3 phases Ac Current to 4-20 mA converter
Hi guys:
I've been looking up on the web but I can not find exactly what I'm looking for.
I need a 3 phase ac current to 4-20 mA converter for 14 existing and working motors:
7 motors 50 KW @ 460 VAC
7 motors 40 kW @ 460 VAC
I do not want individual current transformers, one for each phase. I want a device that has to be installed underneath contactors and three phases pass thru the device and as a result I got a 3 phases current average in 4-20 mA format, no problem if I got three 4-20 mA signals one for each phase. The device can be powered by ac or dc.
__________________
My two cents.
Old September 26th, 2015, 10:56 AM   #2
Mickey
United States
Mickey is offline
Mickey's Avatar
http://loadcontrols.com/
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old September 26th, 2015, 11:01 AM   #3
IndustMech
United States
IndustMech is offline
An electronic Overload with remote monitoring might work, but I'm I don't know if they will give you the 4 - 20 mA your looking for.
I googled "Smart Overload" and found an Eaton C440/XT that might work.
Old September 26th, 2015, 11:02 AM   #4
widelto
Colombia
widelto is offline
widelto's Avatar
Mickey you got it , PH-1000 and PH-3A are exactly what i want. My first candidate.
__________________
My two cents.
Old September 26th, 2015, 11:06 AM   #5
Mickey
United States
Mickey is offline
Mickey's Avatar
Quote:
If you use it , let us know how it works out.
__________________
Mickey
Old September 26th, 2015, 11:14 AM   #6
widelto
Colombia
widelto is offline
widelto's Avatar
Hi IndustMech, I took at look at them,but i see they must be attached to a match contactor and that's not my case. My system is and old one based on NEMA contactors, they know by measuring current how production is behaving. So my idea is to connect my devices to a small PLC and send info to a SCADA.
Thanks.
__________________
My two cents.
Old September 26th, 2015, 11:18 AM   #7
Lare
Finland
Lare is offline
motor takes same current for all phases, so you can monitor only one phase.
Old September 26th, 2015, 11:20 AM   #8
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
I have used the Load Controls Universal Power Cell hardware before and it works very well, even with the output of AC drives.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old September 26th, 2015, 11:31 AM   #9
widelto
Colombia
widelto is offline
widelto's Avatar
We are in south america
Quote:
Yes, that's true, but here in south america power companys are not the best.
__________________
My two cents.
Old September 26th, 2015, 11:49 PM   #10
TheWaterboy
United States
TheWaterboy is offline
TheWaterboy's Avatar
Here in USA the same can be true
Old September 27th, 2015, 08:55 AM   #11
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
Used these with success for many years: http://www.nktechnologies.com/
Old September 27th, 2015, 10:25 AM   #12
jraef
United States
jraef is offline
jraef's Avatar
Allen Bradley's new E300 SSOL can be mounted separately and can be fitted with an analog output, it would be physically smaller than the Load Controls unit. It has built-in Ethernet if that's what you are really after for the SCADA system, so you would not even need the analog output module.
http://literature.rockwellautomation...g010_-en-p.pdf
Old September 27th, 2015, 11:17 AM   #13
boneless
United States
boneless is offline
Check out Simocode from Siemens. You can use them as contactors and get out a bunch of information.
Old September 28th, 2015, 12:21 PM   #14
NetNathan
United States
NetNathan is offline
Flex-Core has good pricing...
I get my meters from them also..
http://www.flex-core.com/current-tra...rs-transducers
__________________
****Control Freak****
Net is where I be and Nathan is me.
Old September 28th, 2015, 01:35 PM   #15
widelto
Colombia
widelto is offline
widelto's Avatar
Tom: I took a look at your, I like them. Thnaks
Jraef: Customer does not want to stop production, so changing overload relay is not an option, though was my first choice because lots of info and easy installation. . Thanks
Netnathan: Yes, they are ok too. Thanks.
__________________
My two cents.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
motor alternating directsoft 32 on a DL06 DRThorne LIVE PLC Questions And Answers 15 November 9th, 2006 08:05 PM
analog input 4 ... 20 mA SIMATIC S7-200 sarac LIVE PLC Questions And Answers 1 October 23rd, 2006 01:22 PM
I/I Converter: 4 - 20 mA to 0 -600 mA Grouper LIVE PLC Questions And Answers 7 September 20th, 2006 08:38 PM
Scale a 4 to 20 mA input Combo LIVE PLC Questions And Answers 4 March 16th, 2005 11:36 AM
adding two 4 to 20 mA analog input to one output in slc 500 05 bks LIVE PLC Questions And Answers 2 December 5th, 2004 01:38 PM