plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old February 20th, 2013, 04:51 PM   #1
m.peric87
Serbia
m.peric87 is offline
1756 if16 Analog Input
I need a help to calibrate analog input 4-20mA.
This is how it should be 4mA=0;20mA=940,
but I'm getting a mistake on input.
4mA=-77; 20mA=863.
How to calibrate current input when there is only voltage calibration on card.
Please help
Old February 20th, 2013, 05:28 PM   #2
Bit_Bucket_07
United States
Bit_Bucket_07 is offline
Bit_Bucket_07's Avatar
Sounds like you are more interested in "scaling" of the analog input channels than in "calibrating" the channels. As for current inputs, they are really only voltage inputs anyway from the module's point of view. Your 4-20mA signal is converted to a 1-5 VDC signal via a 250 ohm resistor across the input terminals.
Old February 20th, 2013, 08:13 PM   #3
daba
United Kingdom
daba is offline
daba's Avatar
If, and a big IF, you are confident that 4.00mA and 20.00mA inputs give you those values you have quoted, then by all means attempt the calibration procedure detailed in the manual for the module. You WILL need an accurate voltage/current source to do this.
However, you readings are so far away from "expected" that i think your 4 and 20mA signals are not 4 and 20mA.
How have you measured these?
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old February 20th, 2013, 08:44 PM   #4
Ron Beaufort
United States
Ron Beaufort is offline
Ron Beaufort's Avatar
have you installed the proper jumpers as part of the wiring on the module's terminal strip? ...
the 250 ohm resistor that's been mentioned above is located INSIDE the module - and the only way to include it in the circuit is by properly using a jumper as part of the wiring ...
and be sure that you consider whether you're using DIFFERENTIAL or SINGLE-ENDED wiring for your system ... there is a separate wiring diagram for each method ...
__________________
2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
I once was lost, but now am found, was blind, but now I see.
Old February 21st, 2013, 02:36 AM   #5
m.peric87
Serbia
I used a accurate curent source to see is there is a mistake on input. (also used a digital multimetar to check curent source)
Signal is good, but problem still exist.
4mA= -77 ; 20mA= 863 =>77+863=940.
Channel which I need to calibrate is 11. That mean 26 IN and 25iRTN.
I read a manuall. But I'm not really sure what to do.
Do I need to set voltage calibrator on 25 IN(+DC) & 9 RTN(-DC), and set 0 V for Low Reference(Volts), and 10 V for High Reference(Volts) in calibration tab on the module properties.
Old February 21st, 2013, 04:08 AM   #6
sthompson
Canada
sthompson is offline
sthompson's Avatar
The 1756 Analog Cards can be Scaled in the Card.
You don't just have some weird Scaling Values in that Channel do you?
Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
Old February 21st, 2013, 04:31 AM   #7
m.peric87
Serbia
I also tried on free input channel 15(36 IN & 35 iRTN) with 4-20mA and there is the same result. 4mA= (-77); 5,6mA=14 and 20mA=863.
I also try to put a new Analog 1756 and the results are the same with low diference. 5.6mA=18; 20mA=867
For rest I will do measurement. Scaling is as in figure.
Old February 21st, 2013, 05:12 AM   #8
ianingram
Australia
ianingram is offline
Last edited by ianingram; February 21st, 2013 at 05:26 AM. Reason: wrong info given
Old February 21st, 2013, 05:19 AM   #9
sthompson
Canada
sthompson's Avatar
Quote:
Originally Posted by ianingram View Post
Is there an option under Input Range of 4-20mA.
The config above will give 0 with 0mA, not 4mA
Hi Ian:
Actually, 0-20mA is the only selection for Current Input. The setup shown will give you 0 at 4 mA, it is just the way things work on the 1756-IF16.
Stu....
__________________
Old February 21st, 2013, 05:38 AM   #10
ianingram
Australia
I will try again..
Should the low signal = -235
then the high signal =940
Copy & paste from excel..
0 -235
1 -176.25
2 -117.5
3 -58.75
4 0
5 58.75
6 117.5
7 176.25
8 235
9 293.75
10 352.5
11 411.25
12 470
13 528.75
14 587.5
15 646.25
16 705
17 763.75
18 822.5
19 881.25
20 940
Old February 21st, 2013, 06:50 AM   #11
Ron Beaufort
United States
so apparently you're using Single-Ended wiring for current ... here's the diagram ...
actually it means 26 IN and 25iRTN - AND - a jumper from 25iRTN to RTN ...
so ... did you install the jumper? ...
I HIGHLY recommend that you quit thinking about "calibration" and look at the wiring - and the scaling ... the big question would be "how did the module get THIS FAR out of calibration in the first place?" ... unless someone has already been messing around with the calibration settings, the chances are VERY slim that "calibration" is going to fix your problem ...
__________________
2-B ?
Ron | |
Old February 21st, 2013, 07:49 AM   #12
Bit_Bucket_07
United States
You perform the calibration for 0-10 VDC and this will assure proper calibration of the channel for all possible configurations. That said, small deviations in your voltage dropping resistors could still result in slight inaccuracy. Since this module's only current input selection is for 0-20mA, you will need to scale the input appropriately to account for the zero offset.
If it were my choice, I'd set the module up to return full 16 bit resolution and then scale the analog input to Engineering Units in my program logic or HMI. That would allow you to easily compensate for any deviation in input resistor value from channel to channel.
Old February 21st, 2013, 09:13 AM   #13
m.peric87
Serbia
I have done measurements another two channels.
Channel 12: Zone 2 Air flow
Scaling for Low 4mA=0; High 20mA=4000
But with input 9.32mA I have 1186 instead of 1330.
Channel 13: Zone 2 Gas flow
Scaling for Low 4mA=0; High 20mA=360
But with input 10.6mA I have 121 instead of 148,64.
That mean all input are wrong.
What than I should to do to fix this?
Old February 21st, 2013, 09:44 AM   #14
m.peric87
Serbia
I still didn't try to install jumper. I need to wait weekend when factory stop Furnace. Until then I need to prepare what to do. But I'm without idea if calibration is not right solution, because I checked wiring, and signal. And everything seems to be ok, unless reading on 1756
And what do you mean to look in the scaling?
Old February 21st, 2013, 10:04 AM   #15
dmargineau
United States
dmargineau is offline
dmargineau's Avatar
Find the respective Analog Input module within the RSL5K hardware "tree", right-click it, choose Properties and pick the Configuration tab; within the resulting applet you will find the scaling for each of the module's points.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
help with 1756 enbt ethernet card larry austin LIVE PLC Questions And Answers 3 October 12th, 2012 08:52 PM
allen bradley 1756 enbt v3.9 to v4.7 larry austin LIVE PLC Questions And Answers 2 October 9th, 2012 01:57 PM
RSView32 Runtime with 1756 L55M14 Controller RZR LIVE PLC Questions And Answers 0 April 13th, 2012 08:25 AM
AB 1756 CNB E - "TEST" displayed backwards???? colly LIVE PLC Questions And Answers 1 October 23rd, 2010 03:27 AM
1756-IB16 and 1756 OB16E VigneshGunasekaran LIVE PLC Questions And Answers 1 April 28th, 2010 06:31 AM