Dear,
there was a requirement to control the variable speed pumps based on level and at the same time change their speed.
The system consists of 2 pumps, please see picture below.
See the sequence of operation:
L1 is the level of dry run protection for the pumps at which low low level alarm shall be activated
At L3, pump 1 shall start.
During operation i.e. between level 2 and level 3, the speed of the pump is controlled by the level of sewage as measured by the hydrostatic level sensor such that when the level of sewage is increased after a predefined time, the speed of the pump shall be increased to cater for the increase of the sewage incoming flow
During operation i.e. between level 2 and level 3, when the level of sewage is decreased after a predefined time, the speed of the pump shall be decreased to cater for the decrease of sewage incoming flow.
When the first pump reaches full speed and sewage level reaches L4, the second pump shall cut in and an high high level alarm shall be activated, both pumps shall start running at the same speed to cater for the required demand.
Do you have feedback on the above, is the system workable from hydraulical point of view and is it easy to program?
thanks a lot for your valuable feedback!
You don't show the "hydrostatic level sensor" in your diagram - to me this implies an analog signal. If that is the case then this essentially a PID or similar feedback control with pump speed proportional to level.
On the other hand, based on your diagram, I suspect that what you really want to do is use level switches to control the pump speed, with a different preset pump speed at each level. That is also feasible and, if you set the speeds properly, should do the job.
Neither system is unusual or particularly complex programming. Whether it is easy or not is a function of your skill level.
hello, I am using FT ME v9.00. I need to load screens based on a product number (1-4). There are few display screens and few unique to the product...
1,926
Hey guys, I have a client that has a pump they want to control based on what day of the week it is. As in, on Monday have the pump turn on at a...
2,091
I also posted this in another forum, but realize that there are folks who use this forum that may not use that forum, so hopefullys someone may...
2,848
I'm working as an engineer with a factory which uses mostly Mitsubishi(FX series) and Omron(CQM1H and CPM1A) plcs. Due to some improvement reason...
13,067
Okay, so I just showed my customer a demo of his controller. I haven't actually ordered the PLC yet; in fact I haven't totally decided which make...
17
16,210