Question Analog input issue!

Hello all.

I'm working with a Siemens C7-635 OP.
And this is the first time that i'm working with the analog inputs. On one of my four analog inputs i have connected a measuring device, wich measuers lenght. For instance 10 centimeters of lenght equals 1V, 20 centimeters 2V and so on to 100 centimeters and 10V. The main problem that i have is that the value wich I read from this particular analog input isn't riseing lineary.

For example:
When I measure 10 cm(1V on the analog input) of distance I read 144(INT value) on that analog input.
When I measure 20 cm(2V on the analog input) of distance I read 304(INT value). There is a deviation allready.
When I measure 30 cm(3V on the analog input) of distance I read 448(INT value).

Why is this happening??? I expected that the value would be riseing linearly like the Volts but it doesn't. Is there any way to correct this???
I should also state that i then convert the INT value do DINT and DINT to Real. So that I than devide the REAL value by that much that the final resoult is than 10 if the measuring device is measuring 10 cm...
If it is supposed to be measuring 40 cm the value that i get from the devidement is 75

BTW: the analog input is configured like this:
Measurnig Unit: V
Measuring raneg: 0-10V
Interference frequency: 50Hz.(I changed this to 60Hz and 400 Hz, and nothing changes, I didn't expect it to change but it's worth trying.)

Thank you.
>Ales<
  Reply With Quote
Old July 6th, 2004, 08:34 AM   #2
Bitmore
Member
United States

Bitmore is offline
 
Bitmore's Avatar
 
Join Date: Dec 2003
Location: Automation Alley, Oakland County, Michigan
Posts: 477
No Name,
My company uses analog inputs at an uncommonly high level. The device you're complaining about is probably some type of resistance feedback (in our world we call it a slidewire pot). Most of which contain linearity issues. Some of these measurement devices have a "zero trim and span trim" using small potentiometers on the device. Check to make sure if you have these. If so it's just a "setup" or adjustment problem. If there is no method for "adjustment" on the device. A method we have come to rely on is called a "characteriser". Which is nothing more than a subroutine that uses the raw input data and a lookup table to "relate or characterise" the raw input. How linear you want the signal will have a definite impact on how many "points" you care to plot. The raw input is then "characterised" based on this table. The intial input could also be slightly adjusted by an offset value to get it more closely to resemble what is actually happening in the real world.
Something like a subtract statement that aligns the raw data at the 1 CM spot. 144 - 44 = 100. This would not adversly affect the remaining points unless, the linearity is so bad, it traverses the intended slope of the line, at some other point.

bitmore
__________________
"A good scientist is a person with original ideas. A good engineer is a person who makes a design that works with as few original ideas as possible. There are no prima donnas in engineering." Freeman Dyson

Last edited by Bitmore; July 6th, 2004 at 08:40 AM.
  Reply With Quote
Old July 6th, 2004, 08:40 AM   #3
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,962
Where are you measuring voltage? At the terminals of the
analog card or at the sensor? You can also try adding
capacitor accross analog input. Maybe signal is picking up some
noise and your meter and input don't scale it same way
(meters often use True RMS).
  Reply With Quote
Old July 6th, 2004, 09:39 AM   #4
NoName
Member
Slovenia

NoName is offline
 
NoName's Avatar
 
Join Date: Sep 2003
Location: Domžale
Posts: 214
Thank you for your reply's.
@Bitmore
The device unfortunatley doesn't have any potentiometers for adjusting zero trim and span trim.I have thought about useing the characteriser in this case. But it's alot of work, so I asked if there is a way to sort out the linearity problem.

I've tryed to substract a specific value from the raw value, but the result's aren't right in values above 40 cm.

@Panic mode

I'll measure the Voltage on the terminals of the analog card tomorow with a Osciloscope to see what kind of a signal I get there.

Thank you for the help guys.
I'll check back with the results of the measurment with the Osciloscope.
  Reply With Quote
Old July 6th, 2004, 02:53 PM   #5
Ken M
Member
Scotland

Ken M is offline
 
Join Date: Mar 2004
Location: .
Posts: 1,136
There seems to be a bit (or two) missing here.

I thought a C7 or S7 analogue input signal is delivered to the CPU as an INT between 0-27648 regardless of the source (amps, volts, ohms, monkeys, whatever). So, for a 0-10V signal, 1V would be 10% of the range or 2760-ish (allowing for rounding). 2V should be 20% or 5520-ish etc.

These are way out compared to your monitored values! 144 vs. 2760? It's more than just arithmetic that needs fixing here.

There's either some major interference, or what you're measuring isn't what the C7's getting. When things are that bad, trust the PLC. In this case I would say it's the victim, not the culprit.

Regards

Ken
  Reply With Quote
Old July 7th, 2004, 02:14 PM   #6
NoName
Member
Slovenia

NoName is offline
 
NoName's Avatar
 
Join Date: Sep 2003
Location: Domžale
Posts: 214
Hello all.

Today I measured the input Voltage on the analog module on my OP. There I found that there is alot of interference.About 0.5V. So I put a capacitator in front and it cleard up all the interferance.

Then I measured the Volt's on that Analog input. The input voltage goes up linearly.For instance 1V is 10 cm... and so on. It's perfect so to speak. But in step 7 if I view the analog input(IW7) the values are not going up linearly. The displayed value is shown in INT-gers.
So what could be wrong??? Is the analog module some how defected or si there a fine tuneing option somewhere??? I doubt that it is though.
It's also strange that at 1V i get 144 on the analog input, not 2760-ish as Ken M stated... What could be the problem...???

The source is linear, but Step 7 doen't wanna play
  Reply With Quote
Old July 7th, 2004, 03:17 PM   #7
Ken M
Member
Scotland

Ken M is offline
 
Join Date: Mar 2004
Location: .
Posts: 1,136
Hi NoName,

In your first post you mentioned using the C7-635. This has built-in analogue inputs, but later you've referred to a 'module'. Have you added some extra I/O with standard S7 modules?

If you have added a SM331 analogue input of some form you will have to make sure you have set it up correctly in the Hardware Configuration and then adjusted the plugs in the side of the module if necessary. Siemens' standard analogue modules handle voltage, current, RTDs, thermocouples etc all in the one module. Tell the CPU how to treat each channel, and then put the measuring range plugs in the right way round. (It's a square plug with 4 alignments) These engage the correct circuitry to feed the A-D converter with the correct signal. Unfortunately I believe the default shipping location for these plugs is the voltage setting so unless you or someone else has 'adjusted' them they should have been OK.

I think we're looking at something pretty major like a plug 180 degrees out of alignment or a setting in the Hardware Config telling the CPU we're expecting a Pt100 or something.

This error definitely doesn't fall in to my "fine-tuning" category!

If you're using the built-in analogues, do they all show the same symptoms? Can you try re-wiring to another input channel? If they are all equally affected it may be something common to them all - e.g. either your signal (which you now are sure is OK) or the multiplexed A-D converter.

Regards

Ken.
  Reply With Quote
Old July 8th, 2004, 02:13 AM   #8
NoName
Member
Slovenia

NoName is offline
 
NoName's Avatar
 
Join Date: Sep 2003
Location: Domžale
Posts: 214
Sorry Ken.
I expressed my self wrong. I ment that I measured the input voltage on the built in module.

In the attached picture there can be seen how the Analog inputs are configurated.
I have also tryed to re-wire it to another input, but the results are the same.
I have connected the source to AI2-U(analog input 2- voltage input), the other 2 inputs of that particular AI AI2-I(currnet measurment), AI2-C(reference potential chanel) I haven't connected any where. They are open so to speak. Is this wired correctly???

Regards
Ales
Attached Images
File Type: jpg ai_config.jpg (43.9 KB, 376 views)

Last edited by NoName; July 8th, 2004 at 03:01 AM.
  Reply With Quote
Old July 8th, 2004, 03:38 AM   #9
NoName
Member
Slovenia

NoName is offline
 
NoName's Avatar
 
Join Date: Sep 2003
Location: Domžale
Posts: 214
I've found out what the problem was. I didn't wire the Analog inputs the correct way I shuld have grounded the AI0-C input.
Now that the AI0-C is grounded it works like it should. 1V is around 2760 in INT... and so on!

Thank you all for helping me through this. If it wasn't for guys nothing would work as it should. So thanks alot Ken M, panic mode, Bitmore!
  Reply With Quote
Old July 8th, 2004, 04:10 AM   #10
Ken M
Member
Scotland

Ken M is offline
 
Join Date: Mar 2004
Location: .
Posts: 1,136
Glad to hear all is OK, NoName.

And don't worry, your secret is safe with us - we won't tell anyone!

Regards

Ken.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1762-IF2OF2 Analog Input Problem davidgay LIVE PLC Questions And Answers 22 August 14th, 2013 04:25 AM
Analog Input Fluctuations Steve Etter LIVE PLC Questions And Answers 18 October 20th, 2004 06:34 AM
Micro Logix 1000 Analog input comparision mikewood LIVE PLC Questions And Answers 5 June 21st, 2004 12:41 PM
SLC analog voltage input card georgeofthejungle02 LIVE PLC Questions And Answers 12 March 15th, 2004 07:47 AM
AB Analog Input Help GTX LIVE PLC Questions And Answers 2 December 14th, 2003 02:37 PM


All times are GMT -5. The time now is 04:15 AM.


.