#1 |
|
Member
|
need help
hi all I have plc omron (cpu CQM1H) I used with a system many Digital inputs many Digital & analog outputs one Digital output module has Dameged I replace with a new one after that the analog output which control the frequncy of many inverters was STOP & this is the problem. |
|
|
|
#2 |
|
Member
|
Did you replace the digital output module with the exact same type?
Did you put the output module in the exact same order? If not, the addressing is different for the whole system. |
|
|
|
#3 |
|
Member
|
thanks Jay Anthony
but I replace the digital output module with the exact same type &I put the output module in the exact same order. |
|
|
|
#4 |
|
Member
|
What's the module address for the DA002?
|
|
|
|
#5 |
|
Member
|
Jay
What you mean DA002. I never saw this term.
__________________
Arik Barak Control Israel
|
|
|
|
#6 |
|
Member
|
Ok, sorry...
CQM1-DA021 |
|
|
|
#7 |
|
Member
![]() Join Date: Mar 2004
Location: Kita-ku, Nagoya, Japan
Posts: 9
|
Maybe the PLC is in PROGRAM mode
Dear Sameh,
I was reading the operation manual of CQM1H (catalog no. W363-E1-2), Section 6 describe the DIP switch settings of CQM1 PLC. I found out that there is DIP switch setting (pin 7) that determine the operation mode of CQM1 upon power up of the PLC. base on the manual, if no device was connected to the PLC (for example hand-held programming terminal) and pin 7 is off on power up the PLC will be in PROGRAM mode but if pin 7 is on, on power up the PLC will be in RUN mode. If the PLC is in PROGRAM all outputs are disabled. see the link below for your reference http://www.trascon.ru/dynamic/manage...s/w363e1-2.pdf |
|
|
|
#8 |
|
Member
|
Did you put the CQM1-IPS01 OR CQM1-IPS02 back on the system and connect it also ?
|
|
|
|
#9 |
|
Member
|
Jay Anthony
I am using CQM1H-CPU51 Vicente Jasareno the pin7 is on & all machine is runing , the analog outputs are not effective & it's power led is on. thanks for the PDF file I read it. Sleepy Wombat the system is running thank's all . |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| communication b/n omron E5ZN temp controller with omron plc | karikalan | LIVE PLC Questions And Answers | 1 | February 23rd, 2010 01:52 AM |
| Wanted technical support for Omron PLC (Sysmac: C 60 K) | kailashmariappan | LIVE PLC Questions And Answers | 0 | December 1st, 2004 11:37 AM |
| Omron Plc | c_gunner | LIVE PLC Questions And Answers | 8 | February 22nd, 2004 11:38 PM |
| Omron NT 31C Programming -> NTST 3.3 | Chris Rhodan | LIVE PLC Questions And Answers | 2 | November 19th, 2003 04:53 PM |
| Omron 3F88L-132 rotory encoder (kinda like a PLC) | Tough_Duck | LIVE PLC Questions And Answers | 3 | June 15th, 2002 07:23 PM |