Modbus and the 1763-NC01

jakeemon

Member
Join Date
Aug 2013
Location
Christchurch
Posts
13
Hi,

I'm tearing my hair out trying to connect a simple temperature controller to an ML1100 using a standard RS485 modbus network.

I've tried everything from swapping the A-B wires over to changing baud rates and handshaking settings. I can't get any comms at all.

I'm getting plenty of messages sent but no messages recieved. The only thing I can think of is the physical wiring of the NC01 breakout box. It has a term, A, B, COM, SHLD and CGND connections.

Obviously my data lines go to A and B but where does the sheild go? Does it connect to COM or SHLD? Other's have mentioned jumpering A to TERM and COM to CGND. I have tried all possibles but still get nothing.

Have also tried a teminating resistor but as I'm withing 300mm on a test bed I can't see this being the problem.

Any ideas?

Jake
 
Attached is the image from one possible setup for Modbus on an 1100. Obviously the upper part may vary in Baud, Parity, Stop Bits and Data Bits. But make sure that the 'Protocol Control' is set up as shown - 'No Handshaking (RS485 Network)'

Modbus 1100 setup.jpg
 
Does the slave device have a data common pin or terminal ?

In RS-485, there is always a common point against which the two data voltages are measured. Many devices use the chassis ground or earth ground for this common point. Rockwell Automation uses an isolated common terminal. This is the one labeled COM.

Shield and Chassis Ground terminals on the 1761-NET-AIC or 1763-NC01 are exactly what they sound like: the Shield is not connected to anything internally but gives you a terminal to daisy-chain shield drain wires. The Chassis Ground pin is connected to the chassis ground of the controller.


Try connecting a wire from the COM terminal to your "2-wire" device's chassis ground.
 
Have brought a RS232 - 485 converter so I can use a MODBUS sniffer. If I get that side working I'll then try again with the PLC. Other thing I'm considering is ditching the NC01 cable and buy a TIBBO serial to ethernet adaptor then I will be able to MSG with TCIP.
 

Similar Topics

I am using a 1763-NC01 Ch0 to RS485 cable along with a ML1400 processor. I'm trying to use it as a Modbus master to communicate with a cut meter...
Replies
6
Views
22,988
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
38
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
20
Views
201
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
95
Good day guys. I have a third party device with its Modbus registers which I want to copy/set up on a plc because I need to convert my Modbus tcp...
Replies
3
Views
119
Back
Top Bottom