kapil2910
India
kapil2910 is offline
Sensor and contactor
Hello,
Is it possible to hold the Electrical "Contactor" using a Single pulse of Sensor...???
I want to hold the "Contactor" using a single Pulse of the sensor.. Please help.
Old March 10th, 2013, 06:08 PM   #2
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Kapil,
Yes, it is possible to cause a contactor to be held ON due to a single pulse from a sensor. However, you will need some other equipment (other than the sensor pulse and the contactor).
Please list the equipment that you are using. Because you came to a PLC site, I assume that you are using some PLC brand, model, and catalog number. If you list the brand of the PLC, the contactor, and the sensor, and state how long that your sensor input is ON, then we can go from there to answer your question.
Old March 10th, 2013, 11:49 PM   #3
jad51
New Zealand
jad51 is offline
Yeah you could also use a set command (omron/ telemechanique) same as hold command, I think. You will also need to be able to reset the contactor using a reset command. How are you going to do this?
You may also need to create a interrupt function if the pulse is on for a short time.
If you are not using a plc the you could just do it with a normally open contact on your contactor, this will be more dependent on the speed of the pulse as contactors are a lot slower than PLC's which are inturn slower than industrial PC's
Old March 11th, 2013, 02:06 AM   #4
iant
Australia
iant is offline
iant's Avatar
is this hard wired?
__________________
Give all the answers
- People seldom learn.
Guide People to the posibilities
- Their Answers will come easily.
- Their Knowledge will grow.
They will then teach others
Regards
Ian Trost
Old March 11th, 2013, 08:49 AM   #5
kapil2910
India
I m Not Using PLC, But is it possible to use a Latching relay between the Sensor and Contactor to hold the Contactor by single pulse of Sensor...... Please give feedback
Old March 11th, 2013, 09:12 AM   #6
ojz0r
Sweden
ojz0r is offline
Quote:
Yes it's possible, but how will you reset it once it latches?
Old March 11th, 2013, 05:27 PM   #7
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Quote:
But is it possible to use a Latching relay between the Sensor and Contactor to hold the Contactor by single pulse of Sensor...... Please give feedback.
Okay. Without knowing the brand and catalog number of your contactor, sensor, and relay, then here is a generic version with a generic pulse stretcher. With more information from you, I could give you more information in return.
Here are some pulse stretchers at this link. I do not know which one you need because it depends on the voltage of the circuit, the sensor, the relay, and so on. A retriggable monostable multivibrator is one type of electronic circuit that can be used as a pulse strectcher. You may not need the latching relay.
http://www.arcade-electronics.com/NT...p/nte-9675.htm
File Type: jpg Contactor Seal-in from One Sensor Pulse.JPG (29.8 KB, 82 views)
Old March 11th, 2013, 07:39 PM   #8
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
This version would be safer and preferred, unless your instructions specify the latching relay.
File Type: jpg Contactor Seal-in from One Sensor Pulse R1.JPG (21.3 KB, 76 views)
Old March 12th, 2013, 02:16 AM   #9
kapil2910
India
Thankyou for your advices, I appriciate.....
Old March 12th, 2013, 02:23 AM   #10
Anirban Hazra
India
Anirban Hazra is offline
Anirban Hazra's Avatar
This circuit diagram will help give you an idea on how to construct a hard-wired Latch:
__________________
Anirban Hazra
Real Time Engineering Pvt. Ltd.
Authorized Channel Partner
of Rockwell Automation
Click to Connect with me on:
Facebook
LinkedIn
Old March 12th, 2013, 06:18 AM   #11
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
How long is your sensor input pulse in the ON state (miliseconds, nanoseconds, seconds)?
Old March 16th, 2013, 01:37 PM   #12
kapil2910
India
It will be in milliseconds
Old March 16th, 2013, 04:48 PM   #13
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Then you definitely will need some electronic device that can "see" or read the milisecond-range pulse and convert it to a Start signal for a contactor. A pulse-stretcher is one such device. There are probably some solid-state relays that could react fast enough to turn on when triggered by a 10 milisecond pulse.
Yes, I see that the Opto Solid-State AC Relays will trigger or operate in 0.5 cycles, and some of the DC relays have a turn on time as short as 100 microseconds (0.1 miliseconds). At 60 cycles per second, 0.5 cycles is a 8.33 millisecond pulse required to operate the solid-state relay. Make sure that your pulse is 1.5 to 2 times longer than the minimum relay turn-on time. Then you would probably need a second electro-mechanical seal-in relay to seal in your contactor.
Old March 16th, 2013, 06:18 PM   #14
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Most common solid state timers may serve as a "pulse stretcher". I think Phoenix makes a din rail version of it.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old March 16th, 2013, 06:24 PM   #15
Lancie1
United States
Lancie1 is offline
Lancie1's Avatar
Okie, a solid-state timer is a brilliant solution. I wish I had thought of that!
The timer timed output (of 2 or 3 seconds duration) could be wired directly to the contactor, with a contacor seal-in contact to hold the contactor on until turned off by a stop button.
Reply