So I thought I understood how to communicate with I/O modules in RSLogix5000. I thought that you would declare an I/O module and simply alias the hardware tag to some other tag you would use in the program.

However, I've been looking through code recently and have seen the use of GSV/SSV for interacting with the I/O modules.

This confuses me. I know that the GSV/SSV is meant for objects(I have some experience with using them for axis objects), but I never thought that you would use them for I/O.

So, could anyone explain to me the purpose of the GSV/SSV and why someone would use those instructions as opposed to using the declared hardware tags that are available when you add a module to your project?
 
The GSV/SSV are used to read status of the controller's connection to the module. Using the GSV you can identify if the module is running, faulted, or inhibited. If it is faulted, the GSV can capture the fault code.

OG
 
The GSV and SSV are often used to interact with the status of an I/O module itself, one level up from the I/O data. Readiness status, specific errors and other information can be read. In some cases the program can correct module problems or at least performs resets.

I often use the GSV commands to read the status of communications with external remote modules (drive interfaces) which may take a while to connect with the end targets (the drives themselves). Only when they are ready can commands to the drives take place.
 
The GSV and SSV are often used to interact with the status of an I/O module itself, one level up from the I/O data. Readiness status, specific errors and other information can be read. In some cases the program can correct module problems or at least performs resets.

I often use the GSV commands to read the status of communications with external remote modules (drive interfaces) which may take a while to connect with the end targets (the drives themselves). Only when they are ready can commands to the drives take place.

Okay, that seems to make sense then. Thank you
 

Similar Topics

Hi folks! I'd like to add to my PLC logic a way to detect what failure is my I/O module (PowerFlex 525 VFD)having. My goal is been able to array...
Replies
10
Views
4,527
Hello, I always have problems with GSV. I have to prepare a sequence in RS5000, which need to operate only at the set time. For example, from...
Replies
11
Views
2,961
Hi guys I have a project in my head that I'm thinking of putting on our machines to help the engineers to fault find ? On our machines we do not...
Replies
1
Views
1,994
Hello everyone, I am having an issue with random I/O faults on a ControlNet network. In the logic, there is a GSV instruction with LedStatus as...
Replies
3
Views
5,402
I'm trying to extract the fault status from a CompactLogix L33ER rev 20 and I cannot get the GSV intruction working on the Fault Routine. I...
Replies
1
Views
3,968
Back
Top Bottom