Good Morning,
I have a sort of easy problem that is driving me nuts.
I have an application where I'd like to take a set point, lets say it starts at 50. Ten seconds later, I want to increase it to 60, another ten seconds 70, and so on...
How can I get this done, seems so easy, and I'm stumped!
Thanks, Burch
Good Morning,
Thanks, Burch
use a timer and a one shot....
You should use a non-retentive timer and make it self-resetting by programming a NC Timer bit as the timer trigger. Set the timer for 10 seconds, then every time it goes done, add 10 to your Setpoint using a 1-shot. You must set a upper limit and stop the ADD once you reach the maximum Setpoint.
This sounds like a ramping function for a heating application. 10 Points per 10 seconds (10 P/10 Sec.) also is the same as 1 point per second (1 P/Second), so you could use a 1-second self-resetting timer and Add 1 point each second. The end Setpoint will occur at the same time as the 10 P/10 Sec. method.
If you are changing the Setpoint of a PID instruction, then the 1P/Sec will give you a smoother upward curve for the Control Variable (with less oscillation).
From your other posts it looks like you are using AB products.
An easy way to do smooth linear ramping with a timer is to use an SCP instruction to "scale" the elapsed time to your setpoint range. The attached example will give you a smooth linear ramp from 0 to 100% in one minute.
So, I get sent a heartbeat, an int that goes from 0-9 every second and then restarts, I need to detect if it stops after 3 secs. Any simple way...
3,084
I'm sure this is an easy one for the experienced guys, how can I use an incrementing dint value to trigger a counter to count? It seems like it...
3,180
Hello World, I am having difficulty incrementing a serial number that needs to start at 0, and go through Z. (After 9, comes A). The serial...
1,853
Hi guys, Im about to add a new flowmeter which pulse every 0.1 cubic meter to my Micrologix 1400. I would like to increment of 0.1 everytime i...
1,999
Hey everyone, I am hoping that i can get an answer on this matter... I have a micrologix 1100 hooked up to a signal conditioner (Omrga DMD-466-DC)...
1,583