Allen Bradley 1747-ASB

Join Date
Nov 2013
Location
Pixley
Posts
1
Hello Everyone,

Im struggling with a plc that we got here in the company where I work at. We use this plc for precooler temperature monitoring only. The plc is mounted on a panel with one main expansion board 10-slot with the AB SLC-500, one output card(dry relay), and six rtd input cards, and a scanner. A secondary, remote 7-slot, expansion board is installed with an AB 1747-ASB remote adapter installed. Lately i got a fault code "8". Going back to the troubleshooting manual, it says that the adapter is still on the Power Up Self Test in Progress, and it recommends to replace the card. I ordered a new card, and as soon as I installed it with the same dip switches settings, the new card went straight to a fault code of "8".

What am I missing?

Thanks in advanced.
Omar Gomez
 
Not sure what to say as i have never had an 8 error code

8 is a power up self test at start up and only for a few seconds normally
Also an 8 or 333 is a watchdog error

Some thoughts

1. What series was the old ASB - What series did you replace it with
2. Can you swop out the SLC rack - Backplane
3. Has anything changed since you started getting the intermittant fault
4. Earthing on the rack all good
5. Have you checked the logix asb config to make sure its correct (and dip switches)
6. What do the LEDs on the ASB do
7. What module is the other end and what (if anything) does this show when under the 8 fault
8. Does the SLC record any faults
 
Hi

I would also start with the power supply on the remote rack as over the years I have replace a few of them

Donnchadh
 

Similar Topics

I am trying to update the firmware of a 1747-SDN Series B that is currently at firmware version 5.01 to version 8.006 which is the only version...
Replies
8
Views
6,183
We have a number of 1747-BSN modules in stock but need 2 1747-SN modules for a project. Can we use a 1747-BSN in lieu of a 1747-SN? Any...
Replies
4
Views
1,652
I have a AB 1747-UIC USB to DH 485 converter Can I use that to connect to a watlow controller EZzone with "standard bus EIA 485" ...
Replies
4
Views
1,855
Hello, Please , I need help, I want to configure a DeviceNet network. Indeed , my DeviceNet network consists of : 1747 SDN Allen Bradley...
Replies
0
Views
4,776
hello, I want to make a DeviceNet communication between Allen Bradley SLC503 and a PCB card, I want to know if in addition to the 1747SDN, is...
Replies
2
Views
3,316
Back
Top Bottom