Old February 6th, 2013, 02:37 PM   #1
Ali Sayghe
Member
United States

Ali Sayghe is offline
 
Join Date: Sep 2012
Location: Tempe
Posts: 14
Exclamation analog input in ladder logic

Hi all
I am trying write a program that has analog input from a pressure sensor in a thank that read the pressure sensor for low level and high level when the pump start filling up the tank the motor for gate valve is closed when the water reach the high level the motor for the gate valve will open so the input and the output is:
input I:0/1 from limit switch 1 to turn off the motor when its opening the valve
input I:0/2 from limit switch 2 to turn off the motor when its closing the valve
input I:2/1 analog input from pressure sensor
turn output O/0 when the signal from pressure sensor is low (111)
turn output O/1 when the signal from presser sensor is high (25000)
I have a 1769-IF8 Analog Input Card in a Micrologix 1500 system.
  Reply With Quote
Old February 6th, 2013, 02:45 PM   #2
passwordg
Member
United States

passwordg is offline
 
Join Date: Aug 2011
Location: Alabama
Posts: 121
Hey, I did not understand what your question is.
  Reply With Quote
Old February 6th, 2013, 03:05 PM   #3
Lancie1
Lifetime Supporting Member + Moderator
United States

Lancie1 is online now
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 9,305
Quote:
...Input I:2/1 [is] the analog input from pressure sensor.
Beacause you are using a 1769-IF8 analog module, I think this analog input should be at address I:2.1 or I:2.0. In other words, it must be a word address instead of a bit address.

Quote:
I am trying to write a program...
If you would print your program to a PDF file, or ZIP it to a compresed file, and post it here, I am sure someone can help with your problem.

Your action elements are simple and only two:
"CLOSE VALVE MOTOR" and "OPEN VALVE MOTOR". Put two rungs in your program for those Outputs, and you will have a place to start.

Remember, the Inputs do not control the valve, but instead your PLC outputs control the motor that controls the valve.

Last edited by Lancie1; February 6th, 2013 at 03:08 PM.
  Reply With Quote
Old February 6th, 2013, 09:55 PM   #4
Ali Sayghe
Member
United States

Ali Sayghe is offline
 
Join Date: Sep 2012
Location: Tempe
Posts: 14
Quote:
Originally Posted by Lancie1 View Post
Beacause you are using a 1769-IF8 analog module, I think this analog input should be at address I:2.1 or I:2.0. In other words, it must be a word address instead of a bit address.

If you would print your program to a PDF file, or ZIP it to a compresed file, and post it here, I am sure someone can help with your problem.

Your action elements are simple and only two:
"CLOSE VALVE MOTOR" and "OPEN VALVE MOTOR". Put two rungs in your program for those Outputs, and you will have a place to start.

Remember, the Inputs do not control the valve, but instead your PLC outputs control the motor that controls the valve.
yes you right i am controlling the valve through the dc motor but my problem is i don't know how can i use less than and more than function to turn the motor whether closing if the level is low or opening if the level is high according to the pressure of the tank the value that indicate low level is 500 and the valve indicate high level 20000 am using the raw/proportional unit for the analog input card. I am using SCP for to scale the input
Attached Images
File Type: jpg untitled.jpg (22.6 KB, 167 views)
  Reply With Quote
Old February 7th, 2013, 07:10 AM   #5
Anirban Hazra
Member
India

Anirban Hazra is offline
 
Anirban Hazra's Avatar
 
Join Date: Jan 2013
Location: Kolkata
Posts: 192
Quote:
Originally Posted by Ali Sayghe View Post
..my problem is i don't know how can i use less than and more than function to turn the motor whether closing if the level is low or opening if the level is high according to the pressure of the tank..
The Logic in the Attached Image shows how to do the above with the I/O addresses provided by you in Post #1 and #4.

However, note that if your motor is very slow and the rate of filling is lesser than the rate of emptying through a partially opened valve then you will need to latch the "Open valve" output till it reaches the limit switch because the level may drop before the valve position reaches the limit switch and turn the motor off.

Inversely if your motor is very slow and the rate of filling is greater than the rate of emptying through a partially closed valve then you will need to latch the "Close valve" output till it reaches the limit switch because the level may increase before the valve position reaches the limit switch and turn the motor off.
Attached Images
File Type: jpg Valve Motor.JPG (22.5 KB, 151 views)
__________________
Anirban Hazra
Real Time Engineering Pvt. Ltd.
Authorized Channel Partner
of Rockwell Automation


Click to Connect with me on:
Facebook
LinkedIn

Last edited by Anirban Hazra; February 7th, 2013 at 07:29 AM.
  Reply With Quote
Old February 7th, 2013, 07:12 AM   #6
iant
Lifetime Supporting Member + Moderator
Australia

iant is offline
 
iant's Avatar
 
Join Date: May 2002
Location: Melbourne
Posts: 3,507
just a note
is the analogue 0~10V or 4~20 mA
because the min max scaling is different for the two
__________________

Give all the answers
- People seldom learn.

Guide People to the posibilities
- Their Answers will come easily.
- Their Knowledge will grow.

They will then teach others

Regards
Ian Trost
  Reply With Quote
Old February 7th, 2013, 05:49 PM   #7
Ali Sayghe
Member
United States

Ali Sayghe is offline
 
Join Date: Sep 2012
Location: Tempe
Posts: 14
Quote:
Originally Posted by Anirban Hazra View Post
The Logic in the Attached Image shows how to do the above with the I/O addresses provided by you in Post #1 and #4.

However, note that if your motor is very slow and the rate of filling is lesser than the rate of emptying through a partially opened valve then you will need to latch the "Open valve" output till it reaches the limit switch because the level may drop before the valve position reaches the limit switch and turn the motor off.

Inversely if your motor is very slow and the rate of filling is greater than the rate of emptying through a partially closed valve then you will need to latch the "Close valve" output till it reaches the limit switch because the level may increase before the valve position reaches the limit switch and turn the motor off.
Thank you very much its really works and i attached the final program
Attached Images
File Type: jpg yuy.JPG (32.6 KB, 133 views)
  Reply With Quote
Old February 7th, 2013, 11:47 PM   #8
Anirban Hazra
Member
India

Anirban Hazra is offline
 
Anirban Hazra's Avatar
 
Join Date: Jan 2013
Location: Kolkata
Posts: 192
Quote:
Originally Posted by Ali Sayghe View Post
Thank you very much its really works and i attached the final program
Glad to have Helped.
__________________
Anirban Hazra
Real Time Engineering Pvt. Ltd.
Authorized Channel Partner
of Rockwell Automation


Click to Connect with me on:
Facebook
LinkedIn
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
what should i do, my analog input cant read the analog value? kartika LIVE PLC Questions And Answers 0 September 9th, 2012 11:14 PM
Scalling for analog input module - SLC 5/04 ckchew666 LIVE PLC Questions And Answers 1 May 15th, 2008 09:31 AM
direct logic D3-04AD 4 channel analog input Nathan Hendrix LIVE PLC Questions And Answers 3 December 2nd, 2004 02:12 PM
Analog input issue! NoName LIVE PLC Questions And Answers 9 July 8th, 2004 04:10 AM
Micro Logix 1000 Analog input comparision mikewood LIVE PLC Questions And Answers 5 June 21st, 2004 12:41 PM


All times are GMT -5. The time now is 01:19 PM.


.