Old June 25th, 2014, 09:33 AM   #1
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
GE Fanuc 90-30 CPU331 Upload

We are going to be removing an existing GE Fanuc 90-30 that is running a particular waste water program. I have an old printed version of the program with hand-written changes. These changes have been made using the old handheld programmer. The original program was written using LM90, as that's what the printout shows as the directory folder name of the logic. i.e. C:\LM90\WasteWater I need to get a copy of the current logic off of the processor to validate the old printed copies for the conversion from the GEFanuc PLC to DCS programming.

I have a copy of Proficy ME version 5.6 on an older laptop and our instrument/PLC guy who has been making the changes using the handheld programmer says he cannot get Proficy to communicate with the processor. That is the extent of my knowledge of that.

I have version 8.0 Proficy ME on its way for my newer laptop, as I contacted a "local" supplier of GEIP and he suggests that there should be no issue uploading a copy of the program. The research I have done led me to the hardware/software compatibility matrix. It shows some of the 331 CPUs as being compatible with Machine Edition and others not. How can I determine the revision of the processor I have? I see it shows 331 on the front of it, but that is it. This is a currently running system, so it cannot be shut down for this work. If we cannot get a copy of the program in the processor, then they will simply work off of the old copies and hope for the best, but I would really like to provide the actual running logic, albeit without comments/descriptions.

Second question: Is there a way to get a copy of the logic off of the processor using the handheld programmer...a copy that can be printed out to compare against our original printout?

Any and all input will be greatly appreciated. By the way, I am fairly new to PLCs in general, and am trying to gain as much knowledge and experience as I can, so please bear with me as I try to figure this out.
  Reply With Quote
Old June 25th, 2014, 10:36 AM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,629
To check the firmware version, look at the last one or two characters of the CPU part number. It will be IC693CPU331x or IC693CPU331yy where "x" or "yy" indicate the version. That's not foolproof because someone could have installed an EPROM with a newer firmware version than indicated by the part number suffix.
Very early firmware versions may not communicate with Proficy. By "very early" I mean older than version 2.5 or 3.0. When the product line first came out, GE Fanuc made a major change at around that level and tried very hard to get everybody to upgrade. I think that the ones that never got upgraded to that minimum level may be the ones that have problems with Proficy.
When you first install Proficy, it defaults to prevent program downloads to versions earlier than 8.x or so, but there is a parameter setting that allows you to bypass that restriction.
I'm not aware of any way to create a printed copy of the program from the file stored on the handheld programmer's memory card. You would have to download to another CPU and use Logicmaster to create the printout.
  Reply With Quote
Old June 25th, 2014, 10:44 AM   #3
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
Quote:
Originally Posted by Steve Bailey View Post
To check the firmware version, look at the last one or two characters of the CPU part number. It will be IC693CPU331x or IC693CPU331yy where "x" or "yy" indicate the version. That's not foolproof because someone could have installed an EPROM with a newer firmware version than indicated by the part number suffix.
Very early firmware versions may not communicate with Proficy. By "very early" I mean older than version 2.5 or 3.0. When the product line first came out, GE Fanuc made a major change at around that level and tried very hard to get everybody to upgrade. I think that the ones that never got upgraded to that minimum level may be the ones that have problems with Proficy.
When you first install Proficy, it defaults to prevent program downloads to versions earlier than 8.x or so, but there is a parameter setting that allows you to bypass that restriction.
I'm not aware of any way to create a printed copy of the program from the file stored on the handheld programmer's memory card. You would have to download to another CPU and use Logicmaster to create the printout.
Thanks, Steve. I'm hesitant to do too much to the PLC hardware, because if we lose power, we have lost our only copy of the program running our waste water process. Would that parameter setting prevent communication for an upload or is that strictly limited to downloads to "old" processors?
  Reply With Quote
Old June 25th, 2014, 11:55 AM   #4
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
Is there a place online that offers the LM90 demo for download? It was previously available on the GEfanuc website, but those links are no longer valid.
  Reply With Quote
Old June 25th, 2014, 12:06 PM   #5
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,629
Quote:
because if we lose power, we have lost our only copy of the program running our waste water process
That's only the case if the battery is dead. There is an LED on the power supply module that indicates the status of the battery. If it is on the battery needs replacing. You can install a new battery while the unit is powered.
I'm not certain about whether the setup parameter places any limits on simply establishing a connection with the PLC. On your computer running the older version of Proficy, check to make sure your PLC target in the project folder is using the correct COM port. What are you using for a cable between the computer and the PLC? The port on the power supply module is RS485. You'll need a converter to connect your computer's RS232 port.
I don't think they still offer the demo version of Logicmaster.
  Reply With Quote
Old June 25th, 2014, 12:16 PM   #6
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
Quote:
Originally Posted by Steve Bailey View Post
That's only the case if the battery is dead. There is an LED on the power supply module that indicates the status of the battery. If it is on the battery needs replacing. You can install a new battery while the unit is powered.
I'm not certain about whether the setup parameter places any limits on simply establishing a connection with the PLC. On your computer running the older version of Proficy, check to make sure your PLC target in the project folder is using the correct COM port. What are you using for a cable between the computer and the PLC? The port on the power supply module is RS485. You'll need a converter to connect your computer's RS232 port.
I don't think they still offer the demo version of Logicmaster.
The battery LED indicator is off. It would probably be smart to order and swap the battery out in the meantime.

I am using the HE693SNP306AX cable. Both port settings match and port COM1 is chosen with the default communication settings, 19,200, odd, 1 stop bit, blank SNP ID.

I'm assuming this is the same issue as unsunghippie back in 2006:
http://www.plctalk.net/qanda/showthr...ight=90-30+331
  Reply With Quote
Old June 25th, 2014, 12:38 PM   #7
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,629
It sounds like your problem is similar to unsunghippie's. Do you still have the handheld programmer? If so, connect it and check what the PLC's port settings are. The handheld will set itself to whatever baud rate and parity the PLC is using. Also check if the PLC is using an SNP ID. Earlier firmware versions were finicky about making sure Logicmaster was asking to communicate with the correct SNP ID.
And, as was mentioned in that other thread, make sure COM1 is available and not being used by some other application. RSLinx sometimes doesn't relinquish the port even when you shut down RSLogix.
  Reply With Quote
Old June 25th, 2014, 01:05 PM   #8
RussB
Lifetime Supporting Member
United States

RussB is offline
 
RussB's Avatar
 
Join Date: Oct 2003
Location: Michigan
Posts: 2,910
If the PLC was first supplied with a modem option it is likely that the serial port was changed to 9600,N,8,1 instead of the default 19200,O,8,1 port parameters.
Also there is a utility called PACsAnalyzer that will pull out the hardware configuration including version levels of some modules. If your hardware is not too old this will work.
Regardless of the CPU (version > 3.x) it is likely that you will be able to 'Upload" using any version of Proficy or LM990. Get the hardware first then logic, even if you cannot download to make things "Equal" it very likely will be.
Also regardless of the hardware/software versions you 'should' be able to go 'Online' with the software and look at the version of the CPU. Under 'Target > Online Commands > View Status'
__________________
LEARN something today so you can TEACH something tomorrow.
DETAIL in your question promotes DETAIL in my answer.
Dominus Vobiscum <))>(
"Where is the wisdom that we have lost in knowledge?" T.S. Elliot


  Reply With Quote
Old June 25th, 2014, 03:18 PM   #9
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
I tried those new parameters to no avail. I also just received Proficy v8.0, so I installed it and gave it a shot on a newer laptop with a USB-serial adapter and the SNP cable. Same issue with both communication parameters. I guess I am going to have to source some Logicmaster software somehow.
  Reply With Quote
Old June 25th, 2014, 11:09 PM   #10
RussB
Lifetime Supporting Member
United States

RussB is offline
 
RussB's Avatar
 
Join Date: Oct 2003
Location: Michigan
Posts: 2,910
Have you tried the Hand Held Programmer? It will tell you the hardware version and the serial parameters needed for giving you the information needed to chose the correct software LM90 or PME.
__________________
LEARN something today so you can TEACH something tomorrow.
DETAIL in your question promotes DETAIL in my answer.
Dominus Vobiscum <))>(
"Where is the wisdom that we have lost in knowledge?" T.S. Elliot


  Reply With Quote
Old June 26th, 2014, 08:54 AM   #11
civicseth
Member
United States

civicseth is offline
 
Join Date: May 2014
Location: Ledbetter
Posts: 9
Quote:
Originally Posted by RussB View Post
Have you tried the Hand Held Programmer? It will tell you the hardware version and the serial parameters needed for giving you the information needed to chose the correct software LM90 or PME.
I have not attempted to use the programmer. I don't have any experience with it, and I would have to "borrow" it from our instrument guy, but it is a possibility that I can.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GE Fanuc Series 90 30 Johnny T LIVE PLC Questions And Answers 31 April 22nd, 2018 04:06 PM
GE Fanuc Series 90 30 No Output gearmachinist LIVE PLC Questions And Answers 4 April 26th, 2011 02:25 PM
Ge fanuc 90 -30 programing using lm 90-30 mamadoo95 LIVE PLC Questions And Answers 3 March 25th, 2011 01:29 PM
GE Fanuc 90 30 info leitmotif LIVE PLC Questions And Answers 3 August 4th, 2007 01:52 PM
GE FANUC - CPU331 - logismaster 90 noman-jamil LIVE PLC Questions And Answers 8 September 17th, 2004 09:27 AM


All times are GMT -5. The time now is 10:20 AM.


.