plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old January 14th, 2013, 10:08 AM   #1
spatricks
United States
spatricks is offline
Debouncing Timer on Micro 830 in Structured Text
I am wanting to debounce an digital input in structured text. I am using connected componets with a MICRO 830 2080-LC30-24-QWB.
So I essentially want to debounce both HIGH->LOW transitions and LOW->HIGH transitions to account for ripple in our digital sensors.
I have the following code that detects transitions like stated above, the problem is the code will react to any momentary ripple. I am wanting to debounce for at least 1 second.
Code:
(*Digital Input 0*)
(*Check for 1-to-0 transition*)
UTIL_input0_f(_IO_EM_DI_00);
(*If 1-to-0 transition detected, send out alarm message*)
IF UTIL_input0_f.Q = TRUE THEN
    DATA_inputONOFFSMSText := '';
	DATA_inputONOFFSMSText := 'Alarm detected: Input 0 is OFF';
	UTIL_SEND_SMS_2( TRUE, CONFIG_slotID, CONFIG_receiverList, DATA_inputONOFFSMSText);
END_IF;
(*Check for 0-to-1 transition*)
UTIL_input0_r(_IO_EM_DI_00);
(*If 0-to-1 transition detected, send out alarm message*)
IF UTIL_input0_r.Q = TRUE THEN
	DATA_inputONOFFSMSText := 'Alarm detected: Input 0 is ON';
END_IF;
Could someone give me a code example that would debounce this for 1 second.
Old January 14th, 2013, 10:31 AM   #2
dmargineau
United States
dmargineau is offline
dmargineau's Avatar
You will need to add a "One_Second_Timer" TON to your project and "enable" it when UTIL_input0_f(_IO_EM_DI_00)is true.
Within your code, replace every occurrence of UTIL_input0_f with One_Second_Timer/DN.
Old January 14th, 2013, 10:43 AM   #3
spatricks
United States
What is /DN?
Old January 14th, 2013, 10:56 AM   #4
dmargineau
United States
dmargineau's Avatar
.DN = Timer "Done" bit; it is set (true) when the timer's accumulated value is equal to the preset value (the timer has timed out).
Old January 14th, 2013, 10:57 AM   #5
spatricks
United States
This results in an infinite loop that keeps sending messages that it is on
Code:
TEST_TON(_IO_EM_DI_00,TEST_MAXTIME);
IF TEST_TON.Q = TRUE THEN
END_IF;
I don't see
EDIT, I don't see that I have access to a .DN bit
Old January 14th, 2013, 11:17 AM   #6
dmargineau
United States
dmargineau's Avatar
I see...Set TEST_TON.PT to 1000 (I believe the CCW Timer base is ms) and use the TEST_TON.Q BOOL operand instead of the "classic" .DN bit.
Old January 14th, 2013, 11:37 AM   #7
spatricks
United States
Like I did in the code I posted? If so that code will get stuck in an infinite loop.
Old January 14th, 2013, 12:03 PM   #8
dmargineau
United States
dmargineau's Avatar
This is so much easier in ladder logic...
I don't see the "Preset" of the timer within your code.
TEST_TON.Q will not be true until TEST_TON.PT has elapsed due to a 1-to-0 transition of (_IO_EM_DI_00) longer than the TEST_TON.PT value.
Old January 14th, 2013, 12:20 PM   #9
spatricks
United States
TEST_TON.PT is TEST_MAXTIME which is 3s. Is this not a valid way to set the PT?
Old January 14th, 2013, 01:11 PM   #10
dmargineau
United States
dmargineau's Avatar
Yes it is...For one second it would be T#1s...
Now I see what's going on...Is (_IO_EM_DI_00) wired up NC ?...If Digital Input 1 is TRUE at all times except when the "event" takes place (1-to-0 transition/falling edge) you might want to use a TOF (Timer OFF) instruction) instead of the TON.
If you want to detect both edges, you will have to deploy two timers (a TON for the rising edge, and a TOF for the falling edge) within an OR statement logic.
Old January 14th, 2013, 01:27 PM   #11
spatricks
United States
I figured it out. Thanks for your help! This is what I settled on using a TONOFF
Code:
TIMER_DEBOUNCE_DI_0(_IO_EM_DI_00,TEST_MAXTIME,TEST_MAXTIME);
UTIL_input0_r(TIMER_DEBOUNCE_DI_0.Q);
UTIL_input0_f(TIMER_DEBOUNCE_DI_0.Q);
   DATA_inputONOFFSMSText := 'Alarm detected: Input 1 is ON';
END_IF;
	DATA_inputONOFFSMSText := 'Alarm detected: Input 1 is OFF';
END_IF;
Old January 14th, 2013, 01:51 PM   #12
dmargineau
United States
dmargineau's Avatar
No problem...Haven't done any STL on CCW yet...Up until now...
Never even thought of using anything but ladder logic on a machine level CPU...
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Modicon Structured Text snipe LIVE PLC Questions And Answers 1 December 4th, 2003 01:35 PM
RS 5000 Structured Text olias LIVE PLC Questions And Answers 10 October 14th, 2003 02:20 AM
Documentation on Structured Text cmulder LIVE PLC Questions And Answers 13 June 11th, 2003 10:10 AM
Structured Text Programming Martin IRL LIVE PLC Questions And Answers 3 January 21st, 2003 11:49 AM