Communication between RSLinx Gateway and OPC Client

Currently OPC Client (PI OPC Interface from OSISOFT) is reading the data from RSLinx Gateway which is installed on different PC. And we are reading near to 800 tags. Normally everything is working fine. But when OPC Client PC got restarted then only few tags out of total 800 tags is reading from RSLinx Gateway. But this problem will get solved once we restart the RSLinx Gateway PC.
Following error on RSLinx Gateway Communication event log
AB_ETHIP-1\0.(192.168.1.12).1.0 : K55-AIT-M-0128B : 05/15/14 - 14:37:28 : 00h
Items: K55-AIT-M-0128B
Type: READ
Mfg: Allen-Bradley
PlcType: Logix5000
Desc: This item does not exist in the processor.
Number of occurrences: 4

Is there any settings to be done in RSLinx Gateway for Auto reconnection.
1. The version for RSLinx Classic Gateway is 2.54.00.11 CPR 9 SR1.
2. The OS in RSLinx Classic Gateway PC is Windows XP.
3. PI Interface configuration UtilityVersion is 1.4.10.0
4. PI Server 2012 is used
5. PI Interface node is on Windows 7.\
  Reply With Quote
Old January 23rd, 2015, 09:08 AM   #2
k_w
Member
United States

k_w is offline
 
Join Date: Jan 2015
Location: Houston
Posts: 30
Try to use the OPC Tunneller of Integration Objects. This can resolve your problem. I did many tests with PI OPC DA interface and PI OPC AE interface and it worked very well.
You can get it and test it from the this link:
http://integrationobjects.com/produc...ker-da-hda-ae/
  Reply With Quote
Old January 26th, 2015, 12:28 AM   #3
abdulafeel@gmail.com
Member
Saudi Arabia

abdulafeel@gmail.com is offline
 
Join Date: May 2014
Location: Jeddah
Posts: 3
Hai K_W,

Other than OPC Tunneler is there any other solution.
  Reply With Quote
Old January 27th, 2015, 04:34 AM   #4
k_w
Member
United States

k_w is offline
 
Join Date: Jan 2015
Location: Houston
Posts: 30
Hi abdulafeel
You said that restarting the RSLinx Gateway PC did resolve the problem. this mean that the problem is with the OPC server or with the Gateway you are using.
You can use DCOM. But this solution is not recommended since it can cause many security problems. I suggest you to test the link that I provided you. You will resolve your problem in 5 min. Let me know about your test result.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MP 277 communication with RSLinx OPC Server arun_mallah LIVE PLC Questions And Answers 3 June 25th, 2009 04:32 AM
How can we use RS link Gateway as remote OPC server for Cimplicity HMI OPC client nitin.salvi LIVE PLC Questions And Answers 22 June 9th, 2009 04:46 PM
RSlinx 2.53 with Vista support available Contr_Conn LIVE PLC Questions And Answers 7 September 4th, 2008 07:56 AM
RsLinx Classsic Gateway 2.52 As OPC server plcnovel LIVE PLC Questions And Answers 4 June 26th, 2008 03:59 PM
OPC Server and Linx Gateway kbradray LIVE PLC Questions And Answers 1 March 11th, 2008 02:51 PM


All times are GMT -5. The time now is 07:59 PM.


.