Question New Scada system - WW of iFix?

Hello all

I really need your help.

I'm in the middle of a process, where we are to point out a new system for our existing BMS system - around 15000 IO's (all new BACnet controller).
The system are going to be split in two sections - a validated BMS system (GMP) and a normal BMS system (Non-GMP).

The two systems has to be seperated due to validation but...
- user interface must be common for the whole system, so user won't see the differens
- alarms and events all are present in one alarmlist
- datalogging has to be bullit proof, no missing data



I like to know which system is the best/fastest regarding engineering?
The system are going to be upgraded with the plant still running, also several engineers will be handling changes constantly...
Which system is the most robust?
Which system do you think will live the longest?
Which system has the best historian?
Any experience with workflow applications, which system is the most flexible?



I like to hear from you guys/girls -which system you would recommend and why?
IFIX 5.5 or Wonderware System Platform 2012

Please don't start advising other systems :o)

PS. Do not think about license cost, because this will be a minor cost compared to engineering and implementation.
  Reply With Quote
Old November 12th, 2012, 02:24 PM   #2
bce123
Lifetime Supporting Member
United States

bce123 is offline
 
bce123's Avatar
 
Join Date: Feb 2011
Location: texas
Posts: 1,173
Quote:
Please don't start advising other systems :o)
I have no connection to Inductive Automation or there Ignition Software so that said:
Quote:
also several engineers will be handling changes constantly...
In theroy several hundred engineers could be working and making changes at the same time.....
Quote:
datalogging has to be bullit proof, no missing data
another reason to rethink your narrow choice of vendors I.M.H.O
__________________
"You can teach a dog to sit and lie down but then he justs gets lazy"
  Reply With Quote
Old November 12th, 2012, 02:51 PM   #3
tisbris
Member
Denmark

tisbris is offline
 
Join Date: Nov 2009
Location: Greve
Posts: 9
Quote:
Originally Posted by bce123 View Post
I have no connection to Inductive Automation or there Ignition Software so that said:

In theroy several hundred engineers could be working and making changes at the same time.....

another reason to rethink your narrow choice of vendors I.M.H.O
Inductive and Ignition is not very common here in EU so havn't looked at these. The reason that we have ended up with ww and ifix is due to the option of a integrated workflow application that we need.

Please explain why we should rethink our choices - bacnet support trendlog local in the device, so if scada is offline, then device is collecting?
  Reply With Quote
Old November 12th, 2012, 03:22 PM   #4
jfuehring
Member
United States

jfuehring is offline
 
Join Date: Nov 2012
Location: Masssena, NY
Posts: 3
I am working with both Wonderware and iFix. Wonderware is a little easier to grasp for new people, and the tag database is pretty easy to work with. Scripting is confined to the Wonderware commands, but is adequate for just about anything you want to do.
If you are a fan of VBA and want to add that kind functionality to your applications, iFix is a good choice. As far as reliability, they are both excellent. iFix has a tag database that is more complex, with a greater variety of I/O and internal blocks, and a nice system for transferring data to an access or sql database. If I had to choose one I would probably go with iFix because of the above but one thing to keep in mind is that if you are adding VB routines to your application it is very important to document the modifications so that they can be understood by others. iFix is at version 5.X and around version 3 they did a change that resulted in some of the VB commands being obsolete. Only good documentation allows for you to upgrade the commands in a reasonable amount of time.
  Reply With Quote
Old November 12th, 2012, 04:20 PM   #5
surferb
Lifetime Supporting Member
United States

surferb is offline
 
surferb's Avatar
 
Join Date: Jun 2007
Location: Naples, Italy
Posts: 1,734
What is the workflow application?

Quote:
Originally Posted by tisbris View Post
The reason that we have ended up with ww and ifix is due to the option of a integrated workflow application that we need.
__________________
Nathan Boeger, CISSP-ISSAP, CCVP/CCNA, MCSE, VCP
"Design Simplicity Cures Engineered Complexity"
Sierra Nevada Brewery MES/ERP case study - 5 minute video, My comments
Comment on Not another industrial software Blog
Ignition by Inductive Automation, rethinking SCADA for modern manufacturing 2 minute video
  Reply With Quote
Old November 12th, 2012, 04:40 PM   #6
bce123
Lifetime Supporting Member
United States

bce123 is offline
 
bce123's Avatar
 
Join Date: Feb 2011
Location: texas
Posts: 1,173
Quote:
Please explain why we should rethink our choices - bacnet support trendlog local in the device, so if scada is offline, then device is collecting?
spend 10 minutes at this site:
http://inductiveautomation.com/scada-software
then come back and ask or just give them a call and ask them, their much better at explaining it than myself.
__________________
"You can teach a dog to sit and lie down but then he justs gets lazy"
  Reply With Quote
Old November 12th, 2012, 09:02 PM   #7
RheinhardtP
Lifetime Supporting Member + Moderator
Australia

RheinhardtP is offline
 
RheinhardtP's Avatar
 
Join Date: Oct 2004
Location: Perth
Posts: 454
Ok,

So i can only state what i know of a system in this case it would be System Platform 2012.

One of the benefits are the object oriented aproach that it has. This gives it massive scalability and easy roll out. The important factor for me is always how long it would take to develop the "Standards" that i roll out. Most systems these days can go to pretty high IO counts and will be reliable if you implement them properly. Another benefit is that System Platform can provide all your requirements from one solution base. ArchestrA

I would reccomend using System Platform with the TOPserver as an IOServer. Lethal Combination and i am yes to see anything it cant do.

My response in Red to your questions.

The two systems has to be seperated due to validation but...
- user interface must be common for the whole system, so user won't see the differens

Not to sure what you mean here maybe explain a little more.If i understand you mean integration of 2 Scada packages. Not sure maybe elaborate here.

- alarms and events all are present in one alarmlist

So in this case you will have a Alarm Database which will be common. System Platform allows this.

- datalogging has to be bullit proof, no missing data

OK So System Platform has what they call storeforward. This means if your link to you Historian from you Object servers is down they Object server will store the Historian Data you specify up to which amount. When the connection is restored it will pass back all the stored data. Important factor here will be your architecture. Hardware locations ect.

The system are going to be upgraded with the plant still running, also several engineers will be handling changes constantly...

I believe any system can be managed in Parralel if you have sufficient hardware and planning.

Which system is the most robust?

Hard to say not knowing the condityions your servers will live under but most systenms these days are robust if you implement them correctly. Hardware and Software.

Which system do you think will live the longest?

Question should rather be how easy you can upgrade to follow on versions. Last couple of versions of system platform have been very smooth. No Issues.
Redundancy is very good and reliable . Quick switchover between object servers.

Which system has the best historian?

Again i can only speak on the WW side but the Wonderware Historian is very good very reliable. There is also the possibility of redundant Historian, no way you will lose data here.

Any experience with workflow applications, which system is the most flexible?

I recently went on a course for the integration of workflow into system platform. I know this capablity is part of your object orientated approach although i have not done a proper installation it looks promising.


I like to hear from you guys/girls -which system you would recommend and why?
IFIX 5.5 or Wonderware System Platform 2012

I have never worked with IFIX and dont know what the capablities are. Maybe one of the other members can give some more information.

Hope this helps.

Feel free if you have any other questions. I know the System Platform side pretty well, and will answer what i can.
__________________
“If a cluttered desk is a sign of a cluttered mind, of what, then, is an empty desk a sign?”

― Albert Einstein

Last edited by RheinhardtP; November 12th, 2012 at 09:05 PM.
  Reply With Quote
Old November 13th, 2012, 04:14 AM   #8
tisbris
Member
Denmark

tisbris is offline
 
Join Date: Nov 2009
Location: Greve
Posts: 9
Quote:
Originally Posted by jfuehring View Post
If you are a fan of VBA and want to add that kind functionality to your applications, iFix is a good choice.
The tech. crue that will maintane this system is not very good in VBA and from what I know everything inside iFix is controlled by VBA - from dynamoes to pages, please correct me if i am wrong.
This is my main concern on iFix, and also standadization across a large application.

Last edited by tisbris; November 13th, 2012 at 04:26 AM.
  Reply With Quote
Old November 13th, 2012, 04:18 AM   #9
tisbris
Member
Denmark

tisbris is offline
 
Join Date: Nov 2009
Location: Greve
Posts: 9
Quote:
Originally Posted by surferb View Post
What is the workflow application?
It's an application that can force the user to follow at predefined standard. We intend to use for our alarm handling, where the end user will get into the loop about what impact the specific alarm has on the product.

If you can draw a Visio flow, then it can be implemented into this workflow application and this workflow can use values from inside the scada system.

Overall a very flexible program, that can be used for almost everything...
  Reply With Quote
Old November 13th, 2012, 04:26 AM   #10
tisbris
Member
Denmark

tisbris is offline
 
Join Date: Nov 2009
Location: Greve
Posts: 9
Quote:
Originally Posted by RheinhardtP View Post
Ok,


The two systems has to be seperated due to validation but...
- user interface must be common for the whole system, so user won't see the differens

Not to sure what you mean here maybe explain a little more.If i understand you mean integration of 2 Scada packages. Not sure maybe elaborate here.

- alarms and events all are present in one alarmlist

So in this case you will have a Alarm Database which will be common. System Platform allows this.

Thank you for you detailed reply.

We are looking for a solution, where each system GMP and Non.GMP is isolated at most (not only on objects).

The upcomming release of system platform is supporting 2 seperate galaxies to communicate with each other.

Please explain your experinece with System platform when it comes to engineering og standardization - we believe that this system will force the engineer to use the standards and also reduce the overall engineering cost?
  Reply With Quote
Old November 13th, 2012, 10:22 AM   #11
RheinhardtP
Lifetime Supporting Member + Moderator
Australia

RheinhardtP is offline
 
RheinhardtP's Avatar
 
Join Date: Oct 2004
Location: Perth
Posts: 454
Quote:
Originally Posted by tisbris View Post
Thank you for you detailed reply.


We are looking for a solution, where each system GMP and Non.GMP is isolated at most (not only on objects).

The upcomming release of system platform is supporting 2 seperate galaxies to communicate with each other.

Please explain your experinece with System platform when it comes to engineering og standardization - we believe that this system will force the engineer to use the standards and also reduce the overall engineering cost?

It is already possible using other methods to have 2 Galaxies transfer data between them,im looking forward to the new release.

The hard part of the engineering is defining building and commissioning your master objects (Standards). From here it is really easy to create instances. The fact is that object based software gives you the power to instantiate very easily. I hardly ever create instances by hand. I use *.csv imports and takes me seconds to create as many objects as i want.

Its all about how you design your objects. With good data structures in your PLC you dont even have to do addressing you can derive addresses and only use device numbers that uses indirect addressing with offsets.

System Platform is a POWERFUL product i will always recommend it..
__________________
“If a cluttered desk is a sign of a cluttered mind, of what, then, is an empty desk a sign?”

― Albert Einstein

Last edited by RheinhardtP; November 13th, 2012 at 10:25 AM.
  Reply With Quote
Old November 14th, 2012, 12:36 PM   #12
PDS
Member
Belgium

PDS is offline
 
Join Date: Jul 2009
Location: Belgium
Posts: 7
while it is true that almost everything in ifix runs on VBA, the actual amount of custom scripting can be kept to an absolute minimum. There are wizards available for most basic tasks like changing pictures.

alarms in one place is off course possible, but filtering is too.

iFIX has extensive redundancy capabilities. For datalogging there is iHistorian, with its own redundancy and capable of dealing with ifix redundancy as well.

iFIX can be troublesome at times, specially with larger systems with allot of clients (at the moment i have a system running with 12 ifix servers, historian and arround 30 clients, it is challenging at times) if you need to add allot of tags you will need to generate those in excel.

Last edited by PDS; November 14th, 2012 at 12:39 PM.
  Reply With Quote
Old November 17th, 2012, 08:10 AM   #13
tisbris
Member
Denmark

tisbris is offline
 
Join Date: Nov 2009
Location: Greve
Posts: 9
if we choose wonderware, we like to seperate this project into two galaxies - GMP and NonGMP.

I believe we need to make two intouch application - one in each galaxy.

My question is how can the user jump from one intouch appliction to another?
  Reply With Quote
Old November 19th, 2012, 08:24 PM   #14
RheinhardtP
Lifetime Supporting Member + Moderator
Australia

RheinhardtP is offline
 
RheinhardtP's Avatar
 
Join Date: Oct 2004
Location: Perth
Posts: 454
I dont think there is a easy way to do this. There is tools available like thinmanager that can ghelp you manage multiple applications. We are currectly looking at using ThinManager for a couple of other projects. You can select which applications you want to run on different machines.

There are many benefits using this product.

Link http://www.thinmanager.com
__________________
“If a cluttered desk is a sign of a cluttered mind, of what, then, is an empty desk a sign?”

― Albert Einstein
  Reply With Quote
Old November 19th, 2012, 11:44 PM   #15
randheerp
Member
India

randheerp is offline
 
Join Date: Aug 2006
Location: Bangalore
Posts: 77
iFix iFix iFix iFix iFix iFix iFix iFix iFix iFix
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Scada system questions Oakley LIVE PLC Questions And Answers 2 December 17th, 2007 12:36 PM
Manual/Auto jthornton LIVE PLC Questions And Answers 9 October 5th, 2006 12:40 PM
Best way to upgrade a SCADA system Johnny T LIVE PLC Questions And Answers 10 May 3rd, 2005 03:38 AM
PID - A challenge, is a PID good enough? Peter Nachtwey LIVE PLC Questions And Answers 19 July 18th, 2004 10:10 PM
auto logout in iFix 3.5 SCADA annette2002 LIVE PLC Questions And Answers 1 May 5th, 2004 06:53 AM


All times are GMT -5. The time now is 08:34 PM.


.