Hello Everyone,
Im struggling with a plc that we got here in the company where I work at. We use this plc for precooler temperature monitoring only. The plc is mounted on a panel with one main expansion board 10-slot with the AB SLC-500, one output card(dry relay), and six rtd input cards, and a scanner. A secondary, remote 7-slot, expansion board is installed with an AB 1747-ASB remote adapter installed. Lately i got a fault code "8". Going back to the troubleshooting manual, it says that the adapter is still on the Power Up Self Test in Progress, and it recommends to replace the card. I ordered a new card, and as soon as I installed it with the same dip switches settings, the new card went straight to a fault code of "8".
What am I missing?
Thanks in advanced.
Omar Gomez
Im struggling with a plc that we got here in the company where I work at. We use this plc for precooler temperature monitoring only. The plc is mounted on a panel with one main expansion board 10-slot with the AB SLC-500, one output card(dry relay), and six rtd input cards, and a scanner. A secondary, remote 7-slot, expansion board is installed with an AB 1747-ASB remote adapter installed. Lately i got a fault code "8". Going back to the troubleshooting manual, it says that the adapter is still on the Power Up Self Test in Progress, and it recommends to replace the card. I ordered a new card, and as soon as I installed it with the same dip switches settings, the new card went straight to a fault code of "8".
What am I missing?
Thanks in advanced.