Fancy Exclamation Need Help Omron

need help
hi all
I have plc omron (cpu CQM1H)
I used with a system many Digital inputs many Digital & analog outputs
one Digital output module has Dameged I replace with a new one
after that the analog output which control the frequncy of many inverters was STOP & this is the problem.
  Reply With Quote
Old March 15th, 2004, 07:57 AM   #2
Jay Anthony
Member
United States

Jay Anthony is offline
 
Jay Anthony's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX
Posts: 645
Did you replace the digital output module with the exact same type?
Did you put the output module in the exact same order?
If not, the addressing is different for the whole system.
  Reply With Quote
Old March 15th, 2004, 08:08 AM   #3
Sameh
Member
Syria

Sameh is offline
 
Sameh's Avatar
 
Join Date: Mar 2004
Location: Damascus
Posts: 4
thanks Jay Anthony
but I replace the digital output module with the exact same type
&I put the output module in the exact same order.
  Reply With Quote
Old March 15th, 2004, 10:42 AM   #4
Jay Anthony
Member
United States

Jay Anthony is offline
 
Jay Anthony's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX
Posts: 645
What's the module address for the DA002?
  Reply With Quote
Old March 15th, 2004, 11:23 AM   #5
ArikBY
Member
Israel

ArikBY is offline
 
ArikBY's Avatar
 
Join Date: Oct 2003
Location: Oranit Israel
Posts: 1,433
Jay

What you mean DA002. I never saw this term.
__________________
Arik

Barak Control Israel
  Reply With Quote
Old March 15th, 2004, 01:36 PM   #6
Jay Anthony
Member
United States

Jay Anthony is offline
 
Jay Anthony's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX
Posts: 645
Ok, sorry...
CQM1-DA021
  Reply With Quote
Old March 15th, 2004, 09:04 PM   #7
Vicente Jasareno
Member
Philippines

Vicente Jasareno is offline
 
Join Date: Mar 2004
Location: Kita-ku, Nagoya, Japan
Posts: 9
Maybe the PLC is in PROGRAM mode

Dear Sameh,

I was reading the operation manual of CQM1H (catalog no. W363-E1-2), Section 6 describe the DIP switch settings of CQM1 PLC. I found out that there is DIP switch setting (pin 7) that determine the operation mode of CQM1 upon power up of the PLC. base on the manual, if no device was connected to the PLC (for example hand-held programming terminal) and pin 7 is off on power up the PLC will be in PROGRAM mode but if pin 7 is on, on power up the PLC will be in RUN mode.

If the PLC is in PROGRAM all outputs are disabled.

see the link below for your reference

http://www.trascon.ru/dynamic/manage...s/w363e1-2.pdf
  Reply With Quote
Old March 16th, 2004, 08:02 AM   #8
Sleepy Wombat
Member
Australia

Sleepy Wombat is offline
 
Sleepy Wombat's Avatar
 
Join Date: Oct 2003
Posts: 139
Did you put the CQM1-IPS01 OR CQM1-IPS02 back on the system and connect it also ?
  Reply With Quote
Old March 16th, 2004, 08:41 AM   #9
Sameh
Member
Syria

Sameh is offline
 
Sameh's Avatar
 
Join Date: Mar 2004
Location: Damascus
Posts: 4
Jay Anthony
I am using CQM1H-CPU51

Vicente Jasareno
the pin7 is on & all machine is runing , the analog outputs are not effective & it's power led is on.
thanks for the PDF file I read it.


Sleepy Wombat
the system is running


thank's all .
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
communication b/n omron E5ZN temp controller with omron plc karikalan LIVE PLC Questions And Answers 1 February 23rd, 2010 01:52 AM
Wanted technical support for Omron PLC (Sysmac: C 60 K) kailashmariappan LIVE PLC Questions And Answers 0 December 1st, 2004 11:37 AM
Omron Plc c_gunner LIVE PLC Questions And Answers 8 February 22nd, 2004 11:38 PM
Omron NT 31C Programming -> NTST 3.3 Chris Rhodan LIVE PLC Questions And Answers 2 November 19th, 2003 04:53 PM
Omron 3F88L-132 rotory encoder (kinda like a PLC) Tough_Duck LIVE PLC Questions And Answers 3 June 15th, 2002 07:23 PM


All times are GMT -5. The time now is 12:23 PM.


.