without NET-AIC at your own risk!
The D-SUB9 standard pinout diagram was linked by Wiktor earlier, so I wont attach it again.
Now you should be ready to make your cable.
Once cable is ready you have to setup your equipment port & driver settings.
Setup Ch2 on ML1400 for Driver: DH485, Baud: 19,200, Node Address: 1
(or whatever Node number your PLC is assigned on your network).
In your Vijeo Designer project scroll down to "IO Manager" & right click then "New Driver". Select Manufacturer "Rockwell Automation", then from left list choose "Allen-Bradley DH485, then from right list choose "DH485 MicroLogix". A new driver is created under "IO Manager" named "AllenBradleyDH48501 [ COM1 ]", double click this. In the Driver Configuration window set connection type: RS-232C, trans speed: 19,200 & node number: 2
(or whatever Node number your HMI is assigned on your network).
Now expand "AllenBradleyDH48501 [ COM1 ]" & you should see your equipment "DH485MicroLogix01". Double click & you get Equipment Configuration window. Set your PLC's node number here: 1 (or whatever).
Don't forget to select "DH485MicroLogix01" as the "Scan Group" for each variable you create(d) or they will not work.
Now you have configured your DH485 driver & equipment in Vijeo Designer ready for download to the HMI.
Once the RSLogix 500 & Vijeo Designer projects are loaded to the equipment, plug in the cable & test your comms status at the PLC. You should see the COMM 2 indicator on the LCD display on steady. Online, check the comms status & you should see messages sent/received totals are active for Ch2. If you have any I/O to the HMI panels, they should be active now also.

DF1 Cable: (Here comes the bonus!)
The DH485 cable will also work for DF1, so no need to make a second cable!
Only differences are:
Set ML1400 Ch2 for DF1 & setup the new DF1 driver in Vijeo. The default settings for both are fine.
Don't forget to change the "Scan Group" for variables to the DF1 driver.
When testing, the COMM 2 indicator on LCD display will blink when comms are active.
Note: DF1 will also work with or without NET-AIC.

Because I chose to test DH485 initially I hadn't read the driver help file for DF1. I just tried the DH485 cable for DF1 after DH485 had worked & DF1 worked first time. But when I saw your diagram from the DF1 help file Wiktor, I noticed something straight away!

Quote:
sthompson wrote:
From the Diagrams you Posted, it would be easy to confuse the RXD, and TXD Pins.

If I am understanding the Diagrams correctly, Pin 1 of the HMI (RXD) goes to Pin 3 of the PLC (TXD), Pin 2 of the HMI (TXD) goes to Pin 2 of the PLC (RXD), Pin 8 of the HMI (SG) goest to Pin 5 of the PLC (SG).
Is that the way you see it?
It would be even easier to confuse the RXD and TXD when the diagram is incorrect! Wiktor, you didn't answer the question as to how you saw it when you went to wire it up? If you followed Schneiders diagram it would never have worked as they show HMI pin1(RXD)> PLC pin2(RXD) & HMI pin2(TXD)> PLC pin3(TXD). Yet another typo. I've attached a corrected version of your earlier diagram. It's all academic beyond "The DH485 cable will also work for DF1, so no need to make a second cable!", but its always nice to get to the bottom of problems for everyone's benefit.

Geospark.
Attached Images
File Type: jpg PLC HMI pinout connection DF1 full duplex(Corrected).jpg (38.4 KB, 23 views)
Attached Files
File Type: pdf RockwellDH485e.pdf (212.6 KB, 19 views)
File Type: pdf RockwellDF1FullDupe.pdf (211.9 KB, 27 views)

Last edited by Geospark; November 8th, 2012 at 09:20 PM.
  Reply With Quote
Old November 9th, 2012, 03:05 AM   #9
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Thanks for explanation Geospark!
I made wrong cable according Schneider diagram! I look only on pin no not TX/RX description
BTW It is some way to import variables form RSlogix to Vijeo?

Geospark, you use RSLogix 500 for ML1xxx? I have RSLogix micro, local AB says that for ML1xxx I must use RSLogix micro, not 500 or 5000.
  Reply With Quote
Old November 9th, 2012, 09:56 AM   #10
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 424
I'll handle the software question first. From my experience of the different versions, here is what I know. If I'm incorrect someone please correct me. I know most users know alot of this already, but I like to post for the benefit of others searching for this kind of info. It may already be here somewhere I'm sure.

Quote:
From Rockwell Documentation:
What is RSLogix Micro?
More cost-effective application development software exclusively for Rockwell Automation MicroLogix Controller customers
Same reference standard features as RSLogix 500, but simplified by
No SLC controller support
No FactoryTalk Services support (except Activation)
Standard Node-locked license only
Smaller footprint install of RSLinx Classic
Support of On-line (run mode) editing for all MicroLogix that support it
Readily shares project files with RSLogix 500
Cannot be installed on same PC as RSLogix 500
The difference between the Micro editions is which controllers, or features of controllers, they support.
Some might mistake the "Micro" in the software description as meaning a lesser featured version of RSLogix 500. In truth it is, but the "Micro" just refers to the MicroLogix Controller Family, as that is all the RSLogix Micro editions support.

"RSLogix Micro Starter Lite" is the minimum edition you can use and is free to download. It replaced "RSLogix 500 Starter Lite". This edition only supports the Micrologix 1000 and 1100. The 1100 allows online editing and Lite supports this feature, but you must download "RSLinx Lite" to use this feature.

They are available for download here:
http://http://www.ab.com/linked/prog...downloads.html

You can use RSLogix Micro "Starter" or "Developer" for all of the MicroLogix Controller family(1000,1100,1200,1400,1500). They are not free. They also support online editing, which the 1100 and 1400 support. So if you use 1400's and want online editing, you must use at least "Micro Starter" edition.
"Starter" edition would probably be ok for most MicroLogix only users.

This is a small doc on RSLogix Micro. There is a "Starter" & "Developer" edition supported features list at the end.
http://literature.rockwellautomation...p001_-en-p.pdf

"RSLogix 500" adds features to the above, such as SLC500 Family Controller support and comes with the following editions:
"RSLogix 500 Starter"
"RSLogix 500 Standard"
"RSLogix 500 Professional"

I won't go into all the differences between them, you can check them out here:
http://literature.rockwellautomation...p001_-en-e.pdf

Again, "Starter" would probably do most users, but only supports online editing for the MicroLogix 1100 and 1400. "Standard" adds on SLC500's to this.

Wiktor, I don't know what version you have, but RSLogix Micro is fine for the 1100 and 1400 you've mentioned using earlier. We, however, use "RSLogix 500 Standard" and the reason is that we have SLC503's and SLC505's as well as MicroLogix Controllers and do use online editing, online cross reference etc.

I'll post another reply on the variables export/import question later.

Geospark.
  Reply With Quote
Old November 20th, 2012, 07:06 AM   #11
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Quote:
Originally Posted by Geospark View Post
....

I'll post another reply on the variables export/import question later.

Geospark.
I still waiting for you answer about export/import to Vijeo. Now I do it manually one by one
  Reply With Quote
Old November 21st, 2012, 10:44 AM   #12
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 424
Sorry Wiktor, I have been busy renovating an en-suite! & tackling some Point I/O issues in work that has tied me up alot I haven't forgotten you. I don't like rushing replies that require detail, documents, links etc. I have finished both jobs now so I'll post you a reply later when I'm in work where I have the resources to help. Might not be all good news though

G.
  Reply With Quote
Old November 22nd, 2012, 03:33 AM   #13
Wiktor
Member
Poland

Wiktor is offline
 
Join Date: Nov 2012
Location: Katowice
Posts: 13
Ok, now it's not high priority for me, project is already done.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
xbtgt1000/vijeo designer -micrologix1000 df1 cable franzela LIVE PLC Questions And Answers 2 January 17th, 2011 07:05 PM


All times are GMT -5. The time now is 12:31 AM.


.