I have a rung in a ControlLogix processor running in the continuous task. When the Step tag is a certain value it latches the corresponding bit number in the SystemFlags tag. This is existing code which I did't write.
In another periodic task, running at 100ms, the set bit is used as permissive to other logic. What appears to be happening occasionally is that since on every scan the flag word is being set to zero, the periodic task "sees" the SystemFlags.xx bit as cleared. I understand the asynchronous nature of ControlLogix. Is what I'm describing possible?
LIM(1,Step,20)MOV(Step,FlagReference)MOV(0,SystemF lags)OTL(SystemFlags.[FlagReference]);
__________________
John
Old February 14th, 2015, 05:16 PM   #2
Basti504
Netherlands
Basti504 is offline
Basti504's Avatar
I encountered something similar during a recent project.
In the continues task:
* A rung where unconditionally a 0 is MOVed into a command DINT
* The rungs below will move the correct command number based on curtain conditions. Meaning a 1 was "Motor forward", 2 "Motor reverse", 0 "stop".
This command number was used in a Periodic Task to drive a motor.
We noticed that while the command DINT was constantly MOVed with 1, sometimes the motor stopped for a fraction of a second. In the end we moved the rungs where the command was formed to the periodic task and the problem was solved.
We concluded that the CPU sometimes executed the periodic task right between the unconditionally 0 MOV, but before the actual command was MOVed again.
In the end it seems like the CPU interrups the continues task at ANY moment to execute a higher priority task. Exceptions I have read about are CPS instructions.
Hope this helps
Old February 14th, 2015, 08:23 PM   #3
jkerekes
United States
jkerekes is offline
jkerekes's Avatar
Yes this looks like a similar issue. I didn't write the piece of code, but I think it's causing an issue in another area of the program. I'm just trying to confirm this behavior. Thanks for the input.
__________________
John
Old February 14th, 2015, 10:33 PM   #4
Ron Beaufort
United States
Ron Beaufort is offline
Ron Beaufort's Avatar
actually a periodic task in capable of interrupting the so-called "continuous" task even part way through an ADD instruction ...
if this type of behavior is causing a problem you might try experimenting with the UID and UIE instructions ... (User Interrupt Disable and User Interrupt Enable) ...
http://www.plctalk.net/qanda/showthr...0&postcount=64
__________________
2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
I once was lost, but now am found, was blind, but now I see.
Old February 15th, 2015, 11:11 AM   #5
jkerekes
United States
jkerekes is offline
jkerekes's Avatar
Thanks, Ron. I forgot about the disable/enable interrupt instructions. That may be what I need to add to that rung.
__________________
John
Old February 16th, 2015, 12:21 AM   #6
rdrast
United States
rdrast is offline
rdrast's Avatar
Quote:
Nope. That won't help a bit with your current situation.
You described the situation as the value of the SystemFlags tag is changed by the continuous task, and sometimes you aren't reading the value you want in the periodic task.
Disabling interrupts won't help there at all.
You need to change your core logic to prevent zero writes to your Flags tag perhaps, or maybe even buffer it when it has a valid value, and set a latch bit so that the periodic task will only look at the value if the latch bit is set. Then the periodic routine can reset the latch, allowing the continuous task to load a new value into the "Buffered" flags word.
Continuous task:
(when SystemFlags is valid):
XIO FlagsLoaded MOV SystemFlags FlagBuffer OTL FlagsLoaded
Periodic task:
XIC FlagsLoaded (use your flags word somehow)
OTU FlagsLoaded
Seriously, I'd re-think the core logic. Use your sequencer to set an enable (preferably latched) for your periodic task
__________________
How to ask questions the SMART Way!
Look First, Ask Second!
Old February 16th, 2015, 09:23 AM   #7
jkerekes
United States
jkerekes is offline
jkerekes's Avatar
OK. Then I have a misconception on how it works then. Can you briefly explain why disabling the interrupts won't allow that rung to complete executing before the periodic task reads the tag?
Unfortunately, we can't change significantly the code at this point in time. What we may do instead is use the value in an EQU instruction.
__________________
John
Old February 17th, 2015, 01:21 AM   #8
rdrast
United States
rdrast is offline
rdrast's Avatar
Disabling the interrupt will not prevent the continuous task from updating the tag.
Then when the periodic task is scanned again, you still have no idea where in the continuous scan it is using the tag.
The best method to use would be to pull the routine out of the periodic task that is looking at that tag, and dropping it in to your continuous task immediately the routine where it is updated to become valid.
Use it in an EQU ? What, to make sure it is not zero? What if it is (and by Murphy's law, it will be) zero 300 times in a row?
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
simple tag server question bulletin blues LIVE PLC Questions And Answers 2 March 1st, 2014 07:18 PM
Controllogix tag security Paul351W LIVE PLC Questions And Answers 9 January 25th, 2012 10:55 AM
Red Lion Crimson 3 ControlLogix Driver Question glubash LIVE PLC Questions And Answers 4 January 19th, 2012 02:52 PM
Question about AB ControlLogix 5000 unusual issue cipitio LIVE PLC Questions And Answers 16 August 29th, 2009 11:24 AM
ControlNet MSG communication question for Controllogix coolblind LIVE PLC Questions And Answers 4 April 25th, 2008 10:02 PM