1746-BTM fault
boyd_man
Oct 2002
South Carolina
39
Could I get some one to look at me logic and explain to me what I have wrong.
I’m installing two 1746-BTM cards one is (SER.A, FRN.1) the other is (SER.A FRN. 1.1
PLC Fault
Indirect address file number reference doesn't match the file type of the prefex.
Rung #6 File#3
In LAD 3 Rung 1, there is a MOV instruction for the Slot Number of the First BTM. In your program it is set to 2, but it should be a 5. Also, in the same rung, you need to change the number of BTMs in the system to 2
AB have sample logic pre-done and tested on their www site for the BTM modules and multiples in a rack
I think that FRN 1.? had a problem and when released AB issued new F/W eproms to update the modules, beware though if they send you a series B FW 2 eprom it will fault a series A module
Check with your local AB about this as i may have the FW 1.? and seris wrong but it looks familiar and was quite a few years ago now that i came across this!
N7:14 currently has a value of 12 in it. There is not a N12 data file. How large can N7:14 get? You will have to have data files created to match this.
e.g. N12 data file with at least 193 elements.
Theoretical question. If I have a bad thermal couple and no spares, is there a way to force the BTM to output a specific temperature so that I can...
1,648
I need sample code for programaming a 1746BTM from AB, we are planning to use this to control the temperature of an plastic extruter
1,903
I'm beginning to calibrate the many BTM cards we have in service here, but its turning out to be a real pain in the rear. A power supply capable...
1,819
Hi Does anyone know exactly what the Loop AutoTune Gains level is for (see page 3-2 of the manual) ? The manual is not clear and the KB has...
1,599
Has anyone had any experience with the Allen Bradley 1746-BTM barrel temperature module. We started using them approximately 3 years ago with no...
20
17,621