Old March 14th, 2013, 09:44 AM   #1
bright676
Member
United States

bright676 is offline
 
Join Date: Nov 2012
Location: va
Posts: 87
5/04 Fault, flashing fault light

Some how I managed to mess up my 5/04 and rs linx. Now when I do auto config. the baud rate come in at 1200 instead of 19200.

I know that I hit the wrong setting when configuring a different project but I just dont know what one(s). Aparently I must have changed some thing in the processor but I cannot go on line at all to change any thing.

I have pulled the processor out and reset it by shorting the ground/vbb together for about 60 seconds, and that doesn't work.

It is supposed to be running on DH+ from my serial port on my tough book with a cp3 cable. I dont have a clue what to do next.

Thanks
  Reply With Quote
Old March 14th, 2013, 09:51 AM   #2
Buzzen
Member
United States

Buzzen is offline
 
Join Date: Apr 2010
Location: stockton, ca
Posts: 121
can u get online with other processors on the network?
  Reply With Quote
Old March 14th, 2013, 10:07 AM   #3
dmargineau
Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 1,393
It probably wasn't "running on DH+ from my serial port on my tough book with a cp3 cable".
It was most likely running on Serial RS232 and was using a DF-1 RSLinx driver.
Verify the PC's Device Manager, Ports (COM & LPT), Serial Port configuration; I have a hunch that the PC COM Serial port's baud rate was changed to 1200 kbps; make it 19200 and note the COM X number assigned to the Serial Port.
Reboot the PC and then, within RSLinx, add a new RS232 DF1 Devices driver (SLC-CH0/Micro/Type)related the COM X port you have just modified the settings to.
Hopefully an AutoConfigure will bring up the faulted SLC within the RSWho interface.
  Reply With Quote
Old March 14th, 2013, 10:33 AM   #4
bright676
Member
United States

bright676 is offline
 
Join Date: Nov 2012
Location: va
Posts: 87
That didn't help, it wouldn't even set on 1200. Any other ideas?
  Reply With Quote
Old March 14th, 2013, 10:42 AM   #5
bright676
Member
United States

bright676 is offline
 
Join Date: Nov 2012
Location: va
Posts: 87
I just did a restore point and now I have a port conflic with another port even though there was nothing else plugged in. I deleted the other conflick. and still no luck
  Reply With Quote
Old March 14th, 2013, 10:45 AM   #6
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 3,974
Quote:
Originally Posted by bright676 View Post

It is supposed to be running on DH+ from my serial port on my tough book with a cp3 cable
??? does not sound correct, your serial port will not talk DH+

If you are using a CP3 to your serial port you will be using DF1 driver, see here http://www.youtube.com/watch?v=QIu1AGUR4N8

The CP3 will be plugged into the DB9 port on the 5/04 and your serial port (COM1) most of the time the serial is COM1
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers (New ControlLogix), Fluke Meters, Programming Lessons, MicroLogix 1400, 1100, 1000 and 1762-I/O.... all your automation needs
  Reply With Quote
Old March 14th, 2013, 10:52 AM   #7
bright676
Member
United States

bright676 is offline
 
Join Date: Nov 2012
Location: va
Posts: 87
wtf! This is crazy. But some how I managed to get a program loaded into it!. I wish that I new how.

I think I may have some cable management issues here and need to clean this mess up.(operator error)

Thanks for your help.
  Reply With Quote
Old March 14th, 2013, 11:00 AM   #8
dmargineau
Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 1,393
One thing to remember about a PC's Serial Port: it has the tendency to be "hijacked" by various applications/services, some running in the "background".
The most common issue is the presence of two configured DF1 RSLinx drivers, "fighting" over the COM port.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/04 - HSCE2 problems - processor fault Robotroc LIVE PLC Questions And Answers 6 January 1st, 2012 03:08 PM
SLC 5/04 User Fault Routine IsaacC LIVE PLC Questions And Answers 2 January 27th, 2011 04:21 PM
5/05 enet fault light 2004sk4 LIVE PLC Questions And Answers 15 May 7th, 2009 08:03 AM
Bit shifting? tlvaun LIVE PLC Questions And Answers 17 December 5th, 2002 10:51 PM
PLC flashing alarm light or output zero1954 LIVE PLC Questions And Answers 4 October 17th, 2002 08:32 AM