Without going in to a lot of detail, I'm trying to get an AB PV+ 1000 to talk to the DF1 serial port (Channel 0) on a SLC 5/03. Does anyone out there have any experience with this? If so, I'll offer more detail. A response by 7 AM Eastern Standard on July 22 would be a marvelous thing :)
Bernard
It's not difficult; I have done it lots of times.
The cabling is a straight-through RS-232 serial cable. The PanelView has a "DCE" type serial port and the SLC-5/03 has a "DTE" type serial port, so they don't need a "null modem" cable.
The RSLinx Enterprise DF1 driver configuration is a little more complicated. Make sure that you can browse from your PC to the SLC-5/03 serial port with this driver, before you copy the Local RSLinx Enterprise configuration to the Target tab in the RSLinx Enterprise GUI inside RSView Studio.
Again; you need to configure the Target tab in RSLinx Enterprise so that the PV+ terminal knows how to communicate to your SLC-5/03. The easiest way is to use the Local tab to prove the communications path, then copy that over to the Local tab with the "copy" button.
Make sure that the serial framing and DF1 protocol settings on the SLC-5/03 and the PanelView Plus are both the same. Pay special attention to Error Checking; SLC's use CRC error checking by default, but RSLinx Enterprise uses BCC error checking by default.
I'm using the Allen Bradley 2711-NC13 cable to try to do this. It's the correct cable from my understanding of the documentation, and it's the same cable I'm using to download from my PC to the PV+. Is the cable my problem, by any chance? It's a good cable, but is it the wrong one?
I'm screwing something up, here, and can't seem to find out what.
Thanks so much for your answer.
Bernard
Yes, that cable will work. There has to be something wrong with your RSLinx Enterprise configuration.
You really should get a CompactFlash card for program transfer; it's painfully slow to do that over RS-232.
Post more info about the symptoms of the communication error, and about your RSLinx Enterprise configuration !
(it's also during business hours for RSI technical support if you don't want to wait for a forum discussion of a simple configuration issue.)
I do have the CF card; it is definitely faster.
We've been on the phone with RSI tech sup for most of three hours; my local AB people have done their best and are bringing in the district PLC guy tomorrow.
While I'm not a total geek, I'm no fool either, and AB really needs to do a better job of documenting all their "comms" combinations.
I really appreciate your offer of help, if I get a chance later tonight I'll try to describe better. The key issue is that NOTHING results in a satisfactory comm between PV+ and SLC. All the ports are good, all the cables are good (for some comms), and all the settings match, but it just doesn't talk.
I'm normally of the mindset that I'm doing something wrong for the first two days. After that, I pretty well know I've tried every possible iteration and it's no longer my fault.
I'm usually right :)
I'll let you know one way or another how tomorrow goes. Thanks again.
Bernard
Hi Having issues with a older PanelView touch not working. Screen is connected to a Desktop computer. screen used as a display with touch...
113
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
210
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
734
Hello, I have several SLC-500 based systems. The user interfaces are PanelView 2711-TC1 touchscreens with firmware revision 3. I purchased a...
2,049
i was trying to run a .mer file which i have uploaded from a running pvp1000 same model. when i load it on new pvp1000 it shows " the terminal can...
2,247