Exclamation ABB drive control via modbus communication with FXCPU plc

I do programming in GX developper for ABB drive model ACS 550 control via modbus communication in FXCPU PLC,I can read the Data of drive parameters and other running variables but when i go to write the data into drive for start/Stop or speed reference its not wrriten on to the drive i feel helpless now please suggest what i will do now ???

Thanks in advance
  Reply With Quote
Old April 4th, 2015, 06:30 AM   #2
dginbuffalo
Member
United States

dginbuffalo is offline
 
Join Date: Dec 2010
Location: Buffalo,NY
Posts: 599
It has been a long time since I have done this, But I know you can look on the drive to see the status in bits of the drive input word. If you see all the all the correct bits turn on and the speed reference word change, then most likely one of your parameters not set correctly to control the drive via Modbus.
  Reply With Quote
Old April 4th, 2015, 10:22 AM   #3
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,772
Did you see DickDV's comment (4th post) in this thread

http://www.plctalk.net/qanda/showthread.php?t=53829

on the need for parameter 10.01 to be set to 'comm'?
  Reply With Quote
Old April 5th, 2015, 10:06 PM   #4
prakashchy85
Member
India

prakashchy85 is offline
 
Join Date: Apr 2015
Location: Rudrapur
Posts: 3
ABB drive control via modbus communication with FXCPU plc

First i would like to say thanks u both for replying...........

@dginbuffalo.... mate Please tell how can i check correct status bit of drive for write the refeference value into it. Also may u knw about that perticular parameter of drive (ACS 550) to see the speed reference word change value.

@Danw.....Friend I was already read this thread..and i set the parameter as per below mention point.

1. 1001 EXT1 COMMANDS 10 (COMM) Start/Stop by field buswith Ext1
selected. 40001 bits 03
2. 1102 EXT1/EXT2 SEL 8 (COMM) Reference set selection by fieldbus. 40001 bit 11
3. 1103 REF1 SELECT 8 (COMM) Input reference 1 by fieldbus. 40002

But still clueless.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
ABB ACS 550 Modbus Communication amolthorat1234 LIVE PLC Questions And Answers 1 January 1st, 2014 08:14 PM
Plc suggestion aec LIVE PLC Questions And Answers 36 January 2nd, 2012 12:56 AM
Communication between AB Control Logix and Koyo PLC Forrest LIVE PLC Questions And Answers 10 July 19th, 2010 07:53 PM
Modbus TCP between Quantum PLC and MNS iS Motor Control Center booatoa LIVE PLC Questions And Answers 0 May 26th, 2008 04:17 AM
Communication with ABB plc with VIPA touch panel savyasaasi LIVE PLC Questions And Answers 0 January 25th, 2007 02:26 AM


All times are GMT -5. The time now is 10:09 AM.


.